<jlar...@highlandtechnology.com> wrote:
>If the line voltage stays sinusoidal, there is no true power in the
>current harmonics. But lots of wire losses, which will annoy the power
>company.
The problem with harmonics is that the AC power meters are not very
good at measuring the power in the harmonics. In the power biz,
failure to pay for power is a serious problem. If PG&E were to
deliver square wave instead of sine wave power, 1/3 of the power would
be in the harmonics.
>There have been office fires from all those old non-PFC PCs frying the
>neutral wires in partition wiring. The wiring was sized assuming that
>phase currents in neutral would mostly balance, but they don't for the
>spikes from switching power supplies.
That's usually the official excuse when the insurance company wants to
pass the blame for a fire to the building owner or electrical
contractor and thus avoid paying for the fire damage. The thermal
circuit breaks should|would have tripped long before any danger of
fire.
In the US, the neutral wire is sized to carry the maximum current of
ONE of the two phases. This way, if one phase is loaded to maximum,
and the other has no load, the system would still be safe. With such
a neutral, I don't see how PF changes can create exessive current in
the neutral wire in a 2 phase residential system.
Things are not so convenient with 3 phase power, where the maximum
neutral current is 1.73 times the current in each phase. That can
cause problems, but certainly will not burn down the building. The
article below suggests that for 3 phase power, the neutral is sized at
125% of the current in each phase, but lacking the time to dig through
the NEC code book, I'm not certain that's the correct number.
On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
wrote:
>On Fri, 09 Nov 2012 12:09:57 -0800, John Larkin
><jlar...@highlandtechnology.com> wrote:
>>If the line voltage stays sinusoidal, there is no true power in the
>>current harmonics. But lots of wire losses, which will annoy the power
>>company.
>The problem with harmonics is that the AC power meters are not very
>good at measuring the power in the harmonics. In the power biz,
>failure to pay for power is a serious problem. If PG&E were to
>deliver square wave instead of sine wave power, 1/3 of the power would
>be in the harmonics.
But there's no power in the current harmonics.
>>There have been office fires from all those old non-PFC PCs frying the
>>neutral wires in partition wiring. The wiring was sized assuming that
>>phase currents in neutral would mostly balance, but they don't for the
>>spikes from switching power supplies.
>That's usually the official excuse when the insurance company wants to
>pass the blame for a fire to the building owner or electrical
>contractor and thus avoid paying for the fire damage. The thermal
>circuit breaks should|would have tripped long before any danger of
>fire.
Not many people put breakers in the neutral wires.
>In the US, the neutral wire is sized to carry the maximum current of
>ONE of the two phases. This way, if one phase is loaded to maximum,
>and the other has no load, the system would still be safe. With such
>a neutral, I don't see how PF changes can create exessive current in
>the neutral wire in a 2 phase residential system.
>Things are not so convenient with 3 phase power, where the maximum
>neutral current is 1.73 times the current in each phase. That can
>cause problems, but certainly will not burn down the building. The
>article below suggests that for 3 phase power, the neutral is sized at
>125% of the current in each phase, but lacking the time to dig through
>the NEC code book, I'm not certain that's the correct number.
The classic wire sizing assumes that current from the three phases
will cancel into the neutral. When the current is dominated by higher
harmonics, namely big current spikes at the peak of each sine wave,
they add up; they don't cancel because they are not simultaneous in
time.
Precision electronic instrumentation
Picosecond-resolution Digital Delay and Pulse generators
Custom laser drivers and controllers
Photonics and fiberoptic TTL data links
VME thermocouple, LVDT, synchro acquisition and simulation
On Tue, 13 Nov 2012 13:56:10 -0800, John Larkin <jlar...@highlandtechnology.com> wrote:
>On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
>wrote:
>>On Fri, 09 Nov 2012 12:09:57 -0800, John Larkin
>><jlar...@highlandtechnology.com> wrote:
>>>If the line voltage stays sinusoidal, there is no true power in the
>>>current harmonics. But lots of wire losses, which will annoy the power
>>>company.
>>The problem with harmonics is that the AC power meters are not very
>>good at measuring the power in the harmonics. In the power biz,
>>failure to pay for power is a serious problem. If PG&E were to
>>deliver square wave instead of sine wave power, 1/3 of the power would
>>be in the harmonics.
