Hello,
I supplement these exchanges with a new question on the calculation of the
Spread Rate flame by SDS, when the reaction of combustion of a liquid with
detail has been defined.
By using & VENT, XYZ = and SPREAD_RATE, the combustion happens as expected.
Now, if I want to pilot my reaction by MATL_ID. Surprise: the inflammation of
my spill is almost instantaneous, hence a SPREAD_RATE of more than 5 m / s. For
FOD (Diesel), the value of the literature is around 3 cm / s at 20°C initial
temperature.
I forced SPREAD_RATE in my MATL_ID but it did not change anything. I did not
have this problem with FDS 6.5.1. What to do?
Could the parameter ABSORPTION_COEFFICIENT solve my problem?
FDS is it able to calculate by itself, the
flame spread on a liquid fuel spill?
Here is the detail of my file.
&HEAD CHID='FODR13', TITLE='Combustion d une nappe rectangulaire de FOD par SURF ID $0' /
&MESH IJK=24,16,32, XB=-12.0,12.0,-4.0,4.0,0.0,16.0 /
&TIME T_END=20.0 /
&DUMP NFRAMES=100.0 /
&MISC TMPA=15.0 /
&REAC ID = 'Diesel'
FYI = 'C16H34, NFPA Handbook, Babrauskas, ramené à C13H27.625'
HEAT_OF_COMBUSTION = 43027.
SOOT_YIELD = 0.10
C = 7
H = 14.875 /
&MATL ID = 'Carburant'
FYI = 'Diesel FDS6'
SPECIFIC_HEAT = 1.99
CONDUCTIVITY = 0.127
DENSITY = 855.
N_REACTIONS = 1
NU_SPEC = 1.
SPEC_ID = 'Diesel'
BOILING_TEMPERATURE = 265.
SPECIFIC_HEAT = 1.0
HEAT_OF_REACTION = 200./
&MATL ID = 'STEEL'
EMISSIVITY = 1.0
DENSITY = 7850.
CONDUCTIVITY = 45.8
SPECIFIC_HEAT = 0.46 /
&SURF ID = 'NAPPE'
COLOR = 'YELLOW'
MATL_ID = 'Carburant'
SPREAD_RATE = 0.03
THICKNESS = 0.5 /
&SURF ID = 'STEEL SHEET'
COLOR = 'BLACK'
MATL_ID = 'STEEL'
BACKING = 'EXPOSED'
THICKNESS = 0.003 /
&SURF ID = 'BURNER', COLOR = 'RED', HRRPUA = 1000. /
&VENT XB=8.5,9.5,-0.5,0.5,0.5,0.5, SURF_ID='BURNER' / Ignition sur la nappe
&OBST XB=-10.0,10.0,-2.0,2.0,0.0,0.5, SURF_IDS='NAPPE', 'STEEL SHEET', 'STEEL SHEET' /
&OBST XB=-10.0,-10.0,-2.0,2.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=10.0,10.0,-2.0,2.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=-10.0,10.0,-2.0,-2.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=-10.0,10.0,2.0,2.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&VENT MB='XMIN', SURF_ID='OPEN' /
&VENT MB='XMAX', SURF_ID='OPEN' /
&VENT MB='YMIN', SURF_ID='OPEN' /
&VENT MB='YMAX', SURF_ID='OPEN' /
&VENT MB='ZMAX', SURF_ID='OPEN' /
&BNDF QUANTITY='RADIATIVE HEAT FLUX' /
&BNDF QUANTITY='INCIDENT HEAT FLUX' /
&BNDF QUANTITY='GAUGE HEAT FLUX' /
&SLCF PBY=0.00, QUANTITY='TEMPERATURE' /
&SLCF PBY=0.00, QUANTITY='HRRPUV' / Heat Release Rate per Unit Volume
&TAIL /
I have taken note of your recommendations. I have rewritten the attached
file and the combustion starts. The
entire pool gets into fire instantly. I can’t propose this simulations at my coworkers
(French Commissariat for Atomic Energy: CEA), very picky with the kinetics of
combustion.
