On 5/26/2015 5:12 PM, KenO wrote:
Excellent information on surges and surge protection is at:
http://www.lightningsafety.com/nlsi_lhm/IEEE_Guide.pdf
- "How to protect your house and its contents from lightning: IEEE guide
for surge protection of equipment connected to AC power and
communication circuits" published by the IEEE in 2005 (the IEEE is a
major organization of electrical and electronic engineers).
And also:
http://pml.nist.gov/spd-anthology/files/Surges_happen!.pdf
- "NIST recommended practice guide: Surges Happen!: how to protect the
appliances in your home" published by the US National Institute of
Standards and Technology in 2001
Both guides are from reliable sources.
The IEEE surge guide is more technical.
I wouldn't rely on the testing that was done. There are standard tests
for surge protectors - 600V is not one of them (6,000V is). And I have
no idea if their test is representative of a surge. There is related
information on UL testing in the IEEE surge guide under "2.2.3 Surge
Limiting Voltage"
The vast majority of surge protectors use MOVs as the voltage limiting
element (over 90% according to the IEEE surge guide). These protectors
do not use MOVs. I have not seen them evaluated by a reliable
independent agency, and I would not use them. They, of course, claim to
be better than the MOV based ones. Some of their arguments are downright
stupid.
Westom is an internet nut that googles for "surge" to spread his ideas
about protection. He has joined an astonishing number of forums to
spread his ideas. Some of them are good, some not-so-good, and some are
complete nonsense. Everything he says about plug-in protectors is
complete nonsense. How can you tell? Westom says plug in protectors
don't work. Both the IEEE and NIST guides say they are effective.
I am "bud". I got tired of westom's crap after seeing it on several
Usenet groups I watch over a short period. I have nothing to do with the
surge protection industry other than I am using a couple protectors. A
lot of what I wrote here comes from the IEEE and NIST surge guides
w_tom is a name that westom used to use. More nonsense.
I have not read either of these threads.
>
> I do not have a technical background so would be interested in others comments concerning all this.
>
> Would like to use your advice to build a cost effective audio protection system.
>
> Thanks
>
> Ken
If using a plug-in protector all interconnected equipment needs to be
connected to the same protector. External connections, like coax also
must go through the protector. As explained in the IEEE surge guide
(starting page 30) plug-in protectors work primarily by limiting the
voltage from each wire to the ground at the protector. To do that all
wires must go through the protector.
The NIST surge guide suggests most equipment damage is from high voltage
between power and signal (phone, cable,...) wires. Computer and video
equipment is likely more at risk than audio. And it depends on where you
are. Some parts of the US have significant surge exposure. The major
cause of damaging surges is lightning. Normal and abnormal utility
operations can also cause damaging surges.
The author of the NIST surge guide looked at the surge current that
might come in on power wiring (US). The source was a 100,000A lightning
strike to a utility pole adjacent to a house with typical urban overhead
power distribution. Only 5% of strikes are more powerful and this is,
for practical purposes, the worst case. The surge current was 10,000A
per wire. Service panel protectors with much higher ratings are readily
available. High ratings mean long life. A service panel protector is
likely to protect anything connected only to power wiring (most audio
systems?)
The author of the NIST surge guide also investigated how much energy
might be absorbed in a MOV in a plug-in protector. Branch circuits were
10m and longer, and the surge on incoming power wires was up to 10,000A
(wort case, as above). The maximum energy at the MOV was a surprisingly
small 35 joules. In 13 of 15 cases it was 1 joule or less. There are a
couple simple reasons the energy is so low (one of which may be
particular to US wiring). Any UL listed protector in the US will have
ratings higher than that, and much higher ratings are readily available
(as in your first link). Again high ratings mean long life.
(Neither service panel or plug-in protectors protect by absorbing a
surge. They do absorb some energy in the process of protecting. And
protection from a direct strike to a building requires lightning rods.)
In the US, since 1998 UL has required thermal disconnects for
overheating MOVs. (With world markets they are probably included by all
competent manufacturers everywhere.) APC had an engineering error
resulting in a recall.
The IEEE surge guide describes how the protected equipment can be
connected across the MOVs, or be connected across the incoming power
wires. If connected across the MOVs, the protected equipment will be
disconnected on failure. (That is one reason why manufacturers can have
protected equipment warranties.) I think the IEEE surge guide says UL
requires protectors to state if they do not disconnect the protected
load with the MOVs.)
It would be nice if you could compare protectors based on joule rating.
The IEEE surge guide explains that (US) there is not a standard way of
measuring this, so some manufacturers have misleading ratings. Some
other (reliable) manufacturers responded by not including joule ratings.