Insulation u value wanted.

19 views
Skip to first unread message

robgraham

unread,
Mar 9, 2009, 9:29:18 AM3/9/09
to
I've an old cottage. Our bedroom ceiling - lathe and plaster - is
passed it's best and I'm going to reline it with p/b over a timber
frame. It did just strike me that the cavity so created should be
filled with insulation, but before I do all of this, I would like to
calculate reasonably accurately the heat losses through all the
surfaces. There's 6" of fibreglass in the attic.

Two of the walls are external and stone structure. Can someone give
me a usable U figure for a stone wall that is 560mm thick and consists
of an inner and out stone skin with loose rubble in the middle.
Inside this is 50mm of rockwool and then p/b.

I haven't looked at u tables recently but what is the influence of a
carpet and underlay on a wooden floor with plenty of underfloor
ventilation ?

An alternative thought to using u values is to take the room air
temperature and then IR thermometer each surface; can that be used to
work out the major heat loss ?

Thanks

Rob

RobertL

unread,
Mar 9, 2009, 9:49:47 AM3/9/09
to
On Mar 9, 1:29 pm, robgraham <robkgra...@btinternet.com> wrote:
> I've an old cottage. Our bedroom ceiling - lathe and plaster - is
> passed it's best and I'm going to reline it with p/b over a timber
> frame.  It did just strike me that the cavity so created should be
> filled with insulation, but before I do all of this, I would like to
> calculate reasonably accurately the heat losses through all the
> surfaces.  There's 6" of fibreglass in the attic.


Think twice before you pull it down. I had such a ceiling and
pulled it down (for woodworm treatment in fact) planning to insulate
above it and replace it with plasterboard. But Building Control got
wind of this work and informed me that I had made an "unauthorised
alteration to a thermal unit" and that I needed to file a
regularisation application (£120 IIRC) for it and get their approval
for what I wanted to do. It then had to meet modern building
regulations for insulation. I am having to lower the ceiling to fit in
enough insulation to meet the BC requirements.

Once you pull it down you aren't allowed to simply put it back.

Robert

meow...@care2.com

unread,
Mar 9, 2009, 11:20:23 AM3/9/09
to

Maybe OP means he'll leave the L&P there and add battens and PB.

Refixing an old L&P ceiling and skimming it isnt really any more work
though. Less really.


NT

Mike

unread,
Mar 9, 2009, 1:17:40 PM3/9/09
to

£120 quid down the drain to achieve nothing. Bugger building control,
put the insulation you deem necessary, stick the plasterboard back up
and then ignore them. What are they going to do, insist you pull down
the ceiling yet again only to put it back up? F*ck 'em. Parasites!

--

sm_ja...@hotmail.com

unread,
Mar 9, 2009, 2:41:57 PM3/9/09
to

How did they "get wind of it" ?
Simon

Rob G

unread,
Mar 9, 2009, 5:08:12 PM3/9/09
to
On 9 Mar, 13:49, RobertL <robertml...@yahoo.com> wrote:

I would help, guys, if you answered the question rather than going off
onto another topic because you didn't read the posting correctly - I
did actually say that the new ceiling plasterboard was going onto a
new frame and there was to be a cavity.

It's a bit unfair of you to take advantage of my posting to make your
rant against BCO's.

Rob

george (dicegeorge)

unread,
Mar 9, 2009, 5:17:51 PM3/9/09
to

>> Think twice before you pull it down. I had such a ceiling and
>> pulled it down (for woodworm treatment in fact) planning to insulate
>> above it and replace it with plasterboard. But Building Control got
>> wind of this work and informed me that I had made an "unauthorised
>> alteration to a thermal unit" and that I needed to file a
>> regularisation application (£120 IIRC) for it and get