Mark

unread,
Nov 2, 2006, 10:11:13 AM11/2/06
to
Good morning.

I am nearly ready to replace my 4x4 basement support post.
As part of this project, I plan to cut a hole in the slab and
pour a proper post footing using an 8" sonotube, A Simpson
CB64 bracket, and a bag of 5000psi Sakrete.

I will try to keep the hole small so that the sonotube is a
fairly snug fit. . .may an inch or even less clearance all around.
My question is, how would I properly fill the gap between the
concrete pour and the side of the hole? I have a couple of ideas:

- Pour concrete around the outside of the sonotube during the
initial pour. The paper would be left in place in the "underground"
portion, and removed where the footing projects through the slab.

- Remove all of the sonotube after the concrete sets up. Backfill
around the footing using (what?)

Other suggestions?

Thanks
-Mark


RicodJour

unread,
Nov 2, 2006, 10:16:36 AM11/2/06
to

Yes. Investigate the loads before you settle on an 8" sonotube.
Normally there is a spread footing under the sonotube to increase the
bearing area.

That 8" sonotube only has about .35 SF of bearing area. Guessing at a
soil bearing capacity of 2000 LBS/SF that sonotube will only be able to
bear about 700 pounds of load.

I think you are way undersized. Don't design a solution until you know
the loads involved.

R

Mark

unread,
Nov 2, 2006, 11:10:47 AM11/2/06
to
"RicodJour" <rico...@worldemail.com> wrote:
>
> Yes. Investigate the loads before you settle on an 8" sonotube.
> Normally there is a spread footing under the sonotube to increase the
> bearing area.
>
> That 8" sonotube only has about .35 SF of bearing area. Guessing at a
> soil bearing capacity of 2000 LBS/SF that sonotube will only be able to
> bear about 700 pounds of load.
>
> I think you are way undersized. Don't design a solution until you know
> the loads involved.

Now I'm wondering if I shouldn't just rest the new 4x6 post on top of the
slab, which is how the original 4x4 post was installed. I have no idea what
the
load is, but it was enough for the 4x4 to exceed the crush load of a doubled
two-by joist. That's what is motivating me to upgrade it.


RicodJour

unread,
Nov 2, 2006, 11:22:09 AM11/2/06
to

As an alternative, you could sawcut a 18" square in the slab -
essentially making a control joint, and build a wood form, on top of
the cut slab and pour a "footing" on top of the slab. The size I
mentioned is a total guess, you still must determine your loads. You
may also want to install an adjustable steel post instead of a wood
post.

R

Mark

unread,
Nov 2, 2006, 12:19:45 PM11/2/06
to
"RicodJour" <rico...@worldemail.com> wrote:
>
> As an alternative, you could sawcut a 18" square in the slab -
> essentially making a control joint, and build a wood form, on top of
> the cut slab and pour a "footing" on top of the slab. The size I
> mentioned is a total guess, you still must determine your loads. You
> may also want to install an adjustable steel post instead of a wood
> post.

I think I'll just install the post on the slab using a Simpson ABA46
bracket, with some grout packed inside for good measure. The house
stood for 75 years with a 4x4 post resting on the slab, so this should
suffice. My main concern is to fasten the post to the slab, and spread
the load at the top with a steel post cap so the joist isn't being crushed.

Incidentally, the soil on my lot is compacted glacial till. Having had
the misfortune of needing to dig in it, I can say with confidence that
its bearing capacity is greater than 2000 psf. But I have no idea
what it actually is.

-Mark

tonyg

unread,
Nov 2, 2006, 1:21:38 PM11/2/06
to
If you dig a tidy hole you can pour right in the hole and skip the
tube.However one bag of concrete is not enough for much except a small
fence post. tonyg

RicodJour

unread,
Nov 2, 2006, 2:10:02 PM11/2/06
to

You're doing a structural repair due to someone else failing to pay
attention to or understand the involved loads and material strengths.
I just checked your original post replacement thread - hadn't read it.
In one of your posts you pointed out that you felt a particular post
base would be insufficient as it only had a rated capacity of something
like 3500 pounds, yet your respond to my post about loads with an "I
have no idea".

