3 phase converter monitoring setup
There are currently too many topics in this group that display first. To make this topic appear first, remove this option from another topic.
There was an error processing your request. Please try again.
flag
  13 messages - Collapse all  -  Translate all to Translated (View all originals)
The group you are posting to is a Usenet group. Messages posted to this group will make your email address visible to anyone on the Internet.
Your reply message has not been sent.
Your post was successful
 
From:
To:
Cc:
Followup To:
Add Cc | Add Followup-to | Edit Subject
Subject:
Validation:
For verification purposes please type the characters you see in the picture below or the numbers you hear by clicking the accessibility icon. Listen and type the numbers you hear
 
willray  
View profile  
 More options Jan 10 2009, 11:26 pm
Newsgroups: rec.crafts.metalworking
From: willray <will...@mac.com>
Date: Sat, 10 Jan 2009 20:26:41 -0800 (PST)
Local: Sat, Jan 10 2009 11:26 pm
Subject: [query] 3 phase converter monitoring setup

Greetings all,

I'm working on balancing my rotary converter and need
a sanity check.

(Basic statistics for the record.  1125RPM 15HP idler.
 Feeds off a 125A breaker in the shop panel, through
 a 100A fused disconnect.  L1 and L2 from the disconnect
 feed L1 and L2 in a 3p panel on the rails (I might pull
 single-phase 220 from this subpanel for other uses in
 the shop).  The idler and start circuit feed out, and
 back in through the 3P panel's original 100A Main breaker.
 Starting is the standard push-and-hold auto starting setup,
 with a Grainger voltage-sensing relay to cut out the
 starter switch when L3 comes up.  I've forgotten how
 much starting capacitance I have in the box, but it
 spins the (kinda chunky) 15HP idler up in less than 2
 seconds.  When running, it'll currently spin up a 5HP
 high-pressure blower (Invincible vacuum), in about 5
 seconds, pulling about 45A on L1 and L2, and 23A on
 L3.  Once spinning, it pulls about 25A on L1, 19A on L2,
 and 5A on L3.  I don't currently have voltages on it.)

Just for gits and shiggles, rather than just tweaking
the balancing caps with an amp-clamp and DVM, I thought
I'd build a full-blown current and voltage monitoring
system for it.

For current monitoring, I've stuffed 3x 100:5 current
transformers into the 3P subpanel, and brought them out
to current-sensing resistors.

For voltage monitoring I need voltage in the range -1V -- 1V
to match my scope inputs, so I need to build a voltage-divider.
This would be no big deal, except I just tossed myself a puzzler
when getting ready to solder the bits together.

One could build 3 bridges (say 2MOhm and 2KOhm roughly,
just to make the numbers reasonably neat), and bridge
L1->L2, L2->L3, and L3->L1, thereby being able to measure
the between-leg voltages.  Alternatively one could bridge
L1->C, L2->C, L3->C (and possibly tie C to ground/N).  I've
doodled an ASCII version of this below.  Hopefully it survives
being posted.  L1, L2, and L3 are as traditional.  L1->a is 2MOhms,
a->d is 2KOhms.  The other legs are symmetric.

  L1                   L2
   .                   .
    _                 _
     |               |
      _             _
       |           |
        _         _
         . a   b .
         |       |
          _     _
           |   |
            _ _
             . d
             \
             /
             \
             . c
             \
             /
             \
             /
             \
             /
             .
             L3

This setup appears allows metering of both the between leg
voltages by metering across both middle .1% resistors on
a leg pair ( ie, a to b, b to c, c to a) and the
Leg->Neutral voltages if the d is tied to ground/N.

I hadn't originally thought of using the "Wye connected" meter
setup, but I can't currently think of a downside.  I'm
wondering if anyone who does this stuff more regularly might
know some reason not to do this, that I haven't thought of.

Hmm - while I'm at it, another question -- Is there any reason
that I can't tie together one leg of each current-sensing
resistor for the current monitor part, and use this as a
"common", for metering purposes?  I'm suspicious that my
scope inputs don't have isolated grounds.

