In sci.electronics.repair Gary Walters <
gwp...@yahoo2.cz> wrote:
> In USA.
>
> Source: 208v, 60 hz, 2-wire (2 phases from 3 phase "Y" supply). Load: 240v,
> 20A.
>
> I presumed that sizing a buck-boost transformer is simple KVA math (source
> volts * load amps). But...
>
> This PDF document:
>
> <
http://www.acmepowerdist.com/pdf/Page_104-109.pdf>
>
> on the last page says:
> - - -
> "An example of an everyday application is always a good way to explain the
> intent of the ?Code.? Example: A 1 kVA transformer Catalog No. T111683 has a
> primary of 120 x 240V and a secondary of 12 x 24V. It is to be connected as
> an autotransformer at the time of installation to raise 208V to 230V single
> phase.
>
> When this 1 kVA unit is connected as an autotransformer for this voltage
> combination, its kVA rating is increased to 9.58 kVA (may also be expressed
> as 9,580 VA). This is the rating to be used for determining the full load
> input amps and the sizing of the overcurrent protect device (fuse or breaker)
> on the input.
>
> Full Load Input Amps =
> 9,580 Volt Amps / 208 Volts = 46 Amps"
> - - -
> I'm puzzled by the 10x increase of KVA rating. When and how is this true?
It's true because you're only using the transformer to "create" 24 volts at the current you wish
to draw at 230v. This extra 24 volts is added back into the line voltage.
You can switch flip the leads and subtract voltage too, then the transformer is in buck mode.
> What size B-B transformer do I need?
>
> Thanks.
If you need 20 amps at 230v and start with 208, you need to boost 22volts (208+22=230) x 20 amps
= 480VA transformer. A 24 volt transformer rated over 480VA should be fine.
Autotransformers can be confusing, so pretend it's just DC and some batteries.
Let's say you need 24 volts at 10 amps and have a 12 volt battery that can already output 10
amps.
what size power supply do you need to run in series with this battery to get the 24 volts?
just another 12 volts, at at least 10 amps, or a 120 watt power supply. Those wired in
series (your battery and the new power supply) will provide 240 watts.
If you already had an 18 volt battery, you'd just need a 6 volt, 10 amp or 60 watt power supply.
The less the voltage adjustment, the smaller then buck/boost transformer rating becomes as it's
really not doing all that much work.