Google Groups no longer supports new Usenet posts or subscriptions. Historical content remains viewable.
Dismiss

Somewhat OT: Well Wiring

2 views
Skip to first unread message

Ecnerwal

unread,
Mar 26, 2010, 9:15:34 PM3/26/10
to
From what I understand of wire insulation codes, ANY TW or THWN wire (or
other wire with a W in the type code) is waterproof, period. Conduits
are assumed to be full of water if they run outside, so wet location
wire is supposed to work fine in water.

I'm wiring a submersible well pump. 12-2 w/g "well wire" is thus far so
much more costly than 3 rolls of 12-gauge wire and I "twist it myself"
(the product I'm comparing is just 3 wires twisted, no jacket) that I'm
rather tempted to do exactly that, since I can't see that there's
anything "special" about "submersible well pump wire" other than its
"special bend-over price." At least, if I understand wire insulation
codes correctly. There's no "special insulation code just for wells" -
the stuff is typically TW (60C - no problem in a hole in the ground that
stays near 10-15C most of the time.)

--
Cats, coffee, chocolate...vices to live by

BQ340

unread,
Mar 26, 2010, 9:34:56 PM3/26/10
to

I think pump cable is annealed due to the movement it is subject to when
the pump cuts in/out.

MikeB

Ecnerwal

unread,
Mar 26, 2010, 10:17:53 PM3/26/10
to
In article <hojncf$con$1...@news.eternal-september.org>,
BQ340 <BQ...@roadrunner.com> wrote:

The torque arrestor (rubber football-like thing clamped to the pipe just
above the pump) is supposed to keep the rest of the system from moving,
much. Likewise, a series of standoffs/spacers is supposed to keep the
pipe, wire and rope from tangling up or hitting the sidewalls. Still,
worth a thought. Thanks.

Paul Hovnanian P.E.

unread,
Mar 27, 2010, 1:03:41 AM3/27/10
to

Consider using stranded conductors.

--
Paul Hovnanian mailto:Pa...@Hovnanian.com
------------------------------------------------------------------
It's easier said than done.
... and if you don't believe it, try proving that it's easier done than
said, and you'll see that it's easier said that `it's easier done than
said' than it is done, which really proves that it's easier said than
done.

Ecnerwal

unread,
Mar 27, 2010, 11:37:56 AM3/27/10
to
In article <4BAD91AD...@Hovnanian.com>,

"Paul Hovnanian P.E." <Pa...@Hovnanian.com> wrote:

> Ecnerwal wrote:
> >
> > In article <hojncf$con$1...@news.eternal-september.org>,
> > BQ340 <BQ...@roadrunner.com> wrote:
> > > I think pump cable is annealed due to the movement it is subject to when
> > > the pump cuts in/out.
> > >
> > > MikeB
> >
> > The torque arrestor (rubber football-like thing clamped to the pipe just
> > above the pump) is supposed to keep the rest of the system from moving,
> > much. Likewise, a series of standoffs/spacers is supposed to keep the
> > pipe, wire and rope from tangling up or hitting the sidewalls. Still,
> > worth a thought. Thanks.
>
> Consider using stranded conductors.

I was planning to - and looking into it further most well wire does, as
MikeB suggests, specifically state annealed, while most regular stranded
wire does not. Probably there is some movement despite the football.

A related ugly thought occurred to me last night. The well casing (100
feet of steel) is the end-point of my grounding system (100 feet of 2/0
copper, with 4 8 foot rods driven in from the bottom of a 3-4 foot deep
trench, and then connected to the well casing.) The (PVC) conduit for
the well pump power runs mostly parallel to, but as much as 2 feet away
from the ground wire. If I run a ground with the pump power from house
to well-head, that creates a ground loop if I (as I gather I should)
park a surge arrester at the top of the well casing and tie the piddly
ground wire into the well casing as well. I'm thinking I should just run
power wires in the conduit, and tie the down-hole ground wire (and surge
arrestor) into the well casing, which is tied to the main ground system
(by wire far larger than the well power wires), and thus not create a
ground loop. It does create some loop area between the ground and power,
but at least does not create a full on ground loop.

co_f...@yahoo.com

unread,
Mar 27, 2010, 12:10:26 PM3/27/10
to
On Mar 26, 6:15 pm, Ecnerwal

We live in the desert and have a well about 600 ft deep. The pump is a
3hp.

Last summer we had to replace the pump. The 1 1/2 pipe is 540 ft, as I
remember. The wire was three individual conductors, Twisted, as you
suggest. The pipe had one of those "football" things on it and the
well maintenance guys took it off and threw it away. Said it doesn't
stop twisting of the pipe, only dampens the vibration and with that
much pipe, didn't really do anything.

We reused the old wire and tried our best to examine it and tape any
abraded places. The wire was taped in many places as it went down the
well.

About a month later, the pump quit with a short to ground. Apparently
we had missed an abraded place and it had worn more and shorted to the
pipe. So, another session of pipe removal. They got a spool and a half
of new wire. This wire was flat and the three conductors are molded
together in some type of poly insulation. Yes, it did cost a lot, but
the scrap price for the old wire covered almost 1/2 the cost of the
new stuff. The new flat wire will probably not have the abrasion
problem the old wire had.

