Are these 100 amp panels fed off of one meter?? The blocker/couplers
has to go on the first panel downstream from the meter and my X-10
design book states you should only use one. You might want to remove
one of the blockers to see if the signal strength improves. Get rid of
the capacitors. Install a surge suppressor.
What is Frank's (anonymous?) "X-10 design book" that "states you should
only use one" ?
Why should anyone take that advice instead of Phil Kingery's from Advanced
Control Technologies (ACT) who authoritatively goes into considerable detail
on why and how to deploy multiple couplers?
See http://www.act-solutions.com/kingery03.htm
http://www.act-solutions.com/kingery04.htm
http://www.act-solutions.com/kingery20.htm
Carl:
The 6201 is no longer made as best I know. Leastwise when mine failed --
taking down all x-10 in the house with it -- Leviton replaced it under
warranty with a HCA02.
My experience and that of others is that the 6201, HCA02 and ACT's can all
fail. So you can't assume that it is your topology that is wrong. Sometimes
the most efficient trouble shooting is to swap questionable devices with
"known-good" ones. This becomes expensive with couplers.
Yes, the ACT 134 is an amplifier as well as a coupler.
http://www.act-solutions.com/pdfs/PCCSpecs/cr134%20cr334_spec%20.pdf
Its specs state that it is sensitive down to 25 millivolts and that it
outputs 5v peak-to-peak at 5 ohms powerline impedance. There has been at
least one post in this newsgroup that suggests that this output is low
compared to other devices, but that was a comparison of 1) the published
spec with stated impedance with 2) the measured output but unknown power
line impedance of other devices. (This is akin to comparing the output of
two power amplifiers, one with stated impedance, one unstated -- we all know
how misleading that can be.)
.. Marc
Marc_F_Hult
www.ECOntrol.org
Then you _may_ need a coupler repeater in each main panel but I think the
first step is to eliminate one 4851 and then re-evaluate things.
You say you get strong signals with an ESM1 in most locations. The weak
locations may or may not be related to poor coupling. You may have devices
that are attenuating the signals there. While the larger a house, the harder
it is to get good signal everywhere this is not directly related to the
longer wiring runs. Studies have shown there's minimal attenuation that can
be attributed to the length of the wire run but there is a correlation
between the number of J-box terminations and attenuation due to the
increased inductance of those terminations.
The HCA02-10E is a coupler/repeater (the repeated signal is 5Vpp) but it has
been problematic in _some_ installations, especially when a PR511 is also in
the system.
Carl Ford
Finding details on what's inside these Leviton devices is difficult. The
page you referenced has nothing on the 4851.
I think you need...
METER -> 4851 --+--> PANEL A
|
+--> PANEL B
(view with fixed fonts)
Then you may or may not need couplers or coupler/repeaters in both main
panels but I would go at this step-by-step.
Have you tried reaching a tech support person at Leviton? You might also try
the forums on Worthington's site. Tom Morgan sells this stuff and has a
pretty good understanding of it plus contacts at Leviton.
I'm surprised that 6201's are still being sold. When my 6201 died in
January 2001, I was told by the Leviton rep who did the screening for RMA's
that the he 6201 was superceded/obsolete and the HCA02-10E was the
replacement and much better. (There was about a 2-fold _reduction_ in price
from the 6201 to the HCA02-10E so an explanation was needed for why I was
being sent something that cost 1/2 what it was replacing ...)
Note that at least some 6201's have the quirk that they will sometimes
won't start/train/boot properly if the wrong phase is energized first. This
was one of the things I had to check out before Leviton's rep would issue an
RMA. One of the leads/breakers needs to switched on first to avoid the
problem entirely which obviously doesn't happen when the power comes back on
unattended after an outage. So with two 6201's (all else equal) you only
have a one-in-four chance of everything coming up right.
