I think I would "sister" another 2x10 in the area the fireplace is
going to be sitting. Might even do a couple of crossbraces too.
Truthfully, it's pretty difficult to answer your question without
knowing what else is in the room weighing on the floor.
The OP is adding a permanent load, which is a dead load. The duration
of the load affects the calculation somewhat, and the allowable live
loads in most span tables are not based on permanent loads. They're
down-rated like wind and snow loads, though not to the same degree.
http://www.awc.org/technical/spantables/tutorial.htm
R
Like putting a water bed on the second floor or a piano.
I do know that most floor loads in the books are always tested high also.
I am sure they can take more if need be.
john
"RicodJour" <rico...@worldemail.com> wrote in message
news:5b75a950-710b-4221...@m26g2000yqb.googlegroups.com...
The tables show only distributed loads, not point loads. Point loads
require calculation and won't be in any table. Not only ultimate
strength will have to be determined, with a factor of safety of
course, but shear and deflection. The deflection won't be a problem
most likely. Having the load near the wall minimizes the risk, but if
the guy wants to look into it he should do it the right way. That
link gives a good overview of how to do it.
R
OP-
What is the TOTAL weight of the entire fireplace installation?
Framing, fireplace insert & all the finishes (rock face)?
If the load is in the 600 lb range .....13 ft span at 40 psf is 520
but you have more like a concentrated load (really a local
distributied load)
Just a SWAG but one sistered joist wouldn't be enough, two would
probably be ok, three would definitely do it. But to be sure you need
to do ( or have done) some calcs. That means....get it looked at.
I'd open up the floor or the ceiling below & sister in the joists.
cheers
Bob