Hello Stuart and CONTAM team,
(replying to this thread because my post is relevant to the Orifice Area powerlaw model laminar coefficient mentioned)
I am testing behavior of the Orifice Area powerlaw airflow model in CONTAM near the transition from Laminar to turbulent flow. I'm running ContamW 3.4.06 with ContamX 3.4.02.
The model am using is a 10-second transient airflow simulation with no contaminants.
In the model, I use a 0.5 kg/s AHS Supply (no recirculation, not that it would matter) to pressurize the only Zone. This Supply is on the "day1" schedule, which is trapezoidal and always decreasing from the initial value.
I'm not considering transient density effects, so I have "vary density with time step" turned off. I'm using the schedule to consider different set points for the AHS Supply.
I am comparing simulation results to analytical (Kirchhoff's laws based) hand calculations for t=0 through t=5 (seconds). The node network represents a current divider in the electrical circuit analog. Only t=0 should create turbulent flow through the orifice according to my calculations.
After t=4 (so starting at 5s), the results seem to "freeze" and the total mass balance of airflow out does not equal the supply airflow.
Can y'all explain what I'm running into with the solver here? I know that there are likely some issues with precision applying CONTAM to such laminar and low-pressure flow. Is there a calculable point where the solver starts to error out of being useful?
Feel free to download the attached PRJ file as well.
Thank you!