>But there's no power in the current harmonics.
>>>There have been office fires from all those old non-PFC PCs frying the
>>>neutral wires in partition wiring. The wiring was sized assuming that
>>>phase currents in neutral would mostly balance, but they don't for the
>>>spikes from switching power supplies.
>>That's usually the official excuse when the insurance company wants to
>>pass the blame for a fire to the building owner or electrical
>>contractor and thus avoid paying for the fire damage. The thermal
>>circuit breaks should|would have tripped long before any danger of
>>fire.
>Not many people put breakers in the neutral wires.
>>In the US, the neutral wire is sized to carry the maximum current of
>>ONE of the two phases. This way, if one phase is loaded to maximum,
>>and the other has no load, the system would still be safe. With such
>>a neutral, I don't see how PF changes can create exessive current in
>>the neutral wire in a 2 phase residential system.
>>Things are not so convenient with 3 phase power, where the maximum
>>neutral current is 1.73 times the current in each phase. That can
>>cause problems, but certainly will not burn down the building. The
>>article below suggests that for 3 phase power, the neutral is sized at
>>125% of the current in each phase, but lacking the time to dig through
>>the NEC code book, I'm not certain that's the correct number.
>The classic wire sizing assumes that current from the three phases
>will cancel into the neutral. When the current is dominated by higher
>harmonics, namely big current spikes at the peak of each sine wave,
>they add up; they don't cancel because they are not simultaneous in
>time.
On Tue, 13 Nov 2012 14:56:51 -0500, rickman <gnu...@gmail.com> wrote:
>On 11/9/2012 7:10 PM, John Larkin wrote:
>> On Fri, 09 Nov 2012 15:50:51 -0500, rickman<gnu...@gmail.com> wrote:
>>> So then you are agreeing that power can be negative. The fact that your
>>> meters are incapable of representing this as a negative value is of no
>>> consequence to the concept of power.
>> All the meters that I've done can measure positive and negative power;
>> it's actually harder not to. Some, like apartment submeters, can only
>> accumulate positive KWHs. To my knowledge, no apartments at Battery
>> Park City sell power back to the utility.
>Your power meters are only useful in one city in the *world*?
BPC is the only residential submetering that I've done, about 1720
apartments, which keep having bad luck: 9/11, then this flood.
Submetering is a low-margin business, so I don't do it any more.
On Tue, 13 Nov 2012 15:07:47 -0500, rickman <gnu...@gmail.com> wrote:
>On 11/10/2012 2:39 PM, josephkk wrote:
>> On Thu, 08 Nov 2012 18:21:18 -0500, rickman<gnu...@gmail.com> wrote:
>>> On 11/7/2012 9:29 PM, josephkk wrote:
>>>> On Sat, 03 Nov 2012 21:50:43 -0400, rickman<gnu...@gmail.com> wrote:
>>>>> So why do they want to replace the disk meters with digital ones? You
>>>>> could add a VERY simple optical monitor to the disk meter to read the
>>>>> number of revolutions and provide all the other benefits of digital
>>>>> without the mess of the ADCs, etc. I suppose the old meters can be a
>>>>> bit more expensive than the fancy, dancy digital ones?
>>>>> Rick
>>>> Two things:
>>>> The way the certification process works.
>>> How does it work that precludes modification of existing meters?
>>>> They want new features that are not possible by just instrumenting
>>>> rotating disk types.
>>>> ?-)
>>> Such as???
>>> Rick
>> Remote turn-on / turn-off. Time of usage rate billing. Undoubtedly more.
>> ?-)
>I don't follow. If you add a digital back end to a rotating disk meter >you can add any of these features. So what features can't you add to a >rotating disk meter with a digital back end? Is the advantage that the >digital meters are less expensive?
Generally one wouldn't meter current (it would require a second pair
of CTs or shunts) and maybe not voltage, if the added register is
battery powered. The ones I've seen were basically a disk rotation
counter with LCD, battery powered, with one of those opticon readout
things. I guess one could do a disk meter with all the goodies behind
it.
If anybody knows of disk-based meters with all the fancy features,
please say so.
