You certainly have this rather heavily cross-posted. I'm following up
in rec.crafts.metalworking, and I'm assuming that you are planning to
run a machine tool from this. You may get vastly different replies from
the different newsgroups -- or just plain ignored. (Probably the
sci.electronics.design and sci.electronics.equipment newsgroups, as this
seems a bit off topic for them, just based on the newsgroup name.) If I
had any idea where you were reading it, I would restrict followups to
rec.crafts.metalworking where I am.
On 2014-02-11, DaveC <
inv...@invalid.net> wrote:
> Imagine you are asked to install a used buck-boost transformer. Imagine you
> could normally do this in a few minutes. Except if the leads were cut short
> such that identifying characters on the leads' insulation were missing.
O.K. Any color coding of the leads, or are they all black (tar
in braided covering)?
> Identifying 2 leads belonging to any one winding is straightforward ohm meter
> work. Maybe use of a ESR meter might help separate the X windings from the H
> windings?. But identifying which specific winding is which and which end is
> which限not so straightforward. For me.
Plain resistance measurements should be sufficient. I'm not
familiar with the X and H designations, and certainly not two of each
(unless it is designed for operation at two main voltages, like 120V or
240V -- or perhaps 240V or 480V. Isn't an ESR meter intended for
measuring the resistance in a capacitor, not a transformer?
> How would you go about identifying the windings? Maybe use a Variac to input
> voltage to each of the windings then measure the output of the others? What
> outputs should I expect at, for example, the H3/H4 winding with a voltage on
> H1/H2 winding? How to identify backward connection of a winding?
>
> Are the two H windings identical? The two X windings?
Assuming that it is for dual input voltages such as I suggested
above -- the two input windings would be the same resistance, and would
be connected in parallel for the lower voltage or in series for the
higher voltage.
> Suggestions welcome.
>
> This is a 208 -> 230 (ie, 12 & 24 v buck-boost voltage) single-phase
> autotransformer in N. America.
For the transformation shown, you should only need two windings
total -- again unless it is also intended for operation at an input
voltage twice or half the 230/208 nominal range. Three windings to get
your choice of 12V or 24V buck or boost.
Anyway -- for two total windings, I would expect one to have
significantly higher resistance than the other (and for two of each
winding, two would have significantly higher resistance than the other
two. Since the input and output are expected to handle about the same
current, they should be wound with the same wire gauge, and thus the
resistances would be about proportional to the voltages on each winding.
Given two -- pick one of the higher resistance windings and
connect it to the line (or through a Variac autotransformer set to half
voltage if the transformer is for both 120 and 240 range inputs.
Connect one end of the other higher resistance winding to one of the two
ends being connected to the line. Take an AC voltmeter, and connect
between the free lead and the remaining line input lead. If the voltage
measures about twice the line voltage, swap the free lead and the other
from that winding, and re-measure. You should measure something close to
zero (probably no more than a volt or two). Now -- mark the two which
are connected together as "S" (start), and the free end and the one
connected just to the other line input as "F" (finish). For the lower
voltage input range -- connect both "S" ends together to one side of the
line, and both "F" ends together to the other side of the line. For the
higher (say 230 VAC if it is a 230/460 volt transformer) you connect one
'S' to the 'F' of the other widing, and use the other two free ends (one
'S' and one 'F') to the line input.
If you want to determine whether the dual voltage is 115/230 or
230/460 Volts, take one of the input (higher resistance) windings, and
connect it to the 230 V with a 100 Watt 120 VAC light bulb in series.
If it lights brightly then 230 VAC is too much for one winding (it is
saturating the core) and you need the two in series.
Now -- that the input wires are sorted out, we move to the
output wires. Connect one end of each output winding to the other
output winding -- and measure the voltage both between the joined pair
of wires and each end -- they should give you your 12V AC. And if you
then measure between the two free ends and get 24VAC, swap ends on one
winding and check again for a very low voltage. At this point, you have
connected together either a 'S' for each of the secondary windings, or a
'F' for each. To determine which, connect the joined point to the side
of the input power connected to the wires marked 'F' (along with having
your input power going to the primary windings as determined above).
Now -- measure the voltage first between the two primary windings, and
then from the end to which your secondary windings is *not* connected,
to a free wend of the secondary winding. If the voltage measured is
lower than your input voltage, then mark the two joined secondary ends
as 'F', while if the voltage is higher, then mark the joined secondary
ends as 'S'. (Of course, mark each as to which winding it is connected
to. Being unfamiliar with the 'X' and 'H' designations, I would
personally mark them as "P1S", "P1F" "S1S" and S1F" (first of those is
"Primary 1 Start)", and similarly for S2 and P2.
Now -- to *use*, when you want to reduce the voltage (buck),
connect your input power to the primary start and finish wires (either
in parallel for the lower voltage range, or in series for the higher
voltage range), and connect the 'F' wires from the secondary to the 'F'
wires from the primary, so you will subtract 12 V from the 230 V or 24
V from the 460 V) and connect the load to the 'S' wires of the
secondary.
If you want to boost instead of buck, connect the 'S' of the
secondary to the 'F' of the primary, and the 'F' of the secondary to the
load.
If you want to buck or boost by 24V instead, use the two
secondary windings in series (one 'F' to the other winding's 'S', and
threat the free wires as the overall 'S' and 'F' wires. Hopefully, the
secondary wires will handle the series operation while the primary is in
parallel connection.
Be Careful and
Good Luck,
DoN.
--
Remove oil spill source from e-mail
Email: <
BPdnic...@d-and-d.com> | (KV4PH) Voice (all times):
(703) 938-4564
(too) near Washington D.C. |
http://www.d-and-d.com/dnichols/DoN.html
--- Black Holes are where God is dividing by zero ---