You write that you have low measured signal strength in some places. Have
you tried switching circuits one-by-one at the breaker panel(s) to determine
whether removing particular circuits has more effect than others? The length
of the wires themselves is not nearly as much an issue in terms of signal
loss as are devices connected to them that have a low impedance at 120khz
("signal suckers". This is where having a circuit diagram is very helpful.
There may be equipment plugged in that you are unaware of or not suspect to
be causing a problem.
Yes, the HCA02-10E amplifies according to Leviton: the HCA02-10E "also
amplifies and repeats command signals to maintain proper signal strength
throughout the DHC network".
http://www.leviton.com/sections/prodinfo/newprod/npleadin.htm
Note that there have reportedly been several firmware revisions of the
HCA02-10E.
HTH ... Marc
Marc_F_Hult
www.ECOntrol.org
Meter -------- + ------- 4851 ------panel A ------6201 (connecting
both legs of this panel)---sub pnl A
|
| --------4851 -------panel B -------- Sub Panel B
The link i referred to is the information on the HCA02-10E that you
suggested might help and I was wondering about the use of two of these
units one in each panel and the ping pong effect it might start.
Marc,
They (the 6201's) are still in stock in some places. I'm sure they are
just NOS though. I have been running "barefoot" just normal (not
flourscent, halogen, or HID fixtures) and nothing else. Tv's and all
electronics, surge supressors, computers, Wall warts or anything
plugged in anywhere. Trying to alleviate any potential problems. It
seems that some companies claim they amplify when in reality they just
pass to the other leg of the 220 feed. And I was looking to amplify the
signal to the sub panel B as that is the weakest point.
Thanks again
Carl Ford
Thanks,
Carl Ford
I still recommend correcting the problem caused by the two 4851s before
thinking about whether you need one or more HCA02-10Es. Leviton does
recommend one for each panel. I've not heard of two HCA02-10Es playing
"ping-pong" but there have been ample posts about one HCA02-10E flooding the
line with spurious commands. Most have had no problems while others have had
no end of problems with the HCA02-10E. That's one more reason to get the
4851 situation straight first.
One 4851 just downstream of the meter but upstream of the Y should block any
alien signals while passively coupling both panels.
Carl Ford
I understand that they are off at this point.
My point is that they were never installed correctly and this could have
been a part of the signal strength problem.
One correctly installed 4851 _might_ obviate the need for anything else. We
won't really know until the 4851 installation is corrected.
OTOH, if you feel there's no need to block external signals, an HCA02-10E or
6201 (or better yet two of the ACT coupler repeaters) in each panel might do
the trick.
6201 Bridging Capacitor
| |
incoming-----+------Panel A----- Sub Panel A (Within 6 feet of panel
A)
| (breakers) (breakers)
|
|
+-----Panel B-------- Sub Panel B (3 stories up)
(breakers) (breakers)
| |
Capacitor Capacitor
This current setup gives me the best coverage with a few circuits on
sub panel B getting only a weak signal. This is the latest
configuration. Most X10 controllers reside on this panel. One Cm15a and
a Tw523 that communicates from a Comfort Security System.
If the 6201 is placed in Panel B then I get some weak signals on Sub
panel A. This configuration was the worst one.
I even split the 6201 leads (observing the correct "polarity") and
attached one lead to each Panel A and B. This worked fairly well
signal strenght wise but very unreliable in that I had to repeat
commands a lot. Any macro's for cm11'a or cm15's had to have the units
placed into them in a certain order else those units would not respond.
Here I also had the 4851's both on as I used this setup for over a
year. There is little or no difference strength wise with the 4851's in
or out of circuit here.
The capacitors were only put in after moving the 6201 to Panel A and
don't do much at this point either.
As I read back over this post it seems that amplification is needed as
no matter where I place the 6201 there is always a weak end out there
somewhere. Again this is without any electronics, chargers, computers,
cordless phones plugged in. The Air handlers are the only appliances
on so the normal noise makers or "suckers" are off line in the above
instances.
Thanks,
Carl Ford
The 4851 will only block signals from the neighbor sharing your transformer.
Anything else should not get through the transformer.
