Hi,

I've just fitted a built in hob in my new kitchen.

I rang up the plumber today to arrange for him to connect to the gas
up, and double checked with him the requirements for ventilation.

Apparently, as the room is between 5m2 and 10 m2, I need a 50 cm2
ventilator to the outside world, as I have an outside opening window,
but no outside opening door, as per bs5440 part 2.

I've done a search of google, but I can't find anywhere that sells a
50cm2 ventilator, only much bigger ones.

I'd rather get one as small as possible to reduce noise/ drafts etc.

Am I missing something here?

Thanks

auct...@sheldononline.co.uk

unread,
Nov 23, 2009, 4:17:16 PM11/23/09
to

http://www.vents.co.uk/background.asp

A 9 x 3 brick shaped set would be just under, a 125mm core vent would
be just over. The baffled air core (AC7HM) is 50.44cm2, which is
probably as close as you'll get!

They sell direct if you phone them, and are very helpful and
efficient.

A

Heliotrope Smith

unread,
Nov 23, 2009, 5:55:32 PM11/23/09
to

http://www.vents.co.uk/background.asp

A 9 x 3 brick shaped set would be just under, a 125mm core vent would
be just over. The baffled air core (AC7HM) is 50.44cm2, which is
probably as close as you'll get!

They sell direct if you phone them, and are very helpful and
efficient.

A very good site. I have bookmarked that one.

However, gas appliance ventilation must be permanent, that is not hit or
miss or capable of being shut off or reduced.

It must be fully open at all times (and insect screens are not permitted).

Turn to the plumbing page for suitable vents.


xscope

unread,
Nov 23, 2009, 6:09:01 PM11/23/09
to
Thanks - I'll give them a call in the morning