Dear CONTAM Support Team,
I am currently performing a stair pressurization simulation in CONTAM using a duct network with balanced terminals.
The objective of the simulation is to maintain approximately constant airflow at the terminals in order to satisfy the minimum velocity criteria at the stair doors. For this purpose, I used the “Balance Terminal” option and defined a design airflow rate of approximately 0.7 m³/s for each terminal.
However, after running the balancing process, the “Balance Loss Coefficient (Cb)” values calculated by CONTAM became extremely high for all terminals. The values are ranging approximately from 74 to 107.
My question is related to the physical interpretation of these results and how to reduce these values to something more compatible with real balancing or airflow control devices.
What I expected to observe was:
However, CONTAM is generating high Cb values for almost all terminals, including the upper floors located farther from the fan and duct network.
From my understanding, this indicates that the network has excessive available pressure and that the software is artificially creating losses at the terminals in order to achieve the desired airflow rates.
I have already tried:
but the Cb values still remain excessively high.
I would like to better understand:
I am attaching the model file for reference and analysis.
Thank you very much for your support and assistance.
Best regards,
Sávio Almonfrey - Firefighter


Dear CONTAM Support Team,
I hope you are doing well.
I would like to kindly follow up regarding the email I previously sent about the stair pressurization simulation and the high “Balance Loss Coefficient (Cb)” values generated during the “Balance Terminal” process in CONTAM.
I understand your team may be busy, but I would greatly appreciate any support or guidance you could provide when possible. Your assistance would be extremely valuable for helping me better understand the physical interpretation of these results and the most appropriate modeling strategy.
Please let me know if you need any additional information or files from my side.
Thank you very much again for your time and support.
Best regards,
Sávio Almonfrey
Firefighter – Brazil
Duct design incorporates friction losses within the ducts and dynamic losses at duct fittings.
This is a complex topic that requires specific information for various duct geometries.
You can review this information in various design handbooks, including the ASHRAE Handbook of Fundamentals, chapter on Duct Design.
You can also read about the Cb values in the Theoretical Background -> Airflow Analysis -> Ducts section of the User Guide.
It is essentially the dynamic loss coefficient for a zero-length duct (i.e., a duct terminal).
I’m attaching some work I did quite some time ago related to an example in the ASHRAE Handbook of Fundamentals.
I didn’t finalize the work, but it may help you understand the duct design process.
The example is from the Duct Design chapter of the 2005 and 2013 versions (they are the same example, but numbered 6 and 7, respectively).
- Stuart
--
To unsubscribe from this group, send email to
contam+un...@list.nist.gov
View this message at https://list.nist.gov/contam
Dear Stuart,
Thank you for your response and for sharing the duct design example. I have reviewed the material and also read the theoretical section of the CONTAM User Guide regarding duct flow analysis and the definition of the Cb coefficient.
However, I am still struggling to understand why CONTAM generates such high Cb values during the balancing process.
Based on the attached ASHRAE duct design example, I understand the concepts of duct sizing, balancing dampers, equal friction, and static regain methods. My question is specifically related to the way CONTAM performs terminal balancing.
In my model, the airflow rates are successfully equalized among the terminals, but the resulting Cb values are extremely high (approximately 70 to 110). What I do not understand is why CONTAM requires such large loss coefficients to achieve the desired balancing.
From an engineering perspective, it seems that the same airflow equalization could potentially be achieved with lower balancing losses, resulting in lower system pressure requirements and, consequently, a fan with lower performance specifications and lower energy consumption.
Therefore, I would like to better understand:
My main doubt is not about the duct design methodology itself, but rather about the internal logic used by CONTAM to calculate these balancing coefficients and why the resulting values become so high.
Any additional explanation would be greatly appreciated.
Best regards,
Domingos Sávio Almonfrey
Dear Stuart,
Thank you very much for your detailed explanation and for providing the balancing models.
I reviewed the files and reproduced the procedure you used. After analyzing each modification, I now fully understand the balancing methodology adopted in CONTAM.
In particular, I verified that, for the purpose of determining the balancing coefficients (Cb), it is indeed necessary to minimize the influence of the building on the duct network. Increasing the wall leakage area to a very large value effectively makes the zones behave almost like outdoor conditions, allowing the duct system to be balanced without the pressure interactions generated by the building.
After performing the simulations, it became clear that the objective is to isolate the duct network from the effects of zone pressures, temperature differences, stack effect, and other building-related influences, so that the balancing process reflects only the characteristics of the duct system itself.
I also now understand why the balancing algorithm can generate large Cb values when the building effects are present, and that the algorithm simply iterates toward the target flow rates without evaluating whether the resulting coefficients are physically significant.
Your explanation and the example models clarified the entire procedure for me, and I now have a much better understanding of how the balancing process should be carried out in CONTAM.
Thank you again for your time, support, and for helping me understand this topic in greater depth.
Best regards,
Domingos Sávio Almonfrey