W wrote:
> "W" <
persis...@spamarrest.com> wrote in message
> news:7JidnS9as-G75rXS...@giganews.com...
>> Does any credible manufacturer make a 125 amp panel that holds up to 30
> 20A
>> circuit breakers? I need to replace a residential panel that currently
>> has 20 circuits in it and will be expanding to 26. Total anticipated
>> current load is around 50 amps.
>>
>> It would also be great if the panel had extra space at the bottom where
>> we could mount some current conductors so we can measure ongoing energy
>> use
> on
>> the HVAC system and computer room.
>
> A related question is whether there is any way to alter a 200 amp panel to
> only allow 125 amp incoming power without violating code. We are in
> Northern California.
125 amp main breaker.
> Many 200 amp panels support the amount of circuits we need, but
> unfortunately the underground conduit we are using is 2 inch and that
> apparently is under the 3 inch required for 200 amp service by code. If
> there were a 200 amp panel with a standard option to have the main panel
> breaker changed out to 125 amp we would be in business.
>
I don't see why this would be a problem from a decent electrical supply
house.
--
Paul Hovnanian mailto:
Pa...@Hovnanian.com
------------------------------------------------------------------
Steinbach's Guideline for Systems Programming
Never test for an error condition you don't know how to
handle.