Many thanks for your time,
William Ray


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
DoN. Nichols  
View profile  
 More options Jan 11 2009, 2:03 am
Newsgroups: rec.crafts.metalworking
From: "DoN. Nichols" <dnich...@d-and-d.com>
Date: 11 Jan 2009 07:03:37 GMT
Local: Sun, Jan 11 2009 2:03 am
Subject: Re: [query] 3 phase converter monitoring setup
On 2009-01-11, willray <will...@mac.com> wrote:

> Greetings all,

> I'm working on balancing my rotary converter and need
> a sanity check.

> (Basic statistics for the record.  1125RPM 15HP idler.
>  Feeds off a 125A breaker in the shop panel, through

        [ ... ]

> Just for gits and shiggles, rather than just tweaking
> the balancing caps with an amp-clamp and DVM, I thought
> I'd build a full-blown current and voltage monitoring
> system for it.

> For current monitoring, I've stuffed 3x 100:5 current
> transformers into the 3P subpanel, and brought them out
> to current-sensing resistors.

        Good -- that gives you isolation.

        Yes -- one very good reason -- have you tried measuring the
voltage from ground to the center point?  I'll bet that it is a nasty
range above ground, since you have no isolation between the incoming
power line and the rotary converter.

        Get three identical filament transformers with input voltage
appropriate to the leg-to-leg voltage.  You can then tie one side of
each secondary to ground and safely measure voltages (taking into
account the ratio of the transformer, of course.

> Hmm - while I'm at it, another question -- Is there any reason
> that I can't tie together one leg of each current-sensing
> resistor for the current monitor part, and use this as a
> "common", for metering purposes?

        Yes -- since the current transformers give you isolation.

>                                   I'm suspicious that my
> scope inputs don't have isolated grounds.

        Most don't.  The probe ground is connected to the safety ground
pin on the power cord.

        You want the isolation that the current transformers give you,
and similar isolation on the voltage side with the filament
transformers.  (Those used to be cheap enough and common enough so you
should be able to pick up three identical ones.

        Good Luck,
                DoN.

--
 Email:   <dnich...@d-and-d.com>   | Voice (all times): (703) 938-4564
        (too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
           --- Black Holes are where God is dividing by zero ---


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Steve Lusardi  
View profile  
 More options Jan 11 2009, 5:16 am
Newsgroups: rec.crafts.metalworking
From: "Steve Lusardi" <stevenos...@lusardi.de>
Date: Sun, 11 Jan 2009 11:16:17 +0100
Local: Sun, Jan 11 2009 5:16 am
Subject: Re: [query] 3 phase converter monitoring setup
William,
I don't wish to rain on your parade, but if you value your time at all, you
will find you can replace your entire setup with a new solid state
sinusoidal VFD that will easily handle your loads. These are available both
monitored and unmonitored at prices around $500 not made in China on eBay.
These VFDs are far more balanced than your rotary converter with far better
power factors. If you consider the money realized from the sale of your
existing kit and the cost of your time, the VFD would be virtually free.
Steve

"willray" <will...@mac.com> wrote in message

news:66c049b8-e2ac-49c9-87ba-4df630197a23@m4g2000vbp.googlegroups.com...

Greetings all,

I'm working on balancing my rotary converter and need
a sanity check.

(Basic statistics for the record.  1125RPM 15HP idler.
 Feeds off a 125A breaker in the shop panel, through
 a 100A fused disconnect.  L1 and L2 from the disconnect
 feed L1 and L2 in a 3p panel on the rails (I might pull
 single-phase 220 from this subpanel for other uses in
 the shop).  The idler and start circuit feed out, and
 back in through the 3P panel's original 100A Main breaker.
 Starting is the standard push-and-hold auto starting setup,
 with a Grainger voltage-sensing relay to cut out the
 starter switch when L3 comes up.  I've forgotten how
 much starting capacitance I have in the box, but it
 spins the (kinda chunky) 15HP idler up in less than 2
 seconds.  When running, it'll currently spin up a 5HP
 high-pressure blower (Invincible vacuum), in about 5
 seconds, pulling about 45A on L1 and L2, and 23A on
 L3.  Once spinning, it pulls about 25A on L1, 19A on L2,
 and 5A on L3.  I don't currently have voltages on it.)

Just for gits and shiggles, rather than just tweaking
the balancing caps with an amp-clamp and DVM, I thought
I'd build a full-blown current and voltage monitoring
system for it.

