> 107 ohms is about 65?F on a Pt100 alpha = 0.00385 RTD. A bit cool for
> room temperature, but okay..
>
> There are other types of RTDs.. but the old "US Standard" alpha =
> 0.00392 is not very much different from the DIN standard at 40C (less
> than 1 degree C). The old J Pt100 Japanese standard was similar to the
> obsolete US standard. Everyone uses the Euro standard now, pretty
> much.
>
> What you are saying does not make a lot of sense. What is the
> temperature of the developer? 100F is 37.8C, so very close to what you
> say is the upper limit of the controller (but usually the standard
> range is to 49.9C).
The installed omron controllers max out at 39.9C, which really doesn't
give much wiggle room. The operating procedure for the machine is ignore
what the controllers say, but trim the reset pot on the front panel and
fiddle with the numbers until the the temp measured in the tank with a
normal thermometer is correct.
> Is this thing sitting all apart? Are the sensor leads grounded at any
> point? (Unplug the temperature controller, remove the sensor from the
> bath and measure the leads to earth with an ohmmeter - power off).
The machine is in use, so and can only be played with at slow times.
> It is possible they have grounded one of the sensor leads to reduce
> bobble in the controller- the E5CS is/was an early switchmode supply
> controller. Usually Pt100 probes are floating wrt to the shell.. is
> the shell floating on the new probes? Any vigorous EMI sources kicking
> around? Is the developer tank earthed?
The original probes would have been what was cool in West Germany the mid
to late 1980s. It's not clear if the Omron controllers are for the
international Pt100 or Japanese version. They are all fairly old so it's
not out of the question they're all bad.
I've not tested if the new probes are floating or attached to the red or
white lead. Flipping polarity doesn't seem to have any effect. I've not
examined how and if the tank is directly grounded. There is a chain driven
mechanism that raises and lowers rack of film into the tanks. The machine
is mostly single phase 208. Motors and pumps are run with contactors and
heaters and fans with "advanced" solid state relays.
The highest tech thing in those machines are the omron controllers.
There's no know EMI sources, just other similar machines.
> Does it make a difference if the controller is calling for heat or
> not?
It does not. None of this machine makes sense. The rest are straight
forward- replace/rebuild the bad part and they work again.
> One possiblity is that there is not much wrong, but the setup is not
> properly wired so the controllers appear to be malfunctioning. Maybe a
> heater is leaking AC current into the tank. If you take an AC
> voltmeter and hold one lead in your hand and touch the other in the
> tank do you read any voltage?
Will have to try that. Leakage makes sense as a cause, but again, a wire
wrapped around the probe's metal sheath dunked into the developer tank
doesn't cause weird readings of air temp, hand temp or even temp of a
container of developer. Just thought about it now, but the test of is this
an electrolytic reaction problem is bridge the container of developer with
probe to the main tank with a wire. Maybe the wire itself isn't reactive.
The cable running from the operator panel to the back of the machine is
three conductor, white, brown and green with a braided shield. I believe
the shield is chassis grounded, but I'd have to look at it again. The last
working but not OEM probe was somehow lost while trying to source
replacements, so it's not clear how or what was even connected internally.
> If you replace, be sure to use a decent auto-tune PID controller-
> AFAIR, the C41 process is pretty fussy .. IIRC (frm a long time ago)
> the spec is +/-0.1F, which is not easy.
Somehow the size of the machine and all the adjacent tanks and the
constant pumping somehow make it possible.