Air Residence Time

181 views
Skip to first unread message

Bryan Klein

unread,
Sep 8, 2020, 12:55:50 PM9/8/20
to FDS and Smokeview Discussions
"Modelling a car park smoke and pollution ventilation system, and want to show a slice at roughly head-height plotting the mean age of air or air residence time.  Is this possible at all?"


Any suggestions on if/how to do this in FDS?
-Bryan

Kevin McGrattan

unread,
Sep 8, 2020, 1:01:45 PM9/8/20
to fds...@googlegroups.com
You can seed the flow with MASSLESS particles and color them with 'PARTICLE AGE'

dr_jfloyd

unread,
Sep 8, 2020, 1:10:37 PM9/8/20
to FDS and Smokeview Discussions
Another option is run the model with the ventilation system for a long enough period of time to reach steady-state flow, then introduce a tracer gas into the supply vents and run for a short period of time. At the end of that short time period you can use the tracer concentration and the length of time to derive the local air exchange rate. 

Bryan Klein

unread,
Sep 8, 2020, 1:28:19 PM9/8/20
to FDS and Smokeview Discussions
Thank you for these suggestions and they answer my question.
They are very much the way I was thinking to go, I was curious if there was some secret quantity or method to extract this directly in a 3D Slice or Statistical output data.

Best Regards,
Bryan

Michael Abbot

unread,
Sep 8, 2020, 10:37:03 PM9/8/20
to fds...@googlegroups.com
Team,

I tried a method similar to this, and abandoned it as particle injection absorbed a considerable amount of processing time. The particles need to turn off at some point in time, otherwise as model time increases, the amount of CPU time required appears to increase to process.

I would recommend a minimum velocity criteria within the basement car park space, further, and slices measuring Carbon Monoxide levels throughout. 

Regards,

Michael Abbot


--
You received this message because you are subscribed to the Google Groups "FDS and Smokeview Discussions" group.
To unsubscribe from this group and stop receiving emails from it, send an email to fds-smv+u...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/fds-smv/3a3bd51b-6967-4e13-96f3-d665d366bbb1n%40googlegroups.com.

fde

unread,
Sep 9, 2020, 2:49:30 AM9/9/20
to FDS and Smokeview Discussions
Just brainstorming, 
If we set FIXED_MIX_TIME to a very high number and turn off the combustion while releasing the gas at certain concentration, then measure the whole compartment with a device XB to find AVERAGE value of MIXING TIME quantity, would it work?

dr_jfloyd

unread,
Sep 9, 2020, 6:50:43 AM9/9/20
to FDS and Smokeview Discussions
MIXING TIME would not give you what Bryan is looking for.  MIXING TIME is a measure of how species in the cell are mixing in that cell and not a measure of of transport of species to/from the cell.

fde

unread,
Sep 9, 2020, 8:39:05 AM9/9/20
to FDS and Smokeview Discussions
Thank you.