On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
wrote:
>In the US, the neutral wire is sized to carry the maximum current of
>ONE of the two phases.
Arrgh. It is the same phase in 120/240 V systems, NOT phases. Just
opposite ends of a single center tapped winding. Opposite polarity is
correct, and other hot ( / leg) is acceptable. I get twitchy on this
because i have to correct sparkies and dumball "engineers" on this all the
time.
120/208 V "single phase systems" are different. Other leg still applies.
>This way, if one phase is loaded to maximum,
>and the other has no load, the system would still be safe. With such
>a neutral, I don't see how PF changes can create exessive current in
>the neutral wire in a 2 phase residential system.
>>The problem with harmonics is that the AC power meters are not very
>>good at measuring the power in the harmonics. In the power biz,
>>failure to pay for power is a serious problem. If PG&E were to
>>deliver square wave instead of sine wave power, 1/3 of the power would
>>be in the harmonics.
>But there's no power in the current harmonics.
That is just plain wrong. Do the arithmetic. Oh wait, you are allergic
to that.
>>That's usually the official excuse when the insurance company wants to
>>pass the blame for a fire to the building owner or electrical
>>contractor and thus avoid paying for the fire damage. The thermal
>>circuit breaks should|would have tripped long before any danger of
>>fire.
>Not many people put breakers in the neutral wires.
There are a few legally mandated cases for doing so, and failure to do so
when mandated is a serious issue; get your ass sued off serious.
On Tue, 13 Nov 2012 15:07:47 -0500, rickman <gnu...@gmail.com> wrote:
>On 11/10/2012 2:39 PM, josephkk wrote:
>> On Thu, 08 Nov 2012 18:21:18 -0500, rickman<gnu...@gmail.com> wrote:
>>> On 11/7/2012 9:29 PM, josephkk wrote:
>>>> On Sat, 03 Nov 2012 21:50:43 -0400, rickman<gnu...@gmail.com> wrote:
>>>>> So why do they want to replace the disk meters with digital ones? You
>>>>> could add a VERY simple optical monitor to the disk meter to read the
>>>>> number of revolutions and provide all the other benefits of digital
>>>>> without the mess of the ADCs, etc. I suppose the old meters can be a
>>>>> bit more expensive than the fancy, dancy digital ones?
>>>>> Rick
>>>> Two things:
>>>> The way the certification process works.
>>> How does it work that precludes modification of existing meters?
>>>> They want new features that are not possible by just instrumenting
>>>> rotating disk types.
>>>> ?-)
>>> Such as???
>>> Rick
>> Remote turn-on / turn-off. Time of usage rate billing. Undoubtedly more.
>> ?-)
>I don't follow. If you add a digital back end to a rotating disk meter >you can add any of these features. So what features can't you add to a >rotating disk meter with a digital back end? Is the advantage that the >digital meters are less expensive?
>Rick
Certainly both of these and providing for co-generation (e.g. solar) is
much easier by just going all digital direct in the first place (also
cheaper which the utilities DO care about).
On Tue, 13 Nov 2012 15:14:30 -0500, rickman <gnu...@gmail.com> wrote:
>> The utility can claim that they are bound by their charter to meter the
>> electricity, and metering as well as bill-printing/mailing are business
>> expenses, not profit. They might be vulnerable, though, to the
>> claim that motor-type meters are more energy efficient than the
>> electronic ones (about 3W quiescent).
>Three watts seems pretty extreme to me. This is something that should >be doable for well under a quarter of a watt before power supply >inefficiencies are considered. I have no idea how they deal with that >however. In fact, the more efficient, switched power supplies will have >poor PF, lol! I believe I've read that there will be a requirement to >manage PF even on low wattage power supplies.
>Rick
Actually low watt PF corrected power supplies can be efficient, it is just
a different design. What is really difficult is near zero idle power and
short pulses of a fractional to a few watts. MPS430 based designs are
famous for this. Many sleepable uCs and uPs have this issue.
> On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann<je...@cruzio.com>
> wrote:
>> In the US, the neutral wire is sized to carry the maximum current of
>> ONE of the two phases.
