Boiler in basement
Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump
The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
indepently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there. On the
zone I changed the pump the flo-control valve stopped the water from
coming out when I pulled the pump. I'm assuming the other two
flo-control zone valves are also properly preventing back flow. But
the problem is they are are always allowing hot water to flow forward
even if the pump for that zone is off. There are no zone valves on any
of the zones, only the flo-contral valves. The zone pumps, flo-control
valves and thermostats appear to be add-ons to the original system.
Does this system need a circulator pump for each zone?
Should there be zone valves installed for each zone?
Why? You have three zone valves and three circulators. The individual
circulator for the zone should be doing the ork.
> Flo-control valve on the hot/supply side of boiler mounted near ceiling
> Air separater right after main flo-control valve with bladder expansion
> tank
> Three additional zone circulator pumps connected to the thermostat
> relays
> Three zone flo-control valves, one right after each zone pump
>
> The problem is that whenever any zone calls for heat there is flow thru
> all three zones. I verified that each of the zone pumps are working
> indepently and correctly.
Was this a single zone system that was converted to a multi-zone system?
Sounds crazy to have a main circulator plus the individual zones. Could
also be the zone valves are not operating properly. Have you checked to be
sure they are closed?
.
> Does this system need a circulator pump for each zone?
> Should there be zone valves installed for each zone?
Should be one way or the other. Any thermostat calling for heat would start
the pump and open the valve for that zone. My house has two pumps, one for
each zone. The thermostat starts the pump for that zone only and heats
that zone only. The boiler is controlled by an aquastat that starts the
burner when the water temperature gets below the set point.
> > The problem is that whenever any zone calls for heat there is flow thru
> > all three zones. I verified that each of the zone pumps are working
> > indepently and correctly.
>
> Was this a single zone system that was converted to a multi-zone system?
Looks like it to me.
> Sounds crazy to have a main circulator plus the individual zones. Could
> also be the zone valves are not operating properly. Have you checked to be
> sure they are closed?
Again, no zone valves just the flo-control 'gravity flow' preventers.
> > Does this system need a circulator pump for each zone?
> > Should there be zone valves installed for each zone?
>
> Should be one way or the other. Any thermostat calling for heat would start
> the pump and open the valve for that zone. My house has two pumps, one for
> each zone. The thermostat starts the pump for that zone only and heats
> that zone only. The boiler is controlled by an aquastat that starts the
> burner when the water temperature gets below the set point.
I'm guessing the _main_ circulator pump is left-over from before the
system was zoned. My previous house had only one pump and three zone
valves and always worked fine. The pump was on the cold side of the
boiler. I think whoever did the zone work did not set up the system
properly. From what I read about these flo-control valves they will
allow flow with a minimal amount of pressure just not gravity flow from
rising hot water.
> I'm guessing the _main_ circulator pump is left-over from before the
> system was zoned. My previous house had only one pump and three zone
> valves and always worked fine. The pump was on the cold side of the
> boiler. I think whoever did the zone work did not set up the system
> properly. From what I read about these flo-control valves they will
> allow flow with a minimal amount of pressure just not gravity flow from
> rising hot water.
Unless I'm misunderstanding, aren't they designed to prevent backflow,
but allow flow from pumps, which appears to be the problem? When
circulator(s) are running, they are indeed allowing forward flow of
water through entire system. I think you need zone valves. As you say,
appears to be retrofitted system by someone who didn't quite know what
they were doing. Don't know how large the loops are, but main and zone
circulators seem redundant, though don't see why that should be a
problem(doesn't appear to be excessive electrical load at present),
once zone valves are put in.
You got it right. If you look at this page about halfway down they
show these valves installed after the zone pumps.
http://www.bellgossett.com/homeowners/BG-flocontrolvalve.asp
I think the reason his are allowing flow all of the time is 'main' pump
is on the return side of the bolier and forcing all three flo-control
valves open even though the zone pump isn't on.
I'm thinking of disconnecting the main circulator and then running each
zone to see if that cures the problem. Although having the pumps on
the outlet side of the boiler _could_ lead to a boiler overheat more
easily than if the pump was on the inlet side.
If it were my house I would disconnect the zone pumps and install zone
valves and run it for a season just using the main pump. If all went
well I would pull the zone pumps and have three spares.
Again, check to see that they are operating properly. Mine have an
adjustment thumb screw on the top of them.
> I'm guessing the _main_ circulator pump is left-over from before the
> system was zoned.
Sure sounds that way. The main pump would have enough force to get water
past the flo-controls.
"RayV" <Nunya...@comcast.net> wrote in message
news:1162304727....@k70g2000cwa.googlegroups.com...
I don't understand the multiple circulating pumps. If there is a manifold
with zone valves, when a zone thermostat calls for heat, the zone valve will
open, and that turns on the circulating pump. Only that zone will get the
hot water. The same for the other zone. The circulating pump won't shut
off until all the zone valves are closed.
Separate water heater.