You seem to selectively address and ignore load information. Why is
that?

R

Bob Morrison

unread,
Nov 2, 2006, 2:46:56 PM11/2/06
to
In a previous post RicodJour wrote...

> You're doing a structural repair due to someone else failing to pay
> attention to or understand the involved loads and material strengths.
> I just checked your original post replacement thread - hadn't read it.
> In one of your posts you pointed out that you felt a particular post
> base would be insufficient as it only had a rated capacity of something
> like 3500 pounds, yet your respond to my post about loads with an "I
> have no idea".
>
> You seem to selectively address and ignore load information. Why is
> that?
>

I second Rico's concerns here. It should be no big deal to cut a 18"-24"
square hole in the slab, excavate it to 10"-12" deep. Put (3) # bars in
the bottom (3" above the dirt please), fill the hole with concrete back
flush with the top of the slab. If you insist on using Quikrete or a
similar product then add one shovel full of portland cement to each bag of
Quikrete.

--
Bob Morrison, PE, SE
R L Morrison Engineering Co
Structural & Civil Engineering
Poulsbo WA
bob at rlmorrisonengr dot com

Mark

unread,
Nov 2, 2006, 4:46:31 PM11/2/06
to
"RicodJour" <rico...@worldemail.com> wrote:
>
> You're doing a structural repair due to someone else failing to pay
> attention to or understand the involved loads and material strengths.
> I just checked your original post replacement thread - hadn't read it.
> In one of your posts you pointed out that you felt a particular post
> base would be insufficient as it only had a rated capacity of something
> like 3500 pounds, yet your respond to my post about loads with an "I
> have no idea".
>
> You seem to selectively address and ignore load information. Why is
> that?

My assertion that the EPB64 post base with a 3500 lb load capacity would
be insufficient was strictly "from the gut." Having said that, I don't think
it was an unreasonable concern. This is an indoor application, so I
shouldn't
need the standoff that the EPB series brackets provide. The ABA46 that
I propose using is specifically intended for installation on a basement
slab,
and provides about 1" of standoff for good measure. It is also rated for
about 10,000 lbs downward force. Simpson specifies that it may be filled
with grout to "increase its capacity," although they don't specify what the
higher capacity might be.

Without a strain gauge, I cannot tell what the actual loading is on the
existing
post. Perhaps it is less than 3500 lbs, but I am more comfortable with
10,000 lbs capacity.

The existing 4x4 post has stood for 75 years without any obvious distress
in the slab, so I have no reason to believe that it won't serve as a
suitable
base for a 4x6 replacement column. Of course there _may_ be an integral
footing in the slab at that point. Unlikely, but possible.

I plan to use a CC3-1/4-6 post cap, which is made from 7 gauge steel and
spreads the load over 11 inches. I hope that will be sufficient so that the
post no longer exceeds the crush strength of the paired two-by joist.

-Mark


Mark

unread,
Nov 2, 2006, 4:54:08 PM11/2/06
to
"Bob Morrison" <SpamF...@junk.com> wrote:

>
> I second Rico's concerns here. It should be no big deal to cut a 18"-24"
> square hole in the slab, excavate it to 10"-12" deep. Put (3) # bars in
> the bottom (3" above the dirt please), fill the hole with concrete back
> flush with the top of the slab. If you insist on using Quikrete or a
> similar product then add one shovel full of portland cement to each bag of
> Quikrete.

I will think it over for a few days before I start into this. My main
concern
would be how to support the structure while I am doing this; digging a 24"
hole would put my shoring posts a fair distance from where the existing
column is located.

I'm happy to mix my own concrete. Is there a formula that you can
recommend for a high-strength requirement like this?

Thanks
-Mark


RicodJour

unread,
Nov 2, 2006, 5:10:55 PM11/2/06
to

You seem to be a methodical guy. Which makes it a little difficult to
follow your reasoning in basing your design on a failed installation
that almost assuredly doesn't meet code (code being the minimum
acceptable construction).