> Arrgh. It is the same phase in 120/240 V systems, NOT phases. Just
> opposite ends of a single center tapped winding. Opposite polarity is
> correct, and other hot ( / leg) is acceptable. I get twitchy on this
> because i have to correct sparkies and dumball "engineers" on this all the
> time.
If we're considering sine waves with odd harmonics, why would it matter
if one talks of opposite polarity or 180 degrees phase difference?
> 120/208 V "single phase systems" are different. Other leg still applies.
>> This way, if one phase is loaded to maximum,
>> and the other has no load, the system would still be safe. With such
>> a neutral, I don't see how PF changes can create exessive current in
>> the neutral wire in a 2 phase residential system.
As John pointed out, if the load consists of rectifiers without
PF correction, the currents do not cancel in the neutral wire.
In fact, the current may end up to be the *sum* of the currents
in both hot wires.
<jlar...@highlandtechnology.com> wrote:
>On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
>wrote:
>>On Fri, 09 Nov 2012 12:09:57 -0800, John Larkin
>><jlar...@highlandtechnology.com> wrote:
>>>If the line voltage stays sinusoidal, there is no true power in the
>>>current harmonics. But lots of wire losses, which will annoy the power
>>>company.
>>The problem with harmonics is that the AC power meters are not very
>>good at measuring the power in the harmonics. In the power biz,
>>failure to pay for power is a serious problem.
>> If PG&E were to
>>deliver square wave instead of sine wave power, 1/3 of the power would
>>be in the harmonics.
>But there's no power in the current harmonics.
What if the users' equipment was a resistive heater load ? The square
wave wouldn't power that with all its might and use all the energy
to make heat ?
>>>There have been office fires from all those old non-PFC PCs frying the
>>>neutral wires in partition wiring. The wiring was sized assuming that
>>>phase currents in neutral would mostly balance, but they don't for the
>>>spikes from switching power supplies.
>>That's usually the official excuse when the insurance company wants to
>>pass the blame for a fire to the building owner or electrical
>>contractor and thus avoid paying for the fire damage. The thermal
>>circuit breaks should|would have tripped long before any danger of
>>fire.
>Not many people put breakers in the neutral wires.
>>In the US, the neutral wire is sized to carry the maximum current of
>>ONE of the two phases. This way, if one phase is loaded to maximum,
>>and the other has no load, the system would still be safe. With such
>>a neutral, I don't see how PF changes can create exessive current in
>>the neutral wire in a 2 phase residential system.
>>Things are not so convenient with 3 phase power, where the maximum
>>neutral current is 1.73 times the current in each phase. That can
>>cause problems, but certainly will not burn down the building. The
>>article below suggests that for 3 phase power, the neutral is sized at
>>125% of the current in each phase, but lacking the time to dig through
>>the NEC code book, I'm not certain that's the correct number.
>The classic wire sizing assumes that current from the three phases
>will cancel into the neutral. When the current is dominated by higher
>harmonics, namely big current spikes at the peak of each sine wave,
>they add up; they don't cancel because they are not simultaneous in
>time.
>On Tue, 13 Nov 2012 13:56:10 -0800, John Larkin
><jlar...@highlandtechnology.com> wrote:
>>On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
>>wrote:
>>>On Fri, 09 Nov 2012 12:09:57 -0800, John Larkin
>>><jlar...@highlandtechnology.com> wrote:
>>>>If the line voltage stays sinusoidal, there is no true power in the
>>>>current harmonics. But lots of wire losses, which will annoy the power
>>>>company.
>>>The problem with harmonics is that the AC power meters are not very
>>>good at measuring the power in the harmonics. In the power biz,
>>>failure to pay for power is a serious problem.
>>> If PG&E were to
>>>deliver square wave instead of sine wave power, 1/3 of the power would
>>>be in the harmonics.
>>But there's no power in the current harmonics.
>What if the users' equipment was a resistive heater load ? The square
>wave wouldn't power that with all its might and use all the energy
>to make heat ?
> (assume a low-inductance resistor)
>boB
My stipulation was
>>>>If the line voltage stays sinusoidal, there is no true power in the
>>>>current harmonics.
which falls out of the trig. Yet another reason why an electronic
power meter doesn't need a super-high sampling rate.
