>My house is wired with two-wire romex with no ground wire. I have been told
>that I can install a gfci outlet. Does it offer protection to the outlets
>downstream? Do I run a shunt between the ground terminal and the neutral
>on the gfci?
I think it will because it compares the current flowing through the
neutral and hot lines and if there is a difference (because some of
the current is flowing through you) it will trip out.
Heres how. You must find the first receptacle box in each run coming
from the electrical panel. Remove the old receptacle and install the
GFCI according to the directions. Properly installed this receptacle
and all downstream receptacles will be protected. NO ground wires are
required as GFCI's protect by comparing current on the hot wire to the
neutral wire. If the difference exceeds 5 mA the GFCI trips. Your
outlets still won't have grounds but you will now be protected.
Hope this answers your question.
Scott
dstop...@sallie.wellesley.edu wrote:
>My house is wired with two-wire romex with no ground wire. I have been told
>that I can install a gfci outlet. Does it offer protection to the outlets
>downstream? Do I run a shunt between the ground terminal and the neutral
>on the gfci?