For current monitoring, I've stuffed 3x 100:5 current
transformers into the 3P subpanel, and brought them out
to current-sensing resistors.

For voltage monitoring I need voltage in the range -1V -- 1V
to match my scope inputs, so I need to build a voltage-divider.
This would be no big deal, except I just tossed myself a puzzler
when getting ready to solder the bits together.

One could build 3 bridges (say 2MOhm and 2KOhm roughly,
just to make the numbers reasonably neat), and bridge
L1->L2, L2->L3, and L3->L1, thereby being able to measure
the between-leg voltages. Alternatively one could bridge
L1->C, L2->C, L3->C (and possibly tie C to ground/N).  I've
doodled an ASCII version of this below.  Hopefully it survives
being posted.  L1, L2, and L3 are as traditional.  L1->a is 2MOhms,
a->d is 2KOhms.  The other legs are symmetric.

  L1                   L2
   .                   .
    _                 _
     |               |
      _             _
       |           |
        _         _
         . a   b .
         |       |
          _     _
           |   |
            _ _
             . d
             \
             /
             \
             . c
             \
             /
             \
             /
             \
             /
             .
             L3

This setup appears allows metering of both the between leg
voltages by metering across both middle .1% resistors on
a leg pair ( ie, a to b, b to c, c to a) and the
Leg->Neutral voltages if the d is tied to ground/N.

I hadn't originally thought of using the "Wye connected" meter
setup, but I can't currently think of a downside. I'm
wondering if anyone who does this stuff more regularly might
know some reason not to do this, that I haven't thought of.

Hmm - while I'm at it, another question -- Is there any reason
that I can't tie together one leg of each current-sensing
resistor for the current monitor part, and use this as a
"common", for metering purposes?  I'm suspicious that my
scope inputs don't have isolated grounds.

Many thanks for your time,
William Ray


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
pentag...@yahoo.com  
View profile  
 More options Jan 11 2009, 5:52 am
Newsgroups: rec.crafts.metalworking
From: pentag...@yahoo.com
Date: Sun, 11 Jan 2009 10:52:06 +0000
Local: Sun, Jan 11 2009 5:52 am
Subject: Re: [query] 3 phase converter monitoring setup
On 11 Jan 2009 07:03:37 GMT, "DoN. Nichols"

   I see you're aiming for the luxury of both current and
 voltage measurement.

 When there is significant unbalance, the apparent 3 phase
balance of the current set and the voltage set can be very
different.

    With both sets of figures available you may be tempted  to
aim for a rough average betweeen voltage and current balance.

        Because motors are essentially current driven devices
this is not the way. Balanced current should be your aim even if
this results in larger voltage unbalance.

                     Jim


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Jim Wilkins  
View profile  
 More options Jan 11 2009, 8:14 am
Newsgroups: rec.crafts.metalworking
From: Jim Wilkins <KB1...@gmail.com>
Date: Sun, 11 Jan 2009 05:14:45 -0800 (PST)
Local: Sun, Jan 11 2009 8:14 am
Subject: Re: 3 phase converter monitoring setup
On Jan 11, 5:52 am, pentag...@yahoo.com wrote:

What do you think of displaying the current transformer output on the
scope to watch the phase angle? A vectorscope would be really nice but
I don't know how to show 3 phases on an X-Y display.

jw


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
willray  
View profile  
 More options Jan 11 2009, 1:09 pm
Newsgroups: rec.crafts.metalworking
From: willray <will...@mac.com>
Date: Sun, 11 Jan 2009 10:09:33 -0800 (PST)
Local: Sun, Jan 11 2009 1:09 pm
Subject: Re: 3 phase converter monitoring setup
On Jan 11, 5:16 am, "Steve Lusardi" <stevenos...@lusardi.de> wrote:

> William,
> I don't wish to rain on your parade, but if you value your time at all, you
> will find you can replace your entire setup with a new solid state
> sinusoidal VFD that will easily handle your loads. These are available both
> monitored and unmonitored at prices around $500 not made in China on eBay.
> These VFDs are far more balanced than your rotary converter with far better
> power factors. If you consider the money realized from the sale of your
> existing kit and the cost of your time, the VFD would be virtually free.
> Steve

Unless things have changed rather significantly in the VFD world
recently,
I think I'd either need something ridiculous in the VFD world, or a
rather complex and extensive switching and control system to route
power
and control around the shop.