In the amount of time it took you to investigate the post bases you
could have determined exactly what the design load is so you wouldn't
be guessing. Unless you have a large amount of experience in
structures, "from the gut" equates to "wild assed guess". If you need
a little assistance in figuring out how to calculate the loads, just
say so. I assure you that even someone as experienced as Bob Morrison,
engineer extraordinaire, has had to ask some questions - and I've been
happy to answer them! ;)

R

Bob Morrison

unread,
Nov 2, 2006, 7:30:22 PM11/2/06
to
In a previous post Mark wrote...

> Without a strain gauge, I cannot tell what the actual loading is on the
> existing
> post. Perhaps it is less than 3500 lbs, but I am more comfortable with
> 10,000 lbs capacity.

A strain gage won't do you much good unless you can unload the post first.

A 10,000 pound load equates to about 5 square feet of footing. The 24"
square x 12" deep I suggested earlier will give about 8000 pounds
capacity.

> I will think it over for a few days before I start into this. My main
> concern would be how to support the structure while I am doing this;
> digging a 24" hole would put my shoring posts a fair distance from
> where the existing column is located.

Put in a temporary post on either side of the hole about 12 inches away
from the edge of the hole.


>
> I'm happy to mix my own concrete. Is there a formula that you can
> recommend for a high-strength requirement like this?

I don't do field mix design other than to say if you use typical bagged
concrete mix you should add some portland cement.

Bobk207

unread,
Nov 2, 2006, 10:15:24 PM11/2/06
to


Mark-

Not to "pile on" but........

if you're asking about concrete mix design & how to shore the structure
while you're doing the repair

then your "from the gut" evavluation of the post base might be coming
from another part of your anatomy..... :)


I didn't go back & read the old thread (I thought you'd be done with
this repair already)

Are you sure you've diagnosed the problem correctly? Why are you
replacing the post? What caused the original crushing?

If you're going to repair thsi properly you've got the understadn the
load path......just beefing up the post, post base & post cap may or
may not solve the real problem. A stronger post & post base are
really pretty useless if the slab / soil cannot take the load.

Obviously you have some technical skills (strain gage) but there's more
to structural repair then you currently know. Just making some of the
components arbitarily stronger, not knowing (or at least an educated
estimate) the load means you're pretty much guessing wildly.

If you're going through the trouble of doing the repair, take the
advice from the experienced guys in the ng......otherwise, why bother?

this statement pretty much sums up your approach

>>>>> I plan to use a CC3-1/4-6 post cap, which is made from 7 gauge steel and
spreads the load over 11 inches.

>> I hope that will be sufficient <<<<<<

>>>so that the post no longer exceeds the crush strength of the paired two-by joist. <<<<<


7 gage materail is pretty thin (.179) doubt that much load will spread
beyond the width of the 4x6 post


cheers
Bob

carolyn

unread,
Nov 3, 2006, 4:10:43 AM11/3/06
to
Mark wrote:

> Good morning.
>
> I am nearly ready to replace my 4x4 basement support post.
> As part of this project, I plan to cut a hole in the slab and
> pour a proper post footing using an 8" sonotube, A Simpson
> CB64 bracket, and a bag of 5000psi Sakrete.

What are you using as a footing for the post? The post needs to sit on
something that spreads the weight out. If your post is directly on
bedrock, a footing should not be needed. Otherwise check the local regs
and verify the size of footing you will need.

There is a product available at big-box stores, that is basically an
inverted funnel. The bottom of the tube is the correct diameter for a
footing, and over about a four foot rise it narrows to a 6" or 8" inch
diameter. It is made of plastic and meant to be left in the ground. Dig
your hole, drop in the cone, fill with concrete, add any bolts out the top,
backfill and wait for a day. Modern additives for the concrete could have
the concrete set and ready to use, before you have the hole backfilled.

> I will try to keep the hole small so that the sonotube is a
> fairly snug fit. . .may an inch or even less clearance all around.
> My question is, how would I properly fill the gap between the
> concrete pour and the side of the hole? I have a couple of ideas:

If you are able to have you post land on bedrock, then you can use sand,
gravel, or almost anything to backfill the hole. You can even use the dirt
you pulled out in the first place.

> - Pour concrete around the outside of the sonotube during the
> initial pour. The paper would be left in place in the "underground"
> portion, and removed where the footing projects through the slab.