However, the description of the 4851 says it also acts as a passive coupler
so it might help with signal strength as well.
The best setup would probably be one properly installed 4851 and then a
coupler/repeater in each main panel. If you still have problems with
sub-panel B, maybe a BoosterLinc from SmartHome will address that. I believe
Bruce Robin has used them successfully to address similar issues.
Given that many people have had problems with the HCA02-10E and that this is
a vacation home I think I would go with the ACT coupler/repeater to avoid
arriving to an HCA02-10E that has gone berserk. You are probably going there
to relax not to troubleshoot your X-10 system.
I reeeally appreciate your input. You must live on your computer as
you are all over the place in HA and I know that you have been since I
started messing with X10 over 9 years ago.
Merry Christmas
yes I said it and don't care if it's politically correct or not. If
this is not your holiday of choice then I hope you have a happy one
when it's your time. We all should be happy for each other and a
little more understanding instead of being defensive.
Carl Ford
It's called X-10 Pro Design Book, Published by "Silent Servant Home
Control, Inc." Authored by Robert N. Bucceri.
>
> Why should anyone take that advice instead of Phil Kingery's from Advanced
> Control Technologies (ACT) who authoritatively goes into considerable detail
> on why and how to deploy multiple couplers?
>
> See http://www.act-solutions.com/kingery03.htm
> http://www.act-solutions.com/kingery04.htm
> http://www.act-solutions.com/kingery20.htm
Thanks for the links, Marc.
| 6201 Bridging Capacitor
| | |
| incoming-----+------Panel A----- Sub Panel A (Within 6 feet of panel
| A)
| | (breakers) (breakers)
| |
| |
| +-----Panel B-------- Sub Panel B (3 stories up)
| (breakers) (breakers)
| | |
| Capacitor Capacitor
You need to be careful mixing passive coupling and repeaters. Although
I've traced only the CR230's circuit, I believe that most repeaters drive
the two legs with carriers 180 degrees out of phase (presumably for the
benefit of 220V-only receivers). Thus any passive coupling that doesn't
flip the phase works against the repeater. Based on the cautions I've read
I think that the 4851 also couples without flipping the phase, though this
was not immediately obvious on casual inspection.
I'm puzzled that you see a significant difference when moving the repeater
from panel A to panel B if the 4851s are out of the picture. Taking this
at face value (always risky :) you might want to try a CR234 on one panel
(whichever hears the house best) connected by its SCC terminals to a CA000
on the other panel. The CA000 is a dumb output driver. The two problems
are (1) I don't know who actually sells the CA000 at this point and (2)
I assume Phil Kingery would have mentioned this idea to you if he thought
it was appropriate.
Dan Lanciani
ddl@danlan.*com
>You need to be careful mixing passive coupling and repeaters. Although
>I've traced only the CR230's circuit, I believe that most repeaters drive
>the two legs with carriers 180 degrees out of phase (presumably for the
>benefit of 220V-only receivers). Thus any passive coupling that doesn't
>flip the phase works against the repeater. Based on the cautions I've read
>I think that the 4851 also couples without flipping the phase, though this
>was not immediately obvious on casual inspection.
If that's the case, wouldn't any incidental coupling from 220V ovens,
dryers, etc. work against the repeater.
How many 220V X-10 receivers are there?
ACT would probably recommend a single CR234 coupler/repeater. I think the
CR134 is for 3 phase systems only so it's not applicable here. I don't know
whether a properly installed 4851 would create problems for their CR234. I
think you need to ask Phil which coupler/repeater and whether or not you
should keep a properly installed 4851.
On holidays I'm an "original intent" kind of guy. Christmas was not a
federal holiday until about 1870. ;)
I'd still recommend going with my original suggestion. Use only one
blocker as Dave H. described. Everything I've learned about X-10 I got
from "my bible" (the Design Manual I first mentioned). Every X-10
system I've installed has worked flawlessly. Most of the wholesalers I
deal with know little of the subject. One of them recognized that home
automation was going to take off and took it upon themselves to get some
information together for their Dealers. That was in 1998.
