PSV set pressure during hydrotest of piping

2,606 views
Skip to first unread message

Manoj John

unread,
Dec 24, 2019, 12:23:32 AM12/24/19
to material...@googlegroups.com
Dear Experts,

As per B31.3 what is the PSV set pressure during hydrotest.
Please give expert opinion as there is no clause found in B31.3 for hydrotest PSV set pressure, PSV set pressure for pneumatic only prescribed.

Thanks in advance,
Manoj

Shoaib Nisar

unread,
Dec 24, 2019, 12:31:36 AM12/24/19
to material...@googlegroups.com
Usually we install PSV 5% to hydrotesting pressure i also didn't find any reference in the code but it is recommended practice. 

--
https://materials-welding.blogspot.com/
https://www.linkedin.com/groups/122787
---
You received this message because you are subscribed to the Google Groups "Materials & Welding" group.
To unsubscribe from this group and stop receiving emails from it, send an email to materials-weld...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/materials-welding/CACgUO5nJ9-S1uDxZVTxg%2BYRcsUy8F64M-QRiugW%2BKbmYx6s8Lw%40mail.gmail.com.

Vinodchandra Bhatt

unread,
Dec 24, 2019, 2:28:19 AM12/24/19
to material...@googlegroups.com
Gentlemen,

During HT of piping, all the openings are to be blanked suitably, except test gauges mounted for pressure reading. Means you remove the PSV and blank off the opening.

Thanks & Best Regards,

Vinodchandra Bhatt (M) 99250 10858


--

ViNo Varughese

unread,
Dec 24, 2019, 3:14:52 AM12/24/19
to material...@googlegroups.com
Dear Manoj,

Please check through API RP 520 and you should find the set pressure requirement for PRVs. Typically it is set based on the MAWP or  design pressure. However you also need to consider the static head between the protected equipment and the relied valve while deriving the set pressure.

Hope this helps.


Thanks and Regards
Vino



--

Eyup Tan

unread,
Dec 24, 2019, 3:59:45 AM12/24/19
to material...@googlegroups.com
You should blank PSV during the hydro test or remove PSV from line/equipment. 
Because PSV set pressure is adjusted to %10 above of MAWP. But hydrostatic Test Pressure is 1,5 times of MAWP.
You can't make hydrostatic test 1,5 times of MAWP because PSV will open when pressure comes to 1.1 times of MAWP. 
That is why you need to blank or remove PSV during the hydro test

Saygılarımla, / Best Regards,

Eyup Tan



Balajirajan Palanisamy

unread,
Dec 26, 2019, 6:19:38 AM12/26/19
to material...@googlegroups.com
Dear Mr. Manoj,
   During the Hydro test the set pressure of PSV that you had fixed in the manifold will be as 1.1 times of the line test pressure i.e 10% higher than the line test pressure. 

Regards,
P.Balajirajan.

Shrichand Ghanshyam Bathv

unread,
Dec 27, 2019, 1:15:45 AM12/27/19
to material...@googlegroups.com
Hi, 

Expert, please see the below your answer...as per Saudi Aramco Standard, SAES-A-004 Para 5.7.

Protection from Overpressure
All systems (piping and equipment) while being pressure tested shall be protected from being over pressured by the following:

Pressure test relief valve(s) of adequate capacity set to relieve at 5% above the test pressure shall be installed unless the test pressure is less than 85% SMYS at which time it can be set at 10% above the test pressure. Sizing of these relief valves used for testing shall follow the requirements of API RP 520, Part 1. The relief valve(s) shall be tested, dated, and tagged within two weeks prior to the pressure test for new construction projects, and within three months for maintenance operations.
The pressure test relief valve shall be accompanied with a calibration certificate that includes the cold differential test pressure (CDTP), test date and the spring range. The CDTP shall be within the spring range.
Pressure testing relief valves shall be car sealed at the pressure adjusting screw and verified prior to test.

Thank you for your consideration. I look forward to hearing from you. Your Immediate Response will be Highly Appreciated.

Best Regards

Shrichand Ghanshyam Bathv 

Mobile Number : +91 8551911459

Email Id : shricha...@gmail.com 

Skype Id : shrichand.bathv 

-------------------------------------------------------------

"Success doesn't come to you... you go to it. "

"Helping hands are better than praying lips. "

--------------------------------------------------------------

P please consider the environment before printing this mail note.

*******************************************************************






Shoaib Nisar

unread,
Dec 27, 2019, 1:15:45 AM12/27/19
to material...@googlegroups.com
Dear P.Balajirajan do you have any reference??

Reply all
Reply to author
Forward
0 new messages