Anyone know where I can get some ideas as to what might be causing
my RV Roof A/C units to dump a 20 amp breaker when the air temp
gets up a little over 100 degrees? The front one started it a couple
of years ago and I measured the current draw. It started out at 15
amps and slowly climbed up to 20. The rear one held steady at 15
amps no matter what the temp. Now the rear one is doing the same
thing. I swapped all the caps, relays, etc when the back one was
working ok and that had no effect. At one time I thought maybe it
was an overcharge because someone has put valves on the front one.
The back one has no valves. But now that the back one has started
doing the same thing it can't be an overcharge. Any ideas appreciated.
Thanks.

Geo.

--

Technobarbarian

unread,
Jun 7, 2000, 3:00:00 AM6/7/00
to
In article <8hmld8$sfc$1...@news.asu.edu>, geo...@aztec.asu.edu

(GEORGE R. COONEY) wrote:
>
>Anyone know where I can get some ideas as to what might be
causing
>my RV Roof A/C units to dump a 20 amp breaker when the air temp
>gets up a little over 100 degrees?

I'd go back and look at the "Too Hot for A/C!!" thread that
Deborah Tucker stared on May 29. In amongst the pissin' and
moanin' you may find your answer. Sounds like you're sharp
enough that you already checked to be sure you've got good air
flow through the things and you haven't got air filters that are
loaded with gunk. If they're corroded or very dirty, cleaning
and straightening the outside evaporator fins can help a little
bit, but isn't likely to be the problem.

Dennis

* Sent from RemarQ http://www.remarq.com The Internet's Discussion Network *
The fastest and easiest way to search and participate in Usenet - Free!


Neon John

unread,
Jun 7, 2000, 3:00:00 AM6/7/00
to

"GEORGE R. COONEY" wrote:
>
> Anyone know where I can get some ideas as to what might be causing
> my RV Roof A/C units to dump a 20 amp breaker when the air temp

> gets up a little over 100 degrees? The front one started it a couple
> of years ago and I measured the current draw. It started out at 15
> amps and slowly climbed up to 20. The rear one held steady at 15
> amps no matter what the temp. Now the rear one is doing the same
> thing. I swapped all the caps, relays, etc when the back one was
> working ok and that had no effect. At one time I thought maybe it
> was an overcharge because someone has put valves on the front one.
> The back one has no valves. But now that the back one has started
> doing the same thing it can't be an overcharge. Any ideas appreciated.
> Thanks.

If you're where the sun is shining on the condenser (Arizona, duh!),
the behavior is probably normal. Once the condenser temperature
reaches 150 degrees or so, an R-22 system is pretty much lost. The
condensing pressure is so high the compressor can't deal with it.
The critical temperature for 22 is about 205 degs. The pressure
rises dramatically as the temperature approaches the critical temp.
Here's an example. At a condensing temperature of 120 degrees
(pretty normal around here for 90 deg weather), the pressure is 260
psi. At 150 degrees, the pressure is 382 psi. Try to contemplate a
single stage compressor trying to pump 70 psi gas all the way up to
almost 400 psi.

This is why R-22 is never used in automotive systems. I was quite
surprised to see it in roof-top units.

The only way to know whether this is the problem is to measure the
condensing temperature and pressure if there's a test fitting. A
thermocouple stuck in the fins near the hot gas inlet will do. Even
better is a thermocouple stuck to the hot gas tube headed from the
compressor to condenser. A small round dial-type thermometer as
used to check food temperature will work in a pinch.

If your condensing temperature is much above 120 degrees, there are
several remedies, all aimed toward keeping heat off the condenser.

1) make sure the fan is running at full speed. As the fan motor
bearings wear out and the rotor gets out of center in the stator, it
will slow until it finally stalls. You pretty much need some sort
of optical tach to determine this. Measuring the fan current draw
and comparing to nameplate will give some indication.

2) clean the condenser. Not only will more air flow but the natural
finish of the aluminum will reflect off heat better than the dark,
dirty surface.

3) Shield the condenser from direct sunlight. The Maxxair
replacement cover does a fairly decent job of this by interposing a
white plastic grill in front of the condenser. Some sort of
improvised shielding is also possible.

4) since someone installed a service valve, the unit could be
overcharged. There's an easy way to check. During normal
operation, there should be liquid freon in the last row or two of
condenser tubing at the bottom but no higher. Liquid freon conducts
away heat much faster than vapor. Therefore to figure out where the
liquid level is, simply heat the "U" turns on the condenser for a
few seconds with a propane torch and then feel the tube. A tube
containing liquid will not have heated. A tube with gas in it will
be hot for a few seconds before the flow cools it again.

I kinda doubt that it is overcharged if it's working OK otherwise.
I suspect that it is simply overheating.

John

--
John De Armond
johngd...@bellsouth.net
http://personal.bellsouth.net/~johngd/
Neon John's Custom Neon
Cleveland, TN
"Bendin' Glass 'n Passin' Gas"

LOCOMOTIVE2506

unread,
Jun 8, 2000, 3:00:00 AM6/8/00
to
Did you happen to measure the voltage right at the air conditioner when it was
drawing 20 amps or so? That current is too high even for the large roof mounts.
It almost sounds like the voltage is slowly dropping as wiring warms up.

WBucha

unread,
Jun 8, 2000, 3:00:00 AM6/8/00
to
I would pull the outside cover and blow out the evaporator core in the reversed
direction that the air flows (that is from the inside out) you will be
surprised how much dirt comes out.
Because the evap can't extract the heat from the refrigerant you are putting a
extreme load (high pressure) on the compressor in turn making the compressor
work much harder and drawing more current.

Bill

AI Nut

unread,
Jun 8, 2000, 3:00:00 AM6/8/00
to
Undercharging could also cause the symptoms you describe. Maybe you
have lost refrigerant over time.

AI Nut


"GEORGE R. COONEY" wrote:
>
> Anyone know where I can get some ideas as to what might be causing
> my RV Roof A/C units to dump a 20 amp breaker when the air temp
> gets up a little over 100 degrees? The front one started it a couple
> of years ago and I measured the current draw. It started out at 15
> amps and slowly climbed up to 20. The rear one held steady at 15
> amps no matter what the temp. Now the rear one is doing the same
> thing. I swapped all the caps, relays, etc when the back one was
> working ok and that had no effect. At one time I thought maybe it
> was an overcharge because someone has put valves on the front one.
> The back one has no valves. But now that the back one has started
> doing the same thing it can't be an overcharge. Any ideas appreciated.
> Thanks.
>

> Geo.
>
> --

mikey

unread,
Jun 8, 2000, 3:00:00 AM6/8/00
to
something similar happened to me when moving to Vegas last year. it was 124 degrees and they both tripped breakers.
had a RV tech CLEAN both units and no more tripping breakers.
 
that is take the roof covers off and give them a good scrubbing.
 