Here are a few links which might help.
http://www.worthingtonsolutions.com/activekb/index.php?ToDo=view&questId=25&catId=5
http://www.leviton.com/pdfs/dhctechman.pdf (out of date)
http://www.edcheung.com/automa/blocker.htm
http://www.edcheung.com/automa/repeater.htm
Note that Ed Cheung wrote that ACT says not to use both the whole house
blocker and coupler/repeater but that he saw no problems while doing so.
That was some years back so things might have changed.
" As far as you question on "the 2 100amp panel installation ???", I
wrote most of those old articles from 1996 through 2001. My
responsibilities have since changed and I am no longer in that
position.
However, having said that, let me see if I can give you some things to
consider.
1. First, unless you know that you have a problem with noise or
signals coming "onto" your house from the outside, I would not suggest
using the filter-blocks.
2. If your two 100-amp panels are side-by-side and fed from the same
transformer (and, most likely, the same meter), you should be able to
treat them as one big 200 amp panel.
3. If you can (and you are willing to experiment, and you answered
'true' to the two conditions above), order a CR234 and have your
electrician remove the two filter-blocks and the 6201, then install the
CR234 into one of the panels. It probably will not matter which panel,
but if I was forced to make a choice, I would put it on the panel with
the most X-10 controlled devices.
4. Please be aware that your problem also could be noise or some other
signal related issue, but buying a new CR234 is less expensive than
buying (and then trying to learn how to use) the necessary test
equipment. Plus, it is far less expensive than hiring me to
troubleshoot it for you. Therefore, I am basing my recommendation only
on the information you have provided.
Good luck, and I hope we are both right. "
As far as the difference when moving the 6201 from panel A to B the
only thing I can think of is that CM15A and Comfort's Tw523 are located
on circuits in panel A.
Dave,
As always appreciate you keeping up with this. There are 60+ recievers
and all of them are X-10's. I also think the 6201 would ping pong with
a CR234 also simply because I know first hand that they will do so with
a simpler PR511 under certain conditions.
I will look up Tom Morgan on worthington's discussions and see if he
has any input. I had read some of his articles and did not see an
exact setup like this but I will ask him anyway and let him know of
this discussion over here.
Frank,
Thanks again and as you look at this where would you suggest the
Blocker be put in panel A, panel B or before the Y ????.
As I hear from others I will post their replies or excerpts of them
here to keep everyone interested informed.
Thanks Again to all interested and concerned.
Carl Ford
Before the "Y" (as Dave illustrated) and in the closest panel to it.
> Why should anyone take that advice instead of Phil Kingery's from Advanced
> Control Technologies (ACT) who authoritatively goes into considerable detail
> on why and how to deploy multiple couplers?
Sorry for the double response. I guess I missed this on the "first
pass"... :-)
Easy answer. The suggestion I made didn't involve connecting more
"couplers". I suggested he remove one of his *blockers*. I think he
already has all the "couplers" he needs. I also suggested connecting
the X10 Pro surge suppressor and eliminating all his capacitors.
One other thing comes to mind I am 28 feet from the power lines and am
at eye level with them on the 3rd floor. I had never realized that the
mains were NOT insulated. I asked one of the CP&L workers about this
and they said the salt would get under the insulation and make the
lines deterriorate much faster than if they were bare.
Thanks again for your input.
Carl Ford
Indeed it does, though no more so than any 120V load works against the
signal on a single leg. The impedance of 220V loads at 120kHz isn't
generally all that much lower than that of 120V loads. The problem comes
when you try to create a low impedance path between phases with a big
capacitor, tuned couplers, or what have you. As far as the repeater is
concerned this is exactly like deliberately installing a "signal sucker" load.
| How many 220V X-10 receivers are there?