Of course, if the AC line were a square wave, things would be
different.
<jer...@nospam.please> wrote:
>On 2012-11-14 05:48, josephkk wrote:
>> On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann<je...@cruzio.com>
>> wrote:
>>> In the US, the neutral wire is sized to carry the maximum current of
>>> ONE of the two phases.
>> Arrgh. It is the same phase in 120/240 V systems, NOT phases. Just
>> opposite ends of a single center tapped winding. Opposite polarity is
>> correct, and other hot ( / leg) is acceptable. I get twitchy on this
>> because i have to correct sparkies and dumball "engineers" on this all the
>> time.
>If we're considering sine waves with odd harmonics, why would it matter
>if one talks of opposite polarity or 180 degrees phase difference?
>> 120/208 V "single phase systems" are different. Other leg still applies.
>>> This way, if one phase is loaded to maximum,
>>> and the other has no load, the system would still be safe. With such
>>> a neutral, I don't see how PF changes can create exessive current in
>>> the neutral wire in a 2 phase residential system.
>As John pointed out, if the load consists of rectifiers without
>PF correction, the currents do not cancel in the neutral wire.
>In fact, the current may end up to be the *sum* of the currents
>in both hot wires.
>Jeroen Belleman
That even applies to 120/240 center-tapped systems where the 120 volt
loads are 0 and 180 degrees. If the loads were half-wave diode
rectified, and each line was running at its rated max RMS current, the
neutral could be overloaded. Again, if the line currents don't overlap
in time they add into the neutral, not balance as would happen with
sinewave loads.
You could get the same effect with a resistive load on one side and a
capacitive load on the other. The orthogonal neutral currents wouldn't
cancel.
Precision electronic instrumentation
Picosecond-resolution Digital Delay and Pulse generators
Custom laser drivers and controllers
Photonics and fiberoptic TTL data links
VME thermocouple, LVDT, synchro acquisition and simulation
<jlar...@highlandtechnology.com> wrote:
>On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
>wrote:
>>Things are not so convenient with 3 phase power, where the maximum
>>neutral current is 1.73 times the current in each phase. That can
>>cause problems, but certainly will not burn down the building. The
>>article below suggests that for 3 phase power, the neutral is sized at
>>125% of the current in each phase, but lacking the time to dig through
>>the NEC code book, I'm not certain that's the correct number.
>The classic wire sizing assumes that current from the three phases
>will cancel into the neutral. When the current is dominated by higher
>harmonics, namely big current spikes at the peak of each sine wave,
>they add up; they don't cancel because they are not simultaneous in
>time.
While I very much doubt that the harmonics will actually burn down the
house, the (possibly urban legends) that the harmonics have burned the
neutral conductor in a cable, causing hazardous voltages appears to be
believable.
At higher distribution levels, it is assumed that the neutral current
will cancel out in a three phase system and thus, the neutral
connector might quite a lot weaker than the phase connector. In a
ground cable, the armoring around the phase conductors might act as
the neutral conductor. In a pole mounted cable system, three aluminum
phase connectors plus a steel cable servicing as the mechanical
strength as well as the neutral condition (assuming neutral conductor
canceling out).
However, if this canceling assumption is not true with electronics
load, the third harmonic current is far larger than initially assumed,
causing burn through of weak neutral conductors.
On Wed, 14 Nov 2012 23:13:58 +0200, upsided...@downunder.com wrote:
>On Tue, 13 Nov 2012 13:56:10 -0800, John Larkin
><jlar...@highlandtechnology.com> wrote:
>>On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
>>wrote:
>>>Things are not so convenient with 3 phase power, where the maximum
>>>neutral current is 1.73 times the current in each phase. That can
>>>cause problems, but certainly will not burn down the building. The
>>>article below suggests that for 3 phase power, the neutral is sized at
>>>125% of the current in each phase, but lacking the time to dig through
>>>the NEC code book, I'm not certain that's the correct number.
>>The classic wire sizing assumes that current from the three phases
>>will cancel into the neutral. When the current is dominated by higher
>>harmonics, namely big current spikes at the peak of each sine wave,
>>they add up; they don't cancel because they are not simultaneous in
>>time.
