What the man told you is essentially correct.
Local hot spots in the boiler let the water boil and what you hear is
stem bubbles collapsing as they cool. (Cavition)
There is a minimum water flow through your boiler, if you go below it,
local hot spots can appear inside the boiler.
If the boiler is piped up "traditionally" as the thermostatic radiator
valves close, water flow is reduced through your boiler which can
cause this problem.
If the pumpis on the return side of the boiler, it reduces water
pressure inside the boiler exacerbating the problem.
The solution is to fit a spring-loaded "bypass" valve which is opened
by the rise in pressure as the thermostatic rad. valves close, so
keeping water going through the boiler.
Example here.
http://www.screwfix.com/p/honeywell-straight-auto-bypass-valve-22mm/34127
It will also let your TS rad valves function better.