&HEAD
CHID='FODR15', TITLE='FOD combustion with MATL $0' /
&MESH IJK=24,24,32, XB=-12.0,12.0,-12.0,12.0,0.0,16.0 /
&TIME T_END=40.0 /
&DUMP NFRAMES=200.0 /
&MISC TMPA=20.0, SUPPRESSION=.FALSE. /
&REAC ID = 'Diesel'
FYI = 'C16H34, NFPA Handbook, Babrauskas, to C7H14.875'
HEAT_OF_COMBUSTION = 43027.
SOOT_YIELD = 0.10
AUTO_IGNITION_TEMPERATURE = 400.
C = 7
H = 14.875 /
&MATL ID = 'Carburant'
FYI = 'Diesel FDS6'
SPECIFIC_HEAT = 1.99
CONDUCTIVITY = 0.127
DENSITY = 855.
N_REACTIONS = 1
NU_SPEC = 1.
SPEC_ID = 'Diesel'
BOILING_TEMPERATURE = 265.
HEAT_OF_REACTION = 200./
&MATL ID = 'STEEL'
EMISSIVITY = 1.0
DENSITY = 7850.
CONDUCTIVITY = 45.8
SPECIFIC_HEAT = 0.46 /
&SURF ID = 'NAPPE'
COLOR = 'YELLOW'
MATL_ID = 'Carburant'
THICKNESS = 0.25 /
&SURF ID = 'STEEL SHEET'
COLOR = 'BLACK'
MATL_ID = 'STEEL'
BACKING = 'EXPOSED'
THICKNESS = 0.003 /
&SURF ID = 'BURNER', COLOR = 'RED', HRRPUA = 500. /
&VENT XB=8.5,9.5,-0.5,0.5,0.5,0.5, SURF_ID='BURNER' / Ignition
&OBST XB=-10.0,10.0,-10.0,10.0,0.0,0.5, SURF_IDS='NAPPE', 'STEEL SHEET', 'STEEL SHEET' /
&OBST XB=-10.0,-10.0,-10.0,10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=10.0,10.0,-10.0,10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=-10.0,10.0,-10.0,-10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=-10.0,10.0,10.0,10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&VENT MB='XMIN', SURF_ID='OPEN' /
&VENT MB='XMAX', SURF_ID='OPEN' /
&VENT MB='YMIN', SURF_ID='OPEN' /
&VENT MB='YMAX', SURF_ID='OPEN' /
&VENT MB='ZMAX', SURF_ID='OPEN' /
&SLCF PBY=0.00, QUANTITY='TEMPERATURE' /
&SLCF PBY=0.00, QUANTITY='HRRPUV' / Heat Release Rate per Unit Volume
&TAIL
/
On the 12-06-2017, you wrote: "FDS is not going to calculate the spread
rate on a liquid pool if you are using fast chemistry.", So, I repeated my
example with the "Complex fuel
Model ". Ultimately,
I will need this type of reaction, because the liquids fuels that can burn on
our chemistry plant, contain Cl, N, S ... and other molecules.
&HEAD CHID='FODR20', TITLE='Combustion d une nappe rectangulaire de FOD $0' /
&MESH IJK=24,24,32, XB=-12.0,12.0,-12.0,12.0,0.0,16.0 /
&TIME T_END=40.0 /
&DUMP NFRAMES=160.0 /
&MISC TMPA=20.0 /
&SPEC ID = 'OXYGEN', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'NITROGEN', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'NITROGEN DIOXIDE', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'WATER VAPOR', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'CARBON MONOXIDE', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'CARBON DIOXIDE', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'HYDROGEN CYANIDE', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'SOOT', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'SULFUR DIOXIDE', LUMPED_COMPONENT_ONLY = .TRUE. /
&SPEC ID = 'AIR',
SPEC_ID(1) = 'OXYGEN', VOLUME_FRACTION(1)=1,
SPEC_ID(2) = 'NITROGEN', VOLUME_FRACTION(2)=3.76,
BACKGROUND=.TRUE. /
&SPEC ID = 'FOD', FORMULA = 'C7H14.875' /
&SPEC ID = 'PRODUCTS_FOD1',
SPEC_ID(1) = 'CARBON DIOXIDE', VOLUME_FRACTION(1) = 6.614380,
SPEC_ID(2) = 'CARBON MONOXIDE', VOLUME_FRACTION(2) = 0.042436,
SPEC_ID(3) = 'WATER VAPOR', VOLUME_FRACTION(3) = 7.418434,
SPEC_ID(4) = 'SOOT', VOLUME_FRACTION(4) = 0.381315,
SPEC_ID(5) = 'NITROGEN', VOLUME_FRACTION(5) = 38.896508 /
&REAC ID = 'Diesel Fuel'
FUEL = 'FOD',
HEAT_OF_COMBUSTION = 43027,
SPEC_ID_NU = 'FOD','AIR','PRODUCTS_FOD1'
NU=-1,-10.34482,1 /
&MATL ID = 'FOD'
FYI = 'Diesel FDS6'
SPECIFIC_HEAT = 1.997
CONDUCTIVITY = 0.127
DENSITY = 855.