The current setup will replace Mains power for 8 to 10 machines,
including
hopefully allowing me to run a step-up transformer to power a 440V 5HP
subsystem.   To simulate Mains power with a VFD (as opposed to using
either
a separate VFD for the switching/control system of each machine, or
one
VFD that can be cut over to each of many machines), I believe the
consensus
has been that it required a monstrously oversized VFD.

Are there inexpensive VFDs out there now that can provide "Mains
Service like"
(capable of handling load-local switching, plug reversing etc)
power to a subpanel for distribution?

(of course, half the reason I'm doing this at all, is for the
amusement
of it, so entirely reasonable suggestions along the lines of "do it
the
smart way", will end up deprecated in favor of suggestions for
byzantine
but functional :-)

Thanks!
Will

Will


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
willray  
View profile  
 More options Jan 11 2009, 1:44 pm
Newsgroups: rec.crafts.metalworking
From: willray <will...@mac.com>
Date: Sun, 11 Jan 2009 10:44:44 -0800 (PST)
Local: Sun, Jan 11 2009 1:44 pm
Subject: Re: 3 phase converter monitoring setup
On Jan 11, 2:03 am, "DoN. Nichols" <dnich...@d-and-d.com> wrote:

Hi DoN - always nice to see familiar knowledgeable faces when I have
time
to drop in!

I haven't measured the center point, but I'm assuming it's off center.
The "Wye Connected" bridge network was my solution to let me monitor
the center - but of course you're right - if it's off center, that
screws up the leg-leg measures.

Filament transformers it is.  I probably have enough identical ones
in a box somewhere here to put that together from spare parts.
Finding
that box, could take a while, so maybe I'll order some more...

> >                                   I'm suspicious that my
> > scope inputs don't have isolated grounds.

>         Most don't.  The probe ground is connected to the safety ground
> pin on the power cord.

I let the smoke out of the first scope I discovered that on...  I
"manually float" most scopes that cross my path now.  I'm pretty sure
my Tek. scopemeter has completely isolated inputs, but I don't
trust that "pretty sure" enough to bet the magic smoke on it, and
I'm less-sure about the 4-channel Tek that I'm planning to use for
monitoring the 3P converter.

Ok.  Back to the barn to search for transformers...

Thanks much!
Will Ray


         You want the isolation that the current transformers give
you,


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Robert Swinney  
View profile  
 More options Jan 11 2009, 2:02 pm
Newsgroups: rec.crafts.metalworking
From: "Robert Swinney" <judy...@tx.rr.com>
Date: Sun, 11 Jan 2009 13:02:02 -0600
Local: Sun, Jan 11 2009 2:02 pm
Subject: Re: 3 phase converter monitoring setup
Willray sez:

"(of course, half the reason I'm doing this at all, is for the
amusement
of it, so entirely reasonable suggestions along the lines of "do it
the
smart way", will end up deprecated in favor of suggestions for
byzantine
but functional :-)"

Depricate as you will . . . but the method of voltage balancing rotary phase converters as outlined
in RCM over the years is probably the best way to go.  See articles in www.metalwebnews.com which
describe the voltage balance method in detail.

Bob Swinney


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
DoN. Nichols  
View profile  
 More options Jan 11 2009, 8:22 pm
Newsgroups: rec.crafts.metalworking
From: "DoN. Nichols" <dnich...@d-and-d.com>
Date: 12 Jan 2009 01:22:24 GMT
Local: Sun, Jan 11 2009 8:22 pm
Subject: Re: [query] 3 phase converter monitoring setup
On 2009-01-11, pentag...@yahoo.com <pentag...@yahoo.com> wrote:

> On 11 Jan 2009 07:03:37 GMT, "DoN. Nichols"
><dnich...@d-and-d.com> wrote:

>>On 2009-01-11, willray <will...@mac.com> wrote:

        [ ... ]

>>> For current monitoring, I've stuffed 3x 100:5 current
>>> transformers into the 3P subpanel, and brought them out
>>> to current-sensing resistors.

>>        Good -- that gives you isolation.

