Giannis,
Where to begin?
Refer to Chapter 16 of the ASHRAE Handbook of Fundamentals 2022 and the Airflow Theory section of the CONTAM User Guide for the following.
CONTAM provides multiple forms of the powerlaw airflow element.
In its most basic form:
![]()
As in the example files provided, one can assume a Normalized Leakage for a residential building or perform a blower door test to measure mass flow,
in kg/s (or
in m3/s), at various values of
to obtain C and n.
One can also assume the powerlaw form of an orifice.
In this form of the powerlaw equation, the orifice Area is available.
One can then obtain an effective leakage area for the orifice from the conversions offered in the HoF.
If one assumes a total leakage area for a building and normalizes it by the total building surface area, then one has a leakage per building surfaca area, e.g., cm2/m2.
This is similar to what was done in the tutorial.
One could also measure the leakge of individual building components, e.g., windows.
This could be normalized by window area or window perimeter (assuming similar construction of windows of various dimensions).
CONTAM allows one to utilize any form, leakage area per item, leakage area per length, or leakage are per area.
For a window, one would then assume one of these “normalized” forms to define a window leakage element.
Then each flow path that references this element would be provided a multiplier to obtain the total leakage for the specific flow path.
Therefore, the multiplier would either be total windows, total window perimeter length, or total window area.
This is for closed windows.
For open windows, one would use the Large Opening element types.
Again, engineering judgement is required to decide how to aportion leakage within a building model.
This judgement includes knowledge of the emperical data avaialbel to the modeler.
For what it’s worth, there are also libraries of input data available on the NIST Multizone Modeling website.
However, you will notice that there is no longer a table of leakge data available in the HoF.
This is due the fact that buildin leakage varies so widely, and there are few correlations that relate leakage to building properties.
- Stuart