If you leave the paper in place, as it rots it will shrink and you will get
settling around it. That in itself isn't much of an issue on a single
column, but around a foundation wall, it can lead to drainage problems if
not watched and repaired when the time comes. The other issue is the
rotting material - will any of the mold and whatever else grows on it, be
able to get into the house? If so, how will you deal with it?

> - Remove all of the sonotube after the concrete sets up. Backfill
> around the footing using (what?)

A shovel? :) Backfill with the original material from the hole.

Carolyn
--
Carolyn Marenger

Bob Morrison

unread,
Nov 3, 2006, 10:33:43 AM11/3/06
to
In a previous post carolyn wrote...

> There is a product available at big-box stores, that is basically an
> inverted funnel. The bottom of the tube is the correct diameter for a
> footing, and over about a four foot rise it narrows to a 6" or 8" inch
> diameter. It is made of plastic and meant to be left in the ground. Dig
> your hole, drop in the cone, fill with concrete, add any bolts out the top,
> backfill and wait for a day. Modern additives for the concrete could have
> the concrete set and ready to use, before you have the hole backfilled.
>

Carolyn:

I believe you may be making more out of this project than may be
necessary. The OP indicated that is soil is glacial till. This material
will stand with a vertical cut for a few days. More than enough time to
simply cut a hole in the slab, excavate the material, then backfill the
hole with concrete flush with the original slab. This kind of work gets
done in my area all the time. It is simple and easy to do. The hard part
is getting the slab cut and removing the concrete in a neat and orderly
way.

For a repair involving a major support for the house it certainly would
not be out of line to spend the money on a concrete sawing company to give
a neat finished appearance to the project.

M

unread,
Nov 3, 2006, 4:45:26 PM11/3/06
to
> I will think it over for a few days before I start into this. My main
> concern
> would be how to support the structure while I am doing this; digging a 24"

I did something like this but not exactly. I did have to unload a house and
re-load it. It is a one story house. I used a 20 ton bottle jack on 2-
2x12 cut slabs.. ap two feet log. then a cinder block two more 2x 12s on
top of the cinder block an 8x8 post and put the bottle jack on top of the
8x8. I was bale to jack the house well over 3/4 of an inch. i also did the
same thing with a 12 ton bottle jack on the other side. The two jacks only
cost a few hundred and was able to buy them at Napa. When I was done I had
to re-fit the house with a different sill and had to shim the load points so
having the bottle jacks helped me get the right fit by jacking and releasing
and putting in more or taking away shims until it was right. None the less
I think a couple of 12 ton jacks would do the job for you.


carolyn

unread,
Nov 4, 2006, 7:21:19 AM11/4/06
to
Bob Morrison wrote:

Bob,

You are probably right. I missed the 'glacial till' bit, and even now I
don't know what it is. Off to google in a moment. Thanks!

Carolyn
--
Carolyn Marenger

david ashworth

unread,
Nov 6, 2006, 9:41:34 AM11/6/06
to
Sir, Do not use a sonor tube. Check to make sure you have adequate depth
(building department). If you are using a 4 by 4, you should make it 12" (at
least in diameter) Free pour the concrete into the hole. By doing this you
fill all voids creating a better bearing position on already compacted soil.
Drop a plumb bob from the spot where the center of the pole is, while the
concrete is WET. This will allow you to place your SIMPSON TIE connector
to the right location. Wait a week before placing weight on it (Concrete
does not reach its fully cured state for about 28 days). When installing the
post, jack up the beam about a 1/4" past where you really want it. cut the
post to this height. The weight of the load above will compress the soil
this much. Here, we use concrete filled steel posts that we buy at a lumber
yard for less than 20.00. Good luck
"Mark" <nos...@thanksanyway.org> wrote in message
news:11624802...@bubbleator.drizzle.com...

Mark

unread,
Nov 6, 2006, 11:57:01 AM11/6/06
to
"david ashworth" <dgash...@verizon.net> wrote:
> When installing the post, jack up the beam about a 1/4" past where you
> really want it. cut the post to this height. The weight of the load above
> will compress the soil this much.