>>> For voltage monitoring I need voltage in the range -1V -- 1V
>>> to match my scope inputs, so I need to build a voltage-divider.
>>> This would be no big deal, except I just tossed myself a puzzler
>>> when getting ready to solder the bits together.

        [ ... ]

        [ ... ]

>    I see you're aiming for the luxury of both current and
>  voltage measurement.

>  When there is significant unbalance, the apparent 3 phase
> balance of the current set and the voltage set can be very
> different.

>     With both sets of figures available you may be tempted  to
> aim for a rough average betweeen voltage and current balance.

>         Because motors are essentially current driven devices
> this is not the way. Balanced current should be your aim even if
> this results in larger voltage unbalance.

        That depends.  Yes, if a motor is the only load.  But if it is
also powering something like a Bridgeport BOSS-3 through BOSS-6, a
voltage imbalance will pop stepper driver power transistors like
popocorn on the opening night of a big movie. :-)

        The transistors used in these systems were just barely high
enough voltage rating to handle what was being applied.  (Of course,
really high voltage power transistors were very rare and very expensive
when the system was designed.  I think that the BOSS-3 hit the streets
about 1977. :-)

        If you're using such a machine, it might be good to use two
rotary converters -- one tuned for current balance for the spindle
motor, and one tuned for voltage balance for the electronics boxes.

        Enjoy,
                DoN.

--
 Email:   <dnich...@d-and-d.com>   | Voice (all times): (703) 938-4564
        (too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
           --- Black Holes are where God is dividing by zero ---


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Ignoramus8841  
View profile  
 More options Jan 11 2009, 8:32 pm
Newsgroups: rec.crafts.metalworking
From: Ignoramus8841 <ignoramus8...@NOSPAM.8841.invalid>
Date: Sun, 11 Jan 2009 19:32:35 -0600
Local: Sun, Jan 11 2009 8:32 pm
Subject: Re: [query] 3 phase converter monitoring setup
They sell three phase power monitors and they are not very expensive
on ebay. I have one and am going to install it on my phase converter
"one day". My phase converter already does a fine job, so I keep
postponing it in favor of more fun things.

i


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
willray  
View profile  
 More options Jan 11 2009, 9:01 pm
Newsgroups: rec.crafts.metalworking
From: willray <will...@mac.com>
Date: Sun, 11 Jan 2009 18:01:46 -0800 (PST)
Local: Sun, Jan 11 2009 9:01 pm
Subject: Re: 3 phase converter monitoring setup
On Jan 11, 2:02 pm, "Robert Swinney" <judy...@tx.rr.com> wrote:

> Willray sez:

> "(of course, half the reason I'm doing this at all, is for the
> amusement of it, so entirely reasonable suggestions along the lines
> of "do it the smart way", will end up deprecated in favor of
> suggestions for byzantine but functional :-)"

> Depricate as you will . . . but the method of voltage balancing rotary phase converters as outlined
> in RCM over the years is probably the best way to go.  See articles in www.metalwebnews.com which
> describe the voltage balance method in detail.

> Bob Swinney

This isn't the first rotary I've built or balanced - just the first
that I decided to incorporate a full monitoring package into, so that
it can draw pretty pictures on my 4-channel scope.  The availability
of 4 channels provides some visualization and monitoring capabilities
that aren't typically taken advantage of by the RCM techniques.

Fitch and Jim R. seem to be the people who have done spent the most
time staring at scopemeters hooked up to their converters, but they
were stuck with the Fluke's dual-sweep inputs, and weren't really
working for designing an available-full-time monitoring system.

In the end, it'll end up balanced just as normal, but it'll be more
fun doing it, and it'll draw pretty, and moderately meaningful
pictures for me :-)

Will


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Don Young  
View profile  
 More options Jan 12 2009, 12:13 am
Newsgroups: rec.crafts.metalworking
From: "Don Young" <no...@nonesuch.com>
Date: Sun, 11 Jan 2009 23:13:53 -0600
Local: Mon, Jan 12 2009 12:13 am
Subject: Re: 3 phase converter monitoring setup

"willray" <will...@mac.com> wrote in message

news:f880c0ba-b967-484c-9001-33c88d865867@e1g2000pra.googlegroups.com...
On Jan 11, 2:03 am, "DoN. Nichols" <dnich...@d-and-d.com> wrote:

Hi DoN - always nice to see familiar knowledgeable faces when I have
time
to drop in!

