Thanks a lot Stuart,
I think I found the problem, but it still puzzles me. I realized that I had left a window in the ground floor of the building fully open every day on a schedule, which brings 500 cfm to the building due to stack effect depending on the outdoor temperature (from the WTH file). I suppose the amount of air entering through the window every day changes the pressure balances in the building, and thus the internal flow rates. However, I am still puzzled about the air distribution system. The system consists of a constant volume 350 cfm fan that supplies air to the rooms, which recirculates back to the fan. Shouldn't the supplied air, from the constant volume fan, not be affected by the interior pressures? The terminals have been balanced, and the ducts are modelled with zero leakage. I understand that the duct temperatures use the same temperature of the space where it is located. However, the interior temperatures remain fixed, not fluctuating with the exterior temperatures.
I tried to explain this by following the conservation of mass, not conservation of volume, principle. Given that the outdoor air is cold, it will change the density of the indoor air and thus all the mass flow rates, even through the ducts. But, again, the temperatures in the spaces remain constant, i.e. are not affected by the outdoor air temperature, therefore the temperatures/densities in the ducts also remain constant. Furthermore, density variations should not have such a big impact on duct airflows.
My conclusion is that even if a constant volume fan is blowing air through the ducts, the actual amount of air flowing through the ducts is a function of the pressure differentials between the air terminals, right?
My file is attached just in case you want to look at it, the open window is named "openw12" in the bathroom of the ground floor.
Thanks!
-Rodrigo