However I go about this, I _had_ planned to install an adjustable shoring
post for a few days, to (hopefully) work out any settling in the new
footing.
Anything wrong with this strategy?

Thanks
-Mark


RicodJour

unread,
Nov 6, 2006, 12:02:10 PM11/6/06
to

Why do you feel that the settling would occur in a few days? If you
see the benefits of an adjustable post, why wouldn't you make the
adjustable post permanent? Installing a temporary adjustable post
would be making extra work for yourself and basing it on the assumption
that all settlement would happen within your theoretical time frame.
Nature and structures rarely cooperate with arbitrary time frames.

R

Bob Morrison

unread,
Nov 6, 2006, 1:04:59 PM11/6/06
to
In a previous post Mark wrote...
> However I go about this, I _had_ planned to install an adjustable shoring
> post for a few days, to (hopefully) work out any settling in the new
> footing.
> Anything wrong with this strategy?
>

Totally unnecessary if you do the job properly in the first place.

A properly sized footing on a solid soil base won't settle. Certainly not
on glacial till. The only type of soils that might have some movement
issues would be expansive clays or soft peats. If you house is on either
one of those then you have a lot more than a single footing to worry
about.

Mark

unread,
Nov 6, 2006, 1:07:06 PM11/6/06
to

"RicodJour" <rico...@worldemail.com> wrote:
>
> Why do you feel that the settling would occur in a few days? If you
> see the benefits of an adjustable post, why wouldn't you make the
> adjustable post permanent? Installing a temporary adjustable post
> would be making extra work for yourself and basing it on the assumption
> that all settlement would happen within your theoretical time frame.
> Nature and structures rarely cooperate with arbitrary time frames.

So is there a consensus here that my proposed new footing is going to
settle? And is settling to be expected even if I make it 2' by 2' as
Bob has proposed?

If I jack up the beam 1/4" in anticipation of settling, the result will be
damage to the structure above the beam.

If I load the new post with the beam at its current level and it
settles 1/4", the result will be damage to the structure above the beam.

The existing post has rested on the slab for 75 years, and I have
no particular reason to expect the slab to fail (or to settle) if I put the
_new_ post on the slab. Barring a slab failure, this approach produces
no damage.

So this brings me full-circle back to the issue that we were discussing
last week Except now it appears that I _can_ expect damage if I pour
a new post footing instead of resting the new post on the slab where the
old post rested.

-Mark


RicodJour

unread,
Nov 6, 2006, 1:39:32 PM11/6/06
to
Mark wrote:
> "RicodJour" <rico...@worldemail.com> wrote:
> >
> > Why do you feel that the settling would occur in a few days? If you
> > see the benefits of an adjustable post, why wouldn't you make the
> > adjustable post permanent? Installing a temporary adjustable post
> > would be making extra work for yourself and basing it on the assumption
> > that all settlement would happen within your theoretical time frame.
> > Nature and structures rarely cooperate with arbitrary time frames.
>
> So is there a consensus here that my proposed new footing is going to
> settle? And is settling to be expected even if I make it 2' by 2' as
> Bob has proposed?

If the footing is placed on undisturbed soil there is no reason that it
would settle unless it was an insufficient, small footing.

> If I jack up the beam 1/4" in anticipation of settling, the result will be
> damage to the structure above the beam.

You mentioned that the bottom of the beam had crushed fibers at the
post. You should take a laser level to the floor above and see if the
floor dips at the beam. If so, jack it up slowly to prevent cracking.
About 1/16" per day should minimize cracking. If it hasn't settled and
you don't need to straighten out the floor, then just jack up the beam
enough to take the load off of the post and maybe a bit more. 1/8" is
all you need. Again, this should be done slowly to minimize cracking -
particularly if the house has plaster walls and tiled floors above.

> If I load the new post with the beam at its current level and it
> settles 1/4", the result will be damage to the structure above the beam.

It shouldn't settle.

> The existing post has rested on the slab for 75 years, and I have
> no particular reason to expect the slab to fail (or to settle) if I put the
> _new_ post on the slab. Barring a slab failure, this approach produces
> no damage.