>While I very much doubt that the harmonics will actually burn down the
>house, the (possibly urban legends) that the harmonics have burned the
>neutral conductor in a cable, causing hazardous voltages appears to be
>believable.
Precision electronic instrumentation
Picosecond-resolution Digital Delay and Pulse generators
Custom laser drivers and controllers
Photonics and fiberoptic TTL data links
VME thermocouple, LVDT, synchro acquisition and simulation
> On Tue, 13 Nov 2012 15:07:47 -0500, rickman<gnu...@gmail.com> wrote:
>> I don't follow. If you add a digital back end to a rotating disk meter
>> you can add any of these features. So what features can't you add to a
>> rotating disk meter with a digital back end? Is the advantage that the
>> digital meters are less expensive?
>> Rick
> Certainly both of these and providing for co-generation (e.g. solar) is
> much easier by just going all digital direct in the first place (also
> cheaper which the utilities DO care about).
That's what I am asking. I haven't heard anyone say the digital meters are cheaper than the disk meters. Is that true?
The issue of solar is moot. When you add your solar collectors, if you want to feed into the grid you have to coordinate with the utility and they give you a special meter. My house *still* has the same disk meter it had 50 years ago.
> On Tue, 13 Nov 2012 15:14:30 -0500, rickman<gnu...@gmail.com> wrote:
>>> The utility can claim that they are bound by their charter to meter the
>>> electricity, and metering as well as bill-printing/mailing are business
>>> expenses, not profit. They might be vulnerable, though, to the
>>> claim that motor-type meters are more energy efficient than the
>>> electronic ones (about 3W quiescent).
>> Three watts seems pretty extreme to me. This is something that should
>> be doable for well under a quarter of a watt before power supply
>> inefficiencies are considered. I have no idea how they deal with that
>> however. In fact, the more efficient, switched power supplies will have
>> poor PF, lol! I believe I've read that there will be a requirement to
>> manage PF even on low wattage power supplies.
>> Rick
> Actually low watt PF corrected power supplies can be efficient, it is just
> a different design. What is really difficult is near zero idle power and
> short pulses of a fractional to a few watts. MPS430 based designs are
> famous for this. Many sleepable uCs and uPs have this issue.
On Wed, 14 Nov 2012 23:13:58 +0200, upsided...@downunder.com wrote:
>On Tue, 13 Nov 2012 13:56:10 -0800, John Larkin
><jlar...@highlandtechnology.com> wrote:
>>On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann <je...@cruzio.com>
>>wrote:
>>>Things are not so convenient with 3 phase power, where the maximum
>>>neutral current is 1.73 times the current in each phase. That can
>>>cause problems, but certainly will not burn down the building. The
>>>article below suggests that for 3 phase power, the neutral is sized at
>>>125% of the current in each phase, but lacking the time to dig through
>>>the NEC code book, I'm not certain that's the correct number.
>>The classic wire sizing assumes that current from the three phases
>>will cancel into the neutral. When the current is dominated by higher
>>harmonics, namely big current spikes at the peak of each sine wave,
>>they add up; they don't cancel because they are not simultaneous in
>>time.
>While I very much doubt that the harmonics will actually burn down the
>house, the (possibly urban legends) that the harmonics have burned the
>neutral conductor in a cable, causing hazardous voltages appears to be
>believable.
>At higher distribution levels, it is assumed that the neutral current
>will cancel out in a three phase system and thus, the neutral
>connector might quite a lot weaker than the phase connector. In a
>ground cable, the armoring around the phase conductors might act as
>the neutral conductor. In a pole mounted cable system, three aluminum
>phase connectors plus a steel cable servicing as the mechanical
>strength as well as the neutral condition (assuming neutral conductor
>canceling out).
>However, if this canceling assumption is not true with electronics
>load, the third harmonic current is far larger than initially assumed,
>causing burn through of weak neutral conductors.
At the old house (1969-1994) I had a (underground) neutral go
resistive. Furnace blower would come on and half the lights in the
house would dim, half would brighten.
I called APS and the token dumb blond lipped me.
I returned the compliment ;-) Which got me in direct touch with an
engineer.