How many are there where? Apparently they are common in industry, but
there are none in my house. For that reason I've been toying with the
idea of modifying a CR230 to drive the legs in phase. I've repaired the
unit with the bad power supply (if anyone cares, yes, the cap had leaked
as well from the heat) so I have one to play with. It isn't completely
trivial since the output driver circuit does not appear to be symmetrical.
Dan Lanciani
ddl@danlan.*com
Thanks,
Carl Ford
[...]
| 2. If your two 100-amp panels are side-by-side and fed from the same
| transformer (and, most likely, the same meter), you should be able to
| treat them as one big 200 amp panel.
The fact that you can see a significant difference between connection
to the two panels is what makes this difficult. It suggests that there
is some impediment to the signal between the two panels. Assuming that
you can't change this situation you won't be able to treat the two panels
as if they were one.
You could try to figure out what is going on or just accept that there is
significant (but not complete) isolation between the panels and work from
there. This is really the worst possible case since without complete
isolation it is very tricky to use multiple repeaters, and with poor coupling
you really want something on each panel. I'd be very tempted to try the
CA000 (with CR234) if it is still available.
| As far as the difference when moving the 6201 from panel A to B the
| only thing I can think of is that CM15A and Comfort's Tw523 are located
| on circuits in panel A.
That may well explain the functional differences, but the fact that there
is a difference at all between two panels which I assume are connected
by heavy (and not too long) cables to the same meter is troubling...
Dan Lanciani
ddl@danlan.*com
The CR234 does have the (potentially useful) SCC connection and some
configuration options to ignore repeated signals.
| Note that Ed Cheung wrote that ACT says not to use both the whole house
| blocker and coupler/repeater but that he saw no problems while doing so.
I use them together as well (in the house with the annoying 200kHz noise).
It's the least bad solution and it works reliably, but I think it's right
on the edge. Hence my interest in modifying a repeater. I suppose I
should first make absolutely sure that the blocker couples in phase.
Dan Lanciani
ddl@danlan.*com
I'm afraid not. It's their phase relative to each other that matters.
Dan Lanciani
ddl@danlan.*com
6201 Bridging Capacitor
| |
incoming-----+------Panel A----- Sub Panel A (Within 6 feet of panel)
weak outlet 2 1/2 stories
power |
from A
| (breakers) (breakers)
|
|
+-----Panel B-------- Sub Panel B (3 stories up)
weak outlet 3 stories from B
(breakers) (breakers)
| |
Capacitor Capacitor
When the 6201 is in panel A (as pictured) the furtherest point is sub
panel B (3rd floor) and then outlets on the opposite end of that floor
that are the weakest.
When the 6201 is in panel B the furtherest point is sub panel A (close
to both Panel A and B) but with outlets 2 and 1/2 stories away and on
the opposite ends of the house that are the weakest.
Trying to guess in linear feet they are about the same distance to the
furtherest point.
I have tested with and without the caps in circuit and all combinations
of caps in and out of circuit. The caps are for testing purposes only.
Total square feet in house is 4800 +
I do now understand about their phases being relative to each other
coming from the couplers or repeaters.
Again Thanks for your input. I have not heard directly from Tom Morgan
yet at Worthington but hope to do soon and will put his thoughts on the
table also as I got the original 6201 from them some 7 years ago.
Carl Ford
>Marc F Hult wrote:
>> On Mon, 12 Dec 2005 05:46:53 GMT, Frank Olson
>> <Use_the_e...@yoursecuritysource.com> wrote in message
>> <h98nf.96119$Eq5.71028@pd7tw1no>:
>>
>
>> What is Frank's (anonymous?) "X-10 design book" that "states you should
>> only use one" ?
>
>It's called X-10 Pro Design Book, Published by "Silent Servant Home
>Control, Inc." Authored by Robert N. Bucceri.
>
>>
>> Why should anyone take that advice instead of Phil Kingery's from
Advanced
>> Control Technologies (ACT) who authoritatively goes into considerable
detail
>> on why and how to deploy multiple couplers?
