On 10/22/2022 11:57 PM, John Crane wrote:
> It's a 12-181b.
>
> As luck would have it, it came with a little paper schematic and user's
> guide tucked in the battery compartment....attaching a jpg of it.
>
>
>
Below is a relatively long post concerning a lower probability
cause of the problem than the cube itself. It was mentioned
earlier, but dismissed when it should not have been. I'm
posting this because there is a small possibility that there
is a safety issue in your home.
You have NOT eliminated all possibilities of EMI/RFI
Walk it down the road, as was mentioned. That is, take
it somewhere to a place far away from any power lines,
houses, buildings etc where electrical devices are.
If it still buzzes then you know the problem is within
the cube. Sources of EMI/RFI can be in a nearby neighbor's
house, a power line fault such as a cracked insulator
or even a loose connection in the wiring in your house.
It doesn't have to be a new electrical device in your
house, even though that is a most likely cause in many
cases.
If the cube works properly when walked down the road,
but starts buzzing as you near your house, use it as
a detector to try to locate the source - perhaps a
power line or a neighbor's house. If the source is
something in your house, you can shut off breakers
until you determine which circuit "hosts" the noise
making device, then further isolate by restoring power
to the circuit and unplugging/switching off one device
at a time. Don't overlook devices that you cannot
switch off like doorbell or thermostat transformers
hard wired devices and so forth. If the problem is
not found in any device you can unplug or switch off,
it could be a loose connection in the wiring. That
is serious, as a fire could result.
I hope diagnosis/fix turns out to be simple and
does not involve safety at all. Good hunting!
Ed