I plan on running conduit at the beginning of next week. I'll need some
help moving the two benches away from the wall, removing ceiling tiles and
other fun stuff. Brett has graciously donated the wire and conduit that
will needed to run the sub panel. The overall goal is to install a 60 amp
sub panel, 4-6 110v outlets, and two 30A 220v twist lock outlets for the
welder and the compressor. This will more than likely take all week to
complete.
Dru: If you are able to get a load center, I will need it by Monday. If
not Lowe's has an Eaton 125-amp 6 breaker for 22 bucks and the ground bar
is another 6 bucks.
--
Ben S. Eishen
773.234.7436 | b...@eishen.com
9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
I'll be there and can help move stuff, but we'll need at least 4 people to
move those benches. I'll also be planning to put an outlet in for the
fridge and garage door while you're working in other areas.
Thanks,
Daniel H.
Google Voice: (901) 214-5326
- Copying one is plagiarism, copying many is research.
On Wed, Oct 3, 2012 at 5:38 PM, Ben Eishen <b...@eishen.com> wrote:
> I plan on running conduit at the beginning of next week. I'll need some
> help moving the two benches away from the wall, removing ceiling tiles and
> other fun stuff. Brett has graciously donated the wire and conduit that
> will needed to run the sub panel. The overall goal is to install a 60 amp
> sub panel, 4-6 110v outlets, and two 30A 220v twist lock outlets for the
> welder and the compressor. This will more than likely take all week to
> complete.
> Dru: If you are able to get a load center, I will need it by Monday. If
> not Lowe's has an Eaton 125-amp 6 breaker for 22 bucks and the ground bar
> is another 6 bucks.
> --
> Ben S. Eishen
> 773.234.7436 | b...@eishen.com
> 9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
I will be out there at 6:30 to start work today. If anyone would like to
help.
--
Ben S. Eishen
773.234.7436 | b...@eishen.com
9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
On Wed, Oct 3, 2012 at 6:14 PM, Dan Hess <dan9...@gmail.com> wrote:
> I'll be there and can help move stuff, but we'll need at least 4 people to
> move those benches. I'll also be planning to put an outlet in for the
> fridge and garage door while you're working in other areas.
> Thanks,
> Daniel H.
> Google Voice: (901) 214-5326
> - Copying one is plagiarism, copying many is research.
> On Wed, Oct 3, 2012 at 5:38 PM, Ben Eishen <b...@eishen.com> wrote:
>> I plan on running conduit at the beginning of next week. I'll need some
>> help moving the two benches away from the wall, removing ceiling tiles and
>> other fun stuff. Brett has graciously donated the wire and conduit that
>> will needed to run the sub panel. The overall goal is to install a 60 amp
>> sub panel, 4-6 110v outlets, and two 30A 220v twist lock outlets for the
>> welder and the compressor. This will more than likely take all week to
>> complete.
>> Dru: If you are able to get a load center, I will need it by Monday. If
>> not Lowe's has an Eaton 125-amp 6 breaker for 22 bucks and the ground bar
>> is another 6 bucks.
>> --
>> Ben S. Eishen
>> 773.234.7436 | b...@eishen.com
>> 9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
We'll be out there at 6:30 again today if you would like to give us a hand.
We've managed to get the main power cable pulled and the sub panel hung
last night. Today help is needed to move the electronics bench back against
the wall and moving stuff away from the back wall of the shop to install
receptacles.
If you are interested in what kind of service in the space, it 3 phase
power with a "bastard" leg. It is capable of supplying 120v/208v/240v. To
get the single phase 208v service it requires a special delta breaker that
were banned in 1978, but 3 phase 240v delta breakers should be available.
Our new sub panel will only be supplying single phase 120v/240v.
On Mon, Oct 8, 2012 at 2:59 PM, Ben Eishen <b...@eishen.com> wrote:
> I will be out there at 6:30 to start work today. If anyone would like to
> help.
> --
> Ben S. Eishen
> 773.234.7436 | b...@eishen.com
> 9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
> On Wed, Oct 3, 2012 at 6:14 PM, Dan Hess <dan9...@gmail.com> wrote:
>> I'll be there and can help move stuff, but we'll need at least 4 people
>> to move those benches. I'll also be planning to put an outlet in for the
>> fridge and garage door while you're working in other areas.
>> Thanks,
>> Daniel H.
>> Google Voice: (901) 214-5326
>> - Copying one is plagiarism, copying many is research.
>> On Wed, Oct 3, 2012 at 5:38 PM, Ben Eishen <b...@eishen.com> wrote:
>>> I plan on running conduit at the beginning of next week. I'll need some
>>> help moving the two benches away from the wall, removing ceiling tiles and
>>> other fun stuff. Brett has graciously donated the wire and conduit that
>>> will needed to run the sub panel. The overall goal is to install a 60 amp
>>> sub panel, 4-6 110v outlets, and two 30A 220v twist lock outlets for the
>>> welder and the compressor. This will more than likely take all week to
>>> complete.
>>> Dru: If you are able to get a load center, I will need it by Monday. If
>>> not Lowe's has an Eaton 125-amp 6 breaker for 22 bucks and the ground bar
>>> is another 6 bucks.
>>> --
>>> Ben S. Eishen
>>> 773.234.7436 | b...@eishen.com
>>> 9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
> We'll be out there at 6:30 again today if you would like to give us a hand. We've managed to get the main power cable pulled and the sub panel hung last night. Today help is needed to move the electronics bench back against the wall and moving stuff away from the back wall of the shop to install receptacles.
> If you are interested in what kind of service in the space, it 3 phase power with a "bastard" leg. It is capable of supplying 120v/208v/240v. To get the single phase 208v service it requires a special delta breaker that were banned in 1978, but 3 phase 240v delta breakers should be available. Our new sub panel will only be supplying single phase 120v/240v.
> --
> Ben S. Eishen
> 773.234.7436 | b...@eishen.com
> 9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
> On Mon, Oct 8, 2012 at 2:59 PM, Ben Eishen <b...@eishen.com> wrote:
> I will be out there at 6:30 to start work today. If anyone would like to help.
> --
> Ben S. Eishen
> 773.234.7436 | b...@eishen.com
> 9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002
> On Wed, Oct 3, 2012 at 6:14 PM, Dan Hess <dan9...@gmail.com> wrote:
> I'll be there and can help move stuff, but we'll need at least 4 people to move those benches. I'll also be planning to put an outlet in for the fridge and garage door while you're working in other areas.
> Thanks,
> Daniel H.
> Google Voice: (901) 214-5326
> - Copying one is plagiarism, copying many is research.
> On Wed, Oct 3, 2012 at 5:38 PM, Ben Eishen <b...@eishen.com> wrote:
> I plan on running conduit at the beginning of next week. I'll need some help moving the two benches away from the wall, removing ceiling tiles and other fun stuff. Brett has graciously donated the wire and conduit that will needed to run the sub panel. The overall goal is to install a 60 amp sub panel, 4-6 110v outlets, and two 30A 220v twist lock outlets for the welder and the compressor. This will more than likely take all week to complete.
> Dru: If you are able to get a load center, I will need it by Monday. If not Lowe's has an Eaton 125-amp 6 breaker for 22 bucks and the ground bar is another 6 bucks.
> --
> Ben S. Eishen
> 773.234.7436 | b...@eishen.com
> 9160 Hwy. 64, Suite 12-302, Lakeland, TN 38002