I'm trying to double check the results I got from my CONTAM model. I have the ambient at -4C and zone temperature at 20C. I have an external door (closed) defined by the flow coefficient 0.0025 m3/s/Pa^n and flow exponent 0.6.
According to my results, the dp on the flow path is 55.2113 Pa, so I would expect a flow rate of 0.0025 * 55.2113^0.6 = 0.0277 m3/s.
... but according to CONTAM, the flow rate is 0.06 sm3/s. Even if I adjust for the difference in density this is still a way off.
Moreover, I don't understand why the pressure difference is reported as 55.2113 Pa, because the Pambt is -217.966 Pa and the Pg in the zone is -57.9929 Pa, so should dp not be around 159 Pa???
I have attached screenshots and my model - in this example I was referring to ExtDoor-CIBSE-A and zone G-BOHNorth on the Ground floor.