I was wondering what is the correct way in setting up a fire with HRRPUA using a burner ramp and a fixed fire surface area and whether there is any difference in the results if the F fraction goes >1.
For example, I want to set up a sprinkler controlled fire scenario. I have determined the burner ramp and maximum HRR. The burner/fire surface area is fixed at 2 m x 4.8 m.
Is the following set up correct? In this case to achieve the maximum HRR, F keeps increasing to >1 until the maximum HRR is reached.
&SURF ID='FIRE D K',
COLOR='RED',
HRRPUA=521.0,
RAMP_Q='FIRE D K_RAMP_Q'/
&RAMP ID='FIRE D K_RAMP_Q', T=0.0, F=0.0/
&RAMP ID='FIRE D K_RAMP_Q', T=10.0, F=3.752E-3/
&RAMP ID='FIRE D K_RAMP_Q', T=20.0, F=0.015/
&RAMP ID='FIRE D K_RAMP_Q', T=30.0, F=0.034/
&RAMP ID='FIRE D K_RAMP_Q', T=40.0, F=0.06/
&RAMP ID='FIRE D K_RAMP_Q', T=50.0, F=0.094/
&RAMP ID='FIRE D K_RAMP_Q', T=60.0, F=0.135/
&RAMP ID='FIRE D K_RAMP_Q', T=70.0, F=0.184/
&RAMP ID='FIRE D K_RAMP_Q', T=80.0, F=0.24/
&RAMP ID='FIRE D K_RAMP_Q', T=90.0, F=0.304/
&RAMP ID='FIRE D K_RAMP_Q', T=100.0, F=0.375/
&RAMP ID='FIRE D K_RAMP_Q', T=110.0, F=0.454/
&RAMP ID='FIRE D K_RAMP_Q', T=120.0, F=0.54/
&RAMP ID='FIRE D K_RAMP_Q', T=130.0, F=0.634/
&RAMP ID='FIRE D K_RAMP_Q', T=140.0, F=0.735/
&RAMP ID='FIRE D K_RAMP_Q', T=150.0, F=0.844/
&RAMP ID='FIRE D K_RAMP_Q', T=160.0, F=0.961/
&RAMP ID='FIRE D K_RAMP_Q', T=170.0, F=1.084/
&RAMP ID='FIRE D K_RAMP_Q', T=180.0, F=1.216/
&RAMP ID='FIRE D K_RAMP_Q', T=190.0, F=1.354/
&RAMP ID='FIRE D K_RAMP_Q', T=200.0, F=1.501/
&RAMP ID='FIRE D K_RAMP_Q', T=210.0, F=1.655/
&RAMP ID='FIRE D K_RAMP_Q', T=220.0, F=1.816/
&RAMP ID='FIRE D K_RAMP_Q', T=230.0, F=1.985/
&RAMP ID='FIRE D K_RAMP_Q', T=240.0, F=2.161/
&RAMP ID='FIRE D K_RAMP_Q', T=250.0, F=2.345/
&RAMP ID='FIRE D K_RAMP_Q', T=260.0, F=2.536/
&RAMP ID='FIRE D K_RAMP_Q', T=270.0, F=2.735/
&RAMP ID='FIRE D K_RAMP_Q', T=276.0, F=2.735/
&RAMP ID='FIRE D K_RAMP_Q', T=400.0, F=2.735/
Or the following is the correct way? Maximum HRR is reached when F is 1.0 (i.e. the value of F is always between 0 and 1, which is the fraction of the HRR at time t over the maximum HRR over the simulation time). In this case, the HRRPUA has to be increased to 1425.
.
&SURF ID='FIRE D K',
COLOR='RED',
HRRPUA=1425.0,
RAMP_Q='FIRE D K_RAMP_Q'/
&RAMP ID='FIRE D K_RAMP_Q', T=0.0, F=0.0/
&RAMP ID='FIRE D K_RAMP_Q', T=10.0, F=0.001372/
&RAMP ID='FIRE D K_RAMP_Q', T=20.0, F=0.005484/
&RAMP ID='FIRE D K_RAMP_Q', T=30.0, F=0.01243/
&RAMP ID='FIRE D K_RAMP_Q', T=40.0, F=0.021938/
&RAMP ID='FIRE D K_RAMP_Q', T=50.0, F=0.034369/
&RAMP ID='FIRE D K_RAMP_Q', T=60.0, F=0.04936/
&RAMP ID='FIRE D K_RAMP_Q', T=70.0, F=0.067276/
&RAMP ID='FIRE D K_RAMP_Q', T=80.0, F=0.087751/
&RAMP ID='FIRE D K_RAMP_Q', T=90.0, F=0.111152/
&RAMP ID='FIRE D K_RAMP_Q', T=100.0, F=0.137112/
&RAMP ID='FIRE D K_RAMP_Q', T=110.0, F=0.165996/
&RAMP ID='FIRE D K_RAMP_Q', T=120.0, F=0.197441/
&RAMP ID='FIRE D K_RAMP_Q', T=130.0, F=0.23181/
&RAMP ID='FIRE D K_RAMP_Q', T=140.0, F=0.268739/
&RAMP ID='FIRE D K_RAMP_Q', T=150.0, F=0.308592/
&RAMP ID='FIRE D K_RAMP_Q', T=160.0, F=0.351371/
&RAMP ID='FIRE D K_RAMP_Q', T=170.0, F=0.396344/
&RAMP ID='FIRE D K_RAMP_Q', T=180.0, F=0.444607/
&RAMP ID='FIRE D K_RAMP_Q', T=190.0, F=0.495064/
&RAMP ID='FIRE D K_RAMP_Q', T=200.0, F=0.548812/
&RAMP ID='FIRE D K_RAMP_Q', T=210.0, F=0.605119/
&RAMP ID='FIRE D K_RAMP_Q', T=220.0, F=0.663985/
&RAMP ID='FIRE D K_RAMP_Q', T=230.0, F=0.725777/
&RAMP ID='FIRE D K_RAMP_Q', T=240.0, F=0.790128/
&RAMP ID='FIRE D K_RAMP_Q', T=250.0, F=0.857404/
&RAMP ID='FIRE D K_RAMP_Q', T=260.0, F=0.927239/
&RAMP ID='FIRE D K_RAMP_Q', T=270.0, F=1.0/
&RAMP ID='FIRE D K_RAMP_Q', T=276.0, F=1.0/
&RAMP ID='FIRE D K_RAMP_Q', T=400.0, F=1.0/
Or both methods above are acceptable?
We have run both and seems that there is a slight difference when we look at visibility slice. Should there by any difference?