They had a temporary (above-ground) neutral installed within the
hour... a cable about as thick as my wrist ;-)
...Jim Thompson
-- | James E.Thompson, CTO | mens |
| Analog Innovations, Inc. | et |
| Analog/Mixed-Signal ASIC's and Discrete Systems | manus |
| Phoenix, Arizona 85048 Skype: Contacts Only | |
| Voice:(480)460-2350 Fax: Available upon request | Brass Rat |
| E-mail Icon at http://www.analog-innovations.com | 1962 |
I love to cook with wine. Sometimes I even put it in the food.
> On 11/14/2012 12:37 AM, josephkk wrote:
>> On Tue, 13 Nov 2012 15:14:30 -0500, rickman<gnu...@gmail.com> wrote:
>>>> The utility can claim that they are bound by their charter to meter the
>>>> electricity, and metering as well as bill-printing/mailing are business
>>>> expenses, not profit. They might be vulnerable, though, to the
>>>> claim that motor-type meters are more energy efficient than the
>>>> electronic ones (about 3W quiescent).
>>> Three watts seems pretty extreme to me. This is something that should
>>> be doable for well under a quarter of a watt before power supply
>>> inefficiencies are considered. I have no idea how they deal with that
>>> however. In fact, the more efficient, switched power supplies will have
>>> poor PF, lol! I believe I've read that there will be a requirement to
>>> manage PF even on low wattage power supplies.
>>> Rick
>> Actually low watt PF corrected power supplies can be efficient, it is
>> just
>> a different design. What is really difficult is near zero idle power and
>> short pulses of a fractional to a few watts. MPS430 based designs are
>> famous for this. Many sleepable uCs and uPs have this issue.
>On 2012-11-14 05:48, josephkk wrote:
>> On Tue, 13 Nov 2012 13:07:59 -0800, Jeff Liebermann<je...@cruzio.com>
>> wrote:
>>> In the US, the neutral wire is sized to carry the maximum current of
>>> ONE of the two phases.
>> Arrgh. It is the same phase in 120/240 V systems, NOT phases. Just
>> opposite ends of a single center tapped winding. Opposite polarity is
>> correct, and other hot ( / leg) is acceptable. I get twitchy on this
>> because i have to correct sparkies and dumball "engineers" on this all the
>> time.
>If we're considering sine waves with odd harmonics, why would it matter
>if one talks of opposite polarity or 180 degrees phase difference?
Yes. Correct description of the situation is crucial to understanding
what is correct or incorrect operation.
>> 120/208 V "single phase systems" are different. Other leg still applies.
>>> This way, if one phase is loaded to maximum,
>>> and the other has no load, the system would still be safe. With such
>>> a neutral, I don't see how PF changes can create exessive current in
>>> the neutral wire in a 2 phase residential system.
>As John pointed out, if the load consists of rectifiers without
>PF correction, the currents do not cancel in the neutral wire.
>In fact, the current may end up to be the *sum* of the currents
>in both hot wires.
That depends a lot on how the rectifier is connected and just what is
connected for legs. If the rectifier is across 240 from a 120/240 system
no neutral current (harmonic or otherwise) flows; very different from
3-phase systems.
>>>> This way, if one phase is loaded to maximum,
>>>> and the other has no load, the system would still be safe. With such
>>>> a neutral, I don't see how PF changes can create exessive current in
>>>> the neutral wire in a 2 phase residential system.
>>As John pointed out, if the load consists of rectifiers without
>>PF correction, the currents do not cancel in the neutral wire.
>>In fact, the current may end up to be the *sum* of the currents
>>in both hot wires.
>>Jeroen Belleman
>That even applies to 120/240 center-tapped systems where the 120 volt
>loads are 0 and 180 degrees. If the loads were half-wave diode
>rectified, and each line was running at its rated max RMS current, the
>neutral could be overloaded. Again, if the line currents don't overlap
>in time they add into the neutral, not balance as would happen with
>sinewave loads.
>You could get the same effect with a resistive load on one side and a
>capacitive load on the other. The orthogonal neutral currents wouldn't
>cancel.
It has been a long time since i saw normal equipment using a half-wave
rectifier. That pretty well went out with 5 tube radios.
I don't think i have ever seen it from each line directly, always a
transformer in-between.