Do you have a manual?
What are the reasons that the 'reset button comes on'?
--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Is this a new installation, and has it *ever* worked properly?
A common cause of lockout is overheating due to the residual heat not being
carried away after the boiler stops firing. Does this boiler require pump
over-run? If so, has the pump been wired correctly, so as to be controlled
by the boiler? Does the water *always* have somewhere to go? [If it's an
S-Plan system, or Y-Plan with TRVs on virtually all radiators, it probably
needs a by-pass circuit. Is there one and, if so, is the by-pass valve
correctly adjusted?]
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!
> Can anyone advise me on a problem I am having with the said boiler as
> the reset button keeps coming on after short periods. I have check the
Do you mean the lockout light comes on? If so is it steady or flashing?
(most Baxi installation manuals have fault finding flow charts in them)
--
Cheers,
John.
/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/
No idea if they are comparable, but I have placed a installation manual
for a 100 HE here:
http://www.internode.co.uk/temp/Baxi 100 HE.pdf
If that looks like it might be a more powerful version of your boiler,
the same fault finding charts on page 36 onward may help.
>> http://www.internode.co.uk/temp/Baxi 100 HE.pdf
>>
>> If that looks like it might be a more powerful version of your boiler,
>> the same fault finding charts on page 36 onward may help.
>>
> Sorry John, the web page was not available. Will try again later. Thanks
> for your help
Make sure your news reader is not breaking the link at the space. If
needs be try this:
http://www.internode.co.uk/temp/Baxi%20100%20HE.pdf
Albatross