I haven't measured the center point, but I'm assuming it's off center.
The "Wye Connected" bridge network was my solution to let me monitor
the center - but of course you're right - if it's off center, that
screws up the leg-leg measures.

Filament transformers it is.  I probably have enough identical ones
in a box somewhere here to put that together from spare parts.
Finding
that box, could take a while, so maybe I'll order some more...

> > I'm suspicious that my
> > scope inputs don't have isolated grounds.

> Most don't. The probe ground is connected to the safety ground
> pin on the power cord.

I let the smoke out of the first scope I discovered that on...  I
"manually float" most scopes that cross my path now.  I'm pretty sure
my Tek. scopemeter has completely isolated inputs, but I don't
trust that "pretty sure" enough to bet the magic smoke on it, and
I'm less-sure about the 4-channel Tek that I'm planning to use for
monitoring the 3P converter.

Ok.  Back to the barn to search for transformers...

Thanks much!
Will Ray


  You want the isolation that the current transformers give
you,
> and similar isolation on the voltage side with the filament
> transformers. (Those used to be cheap enough and common enough so you
> should be able to pick up three identical ones.

> Good Luck,
> DoN.

> --
> Email: <dnich...@d-and-d.com> | Voice (all times): (703) 938-4564
> (too) near Washington D.C. |http://www.d-and-d.com/dnichols/DoN.html
> --- Black Holes are where God is dividing by zero ---

Don't worry too much about the transformers being identical. It is easy
enough to scale the outputs to be equal when the primaries are all connected
in parallel to the same source. Any non-linearities will be insignificant if
the primary voltages are within ratings.

Don Young


 
You must Sign in before you can post messages.
To post a message you must first join this group.
Please update your nickname on the subscription settings page before posting.
You do not have the permission required to post.
Robert Swinney  
View profile  
 More options Jan 12 2009, 8:33 pm
Newsgroups: rec.crafts.metalworking
From: "Robert Swinney" <judy...@tx.rr.com>
Date: Mon, 12 Jan 2009 19:33:53 -0600
Local: Mon, Jan 12 2009 8:33 pm
Subject: Re: 3 phase converter monitoring setup
Phase displacement can be measured with an oscilloscope.  I use 1 turn of heavy wire around the
winding core of a 12:120 Vac transformer and read the voltage scaled  current waveform on either the
primary or secondary of the transformer.  The resulting waveform can be displayed on 1 channel of
the scope at some conveint size determined by the scope's calibrated vertical amplifier.  Place a
voltage divider across the leg under measurement and display it on channel 2, with the two waveforms
dispalyed in the same "size".  View both waveforms on a common timebase and read phase displacement
between the traces.  Make sure the scope is powered through an isolation transformer.

Bob Swinney

"willray" <will...@mac.com> wrote in message

news:f0beafdd-c68b-4f9f-bc9c-b5359df41daa@y1g2000pra.googlegroups.com...
On Jan 11, 2:02 pm, "Robert Swinney" <judy...@tx.rr.com> wrote:

> Willray sez:

> "(of course, half the reason I'm doing this at all, is for the
> amusement of it, so entirely reasonable suggestions along the lines
> of "do it the smart way", will end up deprecated in favor of
> suggestions for byzantine but functional :-)"

> Depricate as you will . . . but the method of voltage balancing rotary phase converters as
> outlined
> in RCM over the years is probably the best way to go. See articles in www.metalwebnews.com which
> describe the voltage balance method in detail.

> Bob Swinney

This isn't the first rotary I've built or balanced - just the first
that I decided to incorporate a full monitoring package into, so that
it can draw pretty pictures on my 4-channel scope.  The availability
of 4 channels provides some visualization and monitoring capabilities
that aren't typically taken advantage of by the RCM techniques.

Fitch and Jim R. seem to be the people who have done spent the most
time staring at scopemeters hooked up to their converters, but they
were stuck with the Fluke's dual-sweep inputs, and weren't really
working for designing an available-full-time monitoring system.

In the end, it'll end up balanced just as normal, but it'll be more
fun doing it, and it'll draw pretty, and moderately meaningful
pictures for me :-)

Will


 