>>
>> See http://www.act-solutions.com/kingery03.htm
>> http://www.act-solutions.com/kingery04.htm
>> http://www.act-solutions.com/kingery20.htm
>
>Thanks for the links, Marc.
Interesting.
www.Amazon.com shows this:
Publisher: Silent Sevant Home Control; 2nd ed edition (1998)
Language: English
ASIN: B0006REPVW
and lists a couple copies available.
Does this reference deal quantitatively with X-10 signal issues, or does it
use 'signal sucker' and similar language to qualitatively explain problems?
Kingery's articles started in 1996, and so are approximately
contemporaneous.
Thanks ... Marc
Marc_F_Hult
www.ECOntrol.org
Thanks again to everyone,
Carl Ford
> Interesting.
>
> www.Amazon.com shows this:
> Publisher: Silent Sevant Home Control; 2nd ed edition (1998)
> Language: English
> ASIN: B0006REPVW
>
> and lists a couple copies available.
>
> Does this reference deal quantitatively with X-10 signal issues, or does it
> use 'signal sucker' and similar language to qualitatively explain problems?
>
> Kingery's articles started in 1996, and so are approximately
> contemporaneous.
Actually he uses what he terms as an "example home" to describe the
operation and installation of X-10 Pro components. He doesn't once
mention "signal sucker", although he uses other terms that are (I
assume) synonymous. Since I purchased the manual in 1998, I've sort of
used it as my "bible". I haven't experienced a single problem with any
components I've installed (other than having to return a very vew
defective items). Mind you my applications are more security related
than home automation (flashing outside lights during an alarm or turning
on different lights on a rotational basis to make it look like people
are home when they're not, turning on lights remotely or during an entry
delay and such like), but lately that's changed. It's really an
excellent resource, packed full of illustrations and sample set-ups.
I'd recommend it for anyone here without hesitation.
Do you know whether it's possible to disable the passive coupling of the
blocking couplers without affecting the blocking?
I never traced the full circuit, but intuitively I don't think it would
be possible without adding active buffers.
Dan Lanciani
ddl@danlan.*com
I built this home so I was able tell the electricians how to organize
the panels. One of the feeds, the one with the sub panel, has all of
the circuits that I don't control, appliances, hot water heaters, HVAC,
etc. The other panel with the lighting, outlets, etc., has a passive
X10 phase coupler on it.
I use PCS switches, numerous lamp & appliance modules and HCA to run the
house.
This setup works very very well. I have tried a HCA-02 Leviton repeater
and although it worked well from a signal level point of view they have
a problem with certain sequences so I just went back to the passive
coupler. From what I have heard the ACT repeaters to do not have this
problem.
I am able to get a good X10 signal across to the second panel for a
couple of outside light circuits that we had to put on that panel. Of
course the X10 signal from my controller has to go out to the meter and
back to get to the other panel but it does work.
I would recommend the following to start:
1) I am not clear on your whole house surge suppressers but put X10
friendly ones at each panel.
2) Put X10 passive couplers on each panel. What I mean by that is a
passive coupler that is tuned to the X10 120 Khz frequency not just a
cap that will pass a lot of noise as well.
3) Control the majority of your lighting from a controller located very
close to the panels. For example, send the "switch on/off" signal to
the controller and then let the controller turn the light on/off. For
remote circuits this cuts in half the distance that the X10 signal has
to go.
4) Of course do all of the standard stuff using filters to improve the
signal.
4) If your panels are not well organized and you have to cross the panel
boundary all of the time and it doesn't work reliably I see a couple of
approaches to try.
1) use a controller for each panel and go controller to controller for
programs that have to cross the panels. I assume the controllers are
located at the panels so at least you only have the distance to the
meter to cover not another long run of house wiring.
2) Use the ACT repeaters that support multiple repeaters and use one
each panel.
Larry
Thanks for all input thus far and I will post my results ASAP.
I never did get a reply from Tom Morgan. Someone else at that site did
also suggest the Cr-234.
Thanks again,
Carl Ford