On 12/11/2012 14:06, The Natural Philosopher wrote:
> On 12/11/12 09:47, simonw91 wrote:
>> Morning all
>>
>> EDIT
>>
>> This problem has been resolved.
>>
>> Could anyone help a complete novice out with a problem he's having with
>> the above boiler?
>> Bled the radiator in the bedroom and now the pressure gauge on the
>> boiler is reading 0 bar and doesn't want to fire up.
>> No central heating or hot water but when the water / heating is turned
>> on there is hum from the device which may or may not be the fan and when
>> the hot taps are turned on it sounds like it should fire but doesn't.
>>
>> Any help would be appreciated
>>
>> Simon
>>
>>
>>
>>
> re pressurise the boiler, dear boy.
>
> There should be a tap and a link pipe that you can turn on
> somewhere..may need reconnecting.
>
>
And don't be tempted to leave it open; there should be a pressure gauge
or possibly a digital display on the boiler. Pressurise it to just over
the minimum (because the pressure will also rise as it heats up, and you
don't want to lift the relief valve).
--