> If it's a coil built into the boiler, you will have a triple
> aquastat relay mounted on the boiler to maintain temperature, but if not,
> you may have issues with the original circulator becoming energized when any
> of the others come on.
>
This is exactly what is happening, every time an individual zone calls
for heat the 'main' circulator pump kicks on with the boiler as well as
the zone pump. The pressure from the main circulator is enough to lift
the flo-control valves off their seats in every zone.
The biggest problem is my BIL makes Tim 'the tool man' Taylor look like
Tommy Silva. So I can't try things like disconnect the main circulator
and let it run for a few days. I told him several times after I
changed the zone pump and refilled the system to check the pressure a
couple times a day for a few days. He still hasn't checked it (he
forgot).
I'm thinking there are three options:
1-Have him buy three zone valves and replace the flo-control valves
with zone valves and leave everything else alone.
2-Put in the zone valves and disconnect the three zone pumps to see if
the single circulator pump can move enough water. If it works then
remove the zone circulators in the spring.
3-Tell him to call in a heating guy who will sell him some fancy
interconnected thermostats with ambient temperature probes along with
with cyclonic self-equalizing pumps. Oh yeah and a new boiler since
the old one isn't up to the task of properly heating the house
efficiently.
Ray, Did you check to make sure that the top nut of the check valve
was closed tight? Most times people forget to tighten this nut. If
not tight, it will allow for the hot water to enter into the other zone
causing ghost heating.
Paul
Yes. After I replaced the pump I fully opened (bypassed) the
flo-control valves and ran all of the circulator pumps to hopefully
flush any dirt from the seats and get the air moving. Then I closed
all of the flo-control valves. They were all closed when I got there
and hadn't been touched in years if ever.
Hmmm. I was just about to suggest exactly that- that the fix might be
as simple as unscrewing the wire nut that secures the hot wire for the
main circulator...
Well, then if they are tight and have been there for awhile and you
are getting ghost heating you may want to try and replace one of the
check valves. There really isn't much to forced hot water system.
Paul
I was thinking about trying that but all three flo-control valves are
allowing flow no matter which of the zones is calling for heat. That
would mean all three of them have failed or are stuck, he also told me
that he has always gotten heat everywhere in the house since he moved
in 8 years ago. This has to be an incorrect zone job done for the
previous owner.
--
Regards,
Doug Miller (alphageek at milmac dot com)
It's time to throw all their damned tea in the harbor again.
Can you post a pic of the whole system? Can you take apart one of the
valves and look inside?
"RayV" <Nunya...@comcast.net> wrote in message
news:1162304727....@k70g2000cwa.googlegroups.com...
Sorry....Disagree!! If you are NOT using zone valves then you need a
circ for each zone...PERIOD. If your using zone valves then one circ
wil work as long as you have the proper controller for the zone vavles.
How else are you going to get the hot water to each zone when there is
a call for heat by the thermostat? In my house I have two zones. I
choose to plumb my heating system with individual circulators because I
don't like zone valves. I have a Taco 503 controller that turns on
each individual circ when each thermostat calls for heat. In a basic
hot water boiler setup the only component that will prevent "Ghost
Heating" into a zone that is NOT calling for heat is a check
valve.....PERIOD.
So, don't remove the circ. I would make sure that the valves are
working properly. You should be able to open up the valve without
removing it completely form the system. Now, if your still confused on
this issue all you have to do is call a professional. They will figure
it out for you.
-paul
<paul.fl...@hotmail.com> wrote in message
news:1162420673....@f16g2000cwb.googlegroups.com...
Good point!!! LOL, wouldn't that be a kick in the A*S. He should make
sure that the arrow on the circ is pointing in the proper
direction......Didn't even think of that.
Here is what the flo-control valves look like
http://www.bellgossett.com/Press/BG-flocontrol.asp
RayV, After all of the suggestions made and what you have tried do you
have a fix? I'm curious to what fixed this problem and I'm sure the
others in the group would like to hear what the solution was.
-paul
I also posted this in alt.hvac and the predominate (reasonable) opinion
there and here is the main circulator pump on the inlet side of the
boiler is not needed in conjunction with the zone pumps. I suspect the
system would be fine with one pump and zone valves. The top floor
might not get as much flow if all 3 zones are calling at the same time
but the lower zones would eventually shut off.
This weekend I will go over and disconnect the wires to the 'main'
circulator and run each zone and see what happens. Worst that can
happen is I have to reconnect it.
If that doesn't work maybe I'll have him call in an HVAC guy for an
opinion. I could install zone valves for him and the parts would be
less than $400 (plus $30 for a bottle of vodka).
I'll post a followup after I try disconnecting the main pump.
Sounds like I misunderstood you. Are you saying that there are
circulators for each zone and then another circulator for all zones
which you call the main pump? If this is the case, then yes I agree
with you. I would disconnect the main circulator and try the heat.
-paul
Yes, the zoning and and zone pumps appear to be an add-on/upgrade to
the original system.