If this unit has been sitting all winter and hasn't ran this
year, there's a good chance that the compressor is just stuck.
One of the old standbys it to turn the thing on and give the
compressor a good hard wack with a 2X4 or rubber mallet--trying
not to dent the compressor can too much. I'd check to make sure
it's getting good voltage to the compressor first. If it isn't
getting voltage to the compressor, you're looking at things like
loose wires or a defective thermostat.
Dennis
* Sent from RemarQ http://www.remarq.com The Internet's Discussion Network *
The fastest and easiest way to search and participate in Usenet - Free!
Thanks,
Todd
Bill
When you turn on the AC do you have a noticeable power drain? (I.E. Dimming
lights, etc.)
If yes, then I agree with the 'Stuck Compressor' theory.
If no, then I think your system has probably lost some quantity of
refrigerant gas (Probably R-12?), causing a 'Low-Pressure' Cut-off switch to
prevent the compressor from running; If this is the case, you need to take
it to a qualified repair shop.
Good luck,
TG
Ops <twil...@avistacorp.com> wrote in message
news:393EF3F7...@avistacorp.com...
Ops wrote:
>
> Here's a follow up to our request for help on our A/C unit. As y'all
> suggested, I upgraded the existing 12 guage extention to a 10 guage (30
> amp) cord and then
> proceeded to turn the unit on... Nothing!! Fan runs fine but still no
> air-conditioning.
> Bummer!! Any other suggestions for items to check before I yank her out
> and take
> to RV repair center?? The unit is a '91 13,500 BTU Emerson "Quite Cool"
> w/heat
> strip.
If there's no evidence of high current draw (lights dimming - NOT 12
volt lights!, funny growling/humming noises, etc) when you turn it
on, then it is likely that the thermal overload compressor protector
has failed. You indicated that you let it attempt to start for
quite some time on the small cord. This means that the thermal
overload had to operate every minute or so over an extended period
of time. The little boogers can't take more than a few dozen cycles
before failure.
To check, take the cover off the AC and find where the wires enter
the compressor. there'll be a bakelite lid held on with spring
clips. Pop those loose and remove the cover. You'll see the three
wires going into the compressor housing and right beside it will be
a round bakelite device about an inch in diameter. Usually labeled
with the Klixon brand. The common lead of the compressor will go
through this device. If it's not physically burned up, check it
with an ohmmeter. Should get continuity between the terminals. If
not, replace it. Cost is cheap - $10-15 retail. Be sure to get the
exact replacement. These things are designed to have similar
thermal characteristics as the motor windings and are matched to the
compressor model. A wide range of Klixons look alike. The part
number printed on the top tells the story.
If you do have continuity, then you have to look elsewhere. While
you have the lid off the compressor, check it out. Put one lead on
the common wire going into the compressor. This is the one that goes
through the Klixon and is usually black. Measure the ohms to the
other two terminals. One terminal should have about 1/2 to 1/3 the
resistance of the other. The higher resistance is the start
winding. For a compressor of this size, the value will be in the
2-10 ohm range. If one is open or zero ohms, bye bye compressor.
Next check to ground from all three terminals. Any continuity and
bye bye compressor.
If you've gotten this far with no obvious problem, hook one side of
your meter to ground and set it to AC volts. Have someone turn the
unit on. Check the two compressor terminals for voltage. Should be
near 120 volts. Check the compressor common. Should be near
ground. If you have voltage on the common, check the other side of
the Klixon. If there is voltage across the klixon, then it is
failing under load. If you have voltage on the compressor terminals
and it isn't running, probably new compressor time. Note that if
the thing is locked up or the starting device is bad (cap, relay or
both), the klixon will open fairly rapidly so you have to make your
measurements fast.
If you don't have full voltage, then it's time to work backwards.
the power switch is a good place to look, as is the thermostat. On
my coleman, the thermostat is very rugged but the power switch looks
quite flimsy. I'd look at it first. Tracing it all out with your
ohmmeter is quite straightforward.
--
John De Armond
johngd...@bellsouth.net
http://personal.bellsouth.net/~johngd/
Neon John's Custom Neon
Cleveland, TN
"Bendin' Glass 'n Passin' Gas"
Thanks again,
Todd
Many of these units also have a control package consisting of assorted
relays and a transformer for the low voltage control circuit. Under the
lid covering these devices you will, in most cases, find a schematic
showing which wire goes where and what that relay, device does.
Use caution as 120 VAC can kill.
As a last resort, if the compressor checks out ok with the resistance
and voltage tests John outlined and the unit will still not run, an HVAC
tech can "rock" the compressor by attempting to alternately start it
backwards and forwards. This will often break loose a stuck compressor.
No guarantees on how long it will last however.
Best
Mike N
Ok, now let's tell 'em how to do it. Get a KickStarter (hard start
kit) from the HVAC supply store and install according to
instructions. This provides extra torque. Then reverse the "start"
and "run" leads on the compressor (those two wires other than the
common one) and attempt to start it. Only for a few seconds. This
tries to start the compressor backwards which will hopefully
dislodge whatever is sticking it but the smaller starting winding is
now the run winding. It can't take more than a few seconds of this
sort of duty. I usually try alternating starting reversed and
straight before I give up and yank the compressor.
John