Question about Modeling Gas Dispersion

14 views
Skip to first unread message

Caleb Taylor

unread,
Sep 24, 2025, 8:26:12 AMSep 24
to CONTAM
Hello everyone,

I am working on a project using CONTAM to model the dispersion of gas species throughout a 3-story building (~90 zones) that does not normally exchange air with the ambient atmosphere (unique application). I connect the “exterior” zones to ambient with flow elements set to have a negligible airflow. This has yielded steady-state airflow results consistent with the expected values. I defined the initial atmosphere (composed of N2, O2, Ar, and CO2) and then used a burst model to release ~10 lbs of a heavy gas contaminant into the building’s atmosphere. I defined the molar mass, diffusion coefficient, effective density, and default concentration for all gas species. Ultimately, I want to determine the steady-state concentration of the contaminant gas in each zone and then ventilate with the ambient atmosphere to restore the buildings air.

When I perform transient contaminant simulations the results converge to the same concentration in each zone, regardless of zone elevation. This is inconsistent with the expected result of the heavier gas having a higher concentration on lower elevation zones. When reviewing the program documentation I have been struggling to determine if this is an intended result, based on the well-mixed assumption. I am currently experimenting with 1-D zones to correct this, but haven’t had much success. Is it possible to simulate gas dispersion with CONTAM and have buoyancy effects enabled?

Thank you,
Caleb

William Dols

unread,
Sep 25, 2025, 8:16:14 AMSep 25
to CONTAM, tayl...@vcu.edu
Caleb,
CONTAM is generally a "well-mixed" model, so zones are represented as having a single concentration within each zone/node.
It does not provide for the separation or settling of a gas species within different regions of air of a given zone based on species properties.
There are several aspects of CONTAM that you may be misunderstanding and would take more than a single email to clarify.
Please start with a simple model and explore the behavior before working with such a complex, 90-zone system.
You might also consider working with a different model altogether, depending on your requirements. 
Feel free to reach out to me directly via email if you wish to discuss further.
- Stuart