My original advice was to saw cut the slab and place the footing on top
of it. The footing would not have to be quite as large nor deep if it
were on top of the slab. Build shelves around the post on top of the
footing if you'd like.

> So this brings me full-circle back to the issue that we were discussing
> last week Except now it appears that I _can_ expect damage if I pour
> a new post footing instead of resting the new post on the slab where the
> old post rested.

If you continue back full circle, check out my advice on placing the
footing on top of the slab. Thanks.

R

Bob Morrison

unread,
Nov 6, 2006, 1:53:21 PM11/6/06
to
In a previous post Mark wrote...
> So is there a consensus here that my proposed new footing is going to
> settle? And is settling to be expected even if I make it 2' by 2' as
> Bob has proposed?

No. As I just said a properly sized footing on undisturbed glacial till
will not settle.


> If I jack up the beam 1/4" in anticipation of settling, the result will be
> damage to the structure above the beam.
>
> If I load the new post with the beam at its current level and it
> settles 1/4", the result will be damage to the structure above the beam.

Raise the beam to level + a little. 1/16"-1/8" would be plenty. This has
nothing to do with settling and everything to do with being able to
install the new post cap.

> The existing post has rested on the slab for 75 years, and I have
> no particular reason to expect the slab to fail (or to settle) if I put the
> _new_ post on the slab. Barring a slab failure, this approach produces
> no damage.

Still doesn't make it the right solution. If you do the work properly and
carefully there will be no damage to the existing structure.

>
> So this brings me full-circle back to the issue that we were discussing
> last week Except now it appears that I _can_ expect damage if I pour
> a new post footing instead of resting the new post on the slab where the
> old post rested.

No. Wrong answer. If you don't want our advice then don't post
questions. I have given you a solution that has worked many times with no
damage to the existing structure. If you don't want to take the advice,
then don't. Just don't complain when you have problems down the road.

Overall, I think you are obsessing over this too much. If you had shored
the beam, cut the hole, and poured the concrete last week, you would now
be done with the project.

Mark

unread,
Nov 6, 2006, 3:32:13 PM11/6/06
to
"Bob Morrison" <SpamF...@junk.com> wrote:
>
> No. Wrong answer. If you don't want our advice then don't post
> questions. I have given you a solution that has worked many times with no
> damage to the existing structure. If you don't want to take the advice,
> then don't. Just don't complain when you have problems down the road.

Bob, I am not questioning your advice one bit. I was just following up
because someone else on the list chimed in with "It's gonna settle. . .
you'd better jack it up 1/4" first." Being prone to paranoia, I thought I
should follow up on that.

> Overall, I think you are obsessing over this too much. If you had shored
> the beam, cut the hole, and poured the concrete last week, you would now
> be done with the project.

Oh, no doubt about that. Unless of course the 2' x 2' hole filled up with
water courtesy of the current "pineapple express" we are enjoying here
in the PNW. =8-o

Hmm. . .maybe I should have you take a look at it. I actually have several
basement support issues that need attention. Are you interested in a few
hours of on-site consulting in Seattle?


Bob Morrison

unread,
Nov 6, 2006, 3:46:52 PM11/6/06
to
In a previous post Mark wrote...
> Bob, I am not questioning your advice one bit. I was just following up
> because someone else on the list chimed in with "It's gonna settle. . .
> you'd better jack it up 1/4" first." Being prone to paranoia, I thought I
> should follow up on that.

That was bad advice. As both Rico and I have pointed out you want to be
just above level. This is usually 1/16"-1/8"

>
> Oh, no doubt about that. Unless of course the 2' x 2' hole filled up with
> water courtesy of the current "pineapple express" we are enjoying here
> in the PNW. =8-o

If that hole fills with water you may have some serious drainage problems.
BTW, thanks to that "pineapple express", my power has gone out 4 times
since last Friday afternoon.

> Hmm. . .maybe I should have you take a look at it. I actually have several
> basement support issues that need attention. Are you interested in a few
> hours of on-site consulting in Seattle?

Probably not economically worth it for either of us. However, if you want
a structural engineer to look at the situation, here is a reference list
in PDF form:

http://tinyurl.com/y8s6ne