I would submit that you are foolish to not use the more expensive wire
specifically designed for well usage. The cost of replacement in a few
years will more than exceed the cost difference.

Just my experience.

Paul

wmbjk...@citlink.net

unread,
Mar 27, 2010, 3:40:25 PM3/27/10
to

I've seen a fair bit of both types of wire. Yes, the twisted stuff is
more easily damaged, especially if the hole is crooked, has offset
joints, or is uncased. But generally, it works well. It's an easy way
to save quite a few bux on deep wells if there aren't any special
problems. Even if there are issues on a particular hole, one could
probably still save over the double-jacketed type by putting a torque
arrestor say, every 100'.
http://www.deanbennett.com/misc-well-accessories.htm Or make centering
devices out of strips of pvc and hose clamps.

Reasonable wire prices here.
http://www.deanbennett.com/submersible-pump-wire.htm

Wayne

Ecnerwal

unread,
Mar 27, 2010, 4:20:59 PM3/27/10
to
In article <7jnsq5t35m93nuhmr...@4ax.com>,
wmbjk...@citlink.net wrote:

> Or make centering
> devices out of strips of pvc and hose clamps.

I'm simply buying plastic centering devices (aka cable guides) and
sticking them on the pipe every 10-25 feet (recommendations vary - the
things are only a couple bucks each, with holes to isolate pipe, wire,
and safety rope.) Could certainly add a couple more footballs, I guess.
The things pump guys do (ie, throwing that away) are sometimes based on
future pump guy business...I suspect.

Best price thus far on the well cable is 62 cents a foot delivered,
which is bearable, but I find occasional surprises, like the 100 bucks
less that one local lumberyard is charging me for 200PSI poly pipe .vs.
best price I could find on the internet, (while local lumberyard #2
could not get 200PSI pipe, and wants $1.57/foot plus tax for pump cable.)

I have shifted to mostly shopping for 300 feet of pump cable and putting
a junction (and arrestor) at the top of the well, rather than buying a
reel at 500 feet (should cost less per foot, so far does not) and
running pump cable out to the wellhead from the power source, since
"non-pump-wire" costs considerably less, and that part is just sitting
still in conduit.

It's easy to se where this can get horribly expensive the second time -
right now time is not of the essence and I have the latitude to shop
around. Once dependent on the well working, local lumberyard #2's
extortionate price on pump wire might look better than a week's delay.
Avoiding a second time as much as possible is certainly part of the plan.

Charles U Farley

unread,
Mar 27, 2010, 5:38:17 PM3/27/10
to
Ecnerwal <MyName...@ReplaceWithMyVices.Com.invalid> wrote in
news:MyNameForward-18F...@feeder.eternal-september.org:

> I have shifted to mostly shopping for 300 feet of pump cable and putting
> a junction (and arrestor) at the top of the well, rather than buying a
> reel at 500 feet (should cost less per foot, so far does not) and
> running pump cable out to the wellhead from the power source, since
> "non-pump-wire" costs considerably less, and that part is just sitting
> still in conduit.
>
> It's easy to se where this can get horribly expensive the second time -
> right now time is not of the essence and I have the latitude to shop
> around. Once dependent on the well working, local lumberyard #2's
> extortionate price on pump wire might look better than a week's delay.
> Avoiding a second time as much as possible is certainly part of the plan.
>

That's starting to add up to a bunch of length you're shopping for. The
original post stated 12 ga, have you allowed for voltage drop at that
distance? One job I hooked up we had to go huge (#2) for a few hundred
feet of the underground portion and splice to #10 for the pump wire at the
well head. That kept the pump wire to a reasonable size and voltage drop
under 5%. Total circuit was 600' IIRC.


Ecnerwal

unread,
Mar 27, 2010, 9:25:01 PM3/27/10
to
In article <dVurn.110708$Ye4....@newsfe11.iad>,

Charles U Farley <no....@here.com> wrote:

> That's starting to add up to a bunch of length you're shopping for. The
> original post stated 12 ga, have you allowed for voltage drop at that
> distance? One job I hooked up we had to go huge (#2) for a few hundred
> feet of the underground portion and splice to #10 for the pump wire at the
> well head. That kept the pump wire to a reasonable size and voltage drop
> under 5%. Total circuit was 600' IIRC.

The total wire run is just under 400 feet. 3/4 hp, 2-wire, 230 V - the
pump specs on the particular pump I'm shopping claim 12 Ga is good (for
up to 525 feet) though I might run 10 Ga for the ~100 feet out to the
well-head and switch to 12 for the 300 feet down the hole. The price of
copper has made massive overkill somewhat less appealing, so I'm
sticking with mere overkill, though I had pencilled in 10 Ga as well as
12 Ga on the prospective shopping list, just to see what it added. In
shopping for the 500 foot reel I was planning to use the extra 100+ feet
for some other exterior wiring.

The alternate pump I'm considering claims 545 feet for 12 Ga, so if I
switch units, I'd still be well inside the suggested range.

I could use a 1/2 hp pump but I'd like to both be able to actually use
some of the storage (drawdown) in the well, and not be screwed if the
static water level measured when drilled is not the static water level
at all times of year.

0 new messages