BOILING_TEMPERATURE = 265.
HEAT_OF_REACTION = 200./
&MATL ID = 'STEEL'
EMISSIVITY = 1.0
DENSITY = 7850.
CONDUCTIVITY = 45.8
SPECIFIC_HEAT = 0.46 /
&SURF ID = 'NAPPE'
COLOR = 'YELLOW'
MATL_ID = 'FOD'
THICKNESS = 0.25 /
&SURF ID = 'STEEL SHEET'
COLOR = 'BLACK'
MATL_ID = 'STEEL'
BACKING = 'EXPOSED'
THICKNESS = 0.003 /
&SURF ID = 'BURNER', COLOR = 'RED', HRRPUA = 500. /
&VENT XB=8.5,9.5,-0.5,0.5,0.5,0.5, SURF_ID='BURNER' / Ignition sur la nappe
&OBST XB=-10.0,10.0,-10.0,10.0,0.0,0.5, SURF_IDS='NAPPE', 'STEEL SHEET', 'STEEL SHEET' /
&OBST XB=-10.0,-10.0,-10.0,10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=10.0,10.0,-10.0,10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=-10.0,10.0,-10.0,-10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&OBST XB=-10.0,10.0,10.0,10.0,0.0,2.0, SURF_ID='STEEL SHEET' /
&VENT MB='XMIN', SURF_ID='OPEN' /
&VENT MB='XMAX', SURF_ID='OPEN' /
&VENT MB='YMIN', SURF_ID='OPEN' /
&VENT MB='YMAX', SURF_ID='OPEN' /
&VENT MB='ZMAX', SURF_ID='OPEN' /
&SLCF PBY=0.00, QUANTITY='TEMPERATURE' /
&SLCF PBY=0.00, QUANTITY='HRRPUV' / Heat Release Rate per Unit Volume
&TAIL /
I
have never been able to start the burning of the pool. Even with HRRPUA very
high for my BURNER. For
this choice of pyrolysis modeling, I understood that it was not possible to
indicate to FDS: INGNITION_TEMPERATURE. Because
FLASHPOINT is not a possible variable for FDS too, I don’t know what to add, or
to remove, to have ignition and flame spreading on the pool. I necessarily have
evaporation around my burner. Because AIT is not specified, all vapors produced
should ignite. What’s wrong?
Would
you have an example of a liquid pool combustion, with an complex fuel model, so
that I can analyze it and without wasting your time?
Thanks in advance.
I have taken note of your recommendations. I have rewritten the attached
file and the combustion starts. The
entire pool gets into fire instantly. I can’t propose this simulations at my coworkers, very picky with the kinetics of
combustion.
(File 1.fds)
On the 12-06-2017, you wrote: "FDS is not going to calculate the spread
rate on a liquid pool if you are using fast chemistry.", So, I repeated my
example with the "Complex
fuel Model ". Ultimately, I will need this type of reaction, because the liquids fuels that can burn on our chemistry plant, contain Cl, N, S ... and other molecules.
(File 2.fds)
I have never been able to start the burning of the pool.
Even with HRRPUA very high for my BURNER. For this choice of pyrolysis modeling, I understood that it was not possible to indicate to FDS: INGNITION_TEMPERATURE. Because FLASHPOINT is not a possible variable for FDS too, I don’t know what to add, or to remove, to have ignition and flame spreading on the pool. I necessarily have evaporation around my burner. Because AIT is not specified, all vapors produced should ignite. What’s wrong?
Would
you have an example of a liquid pool combustion, with an complex fuel model, so
that I can analyze it and without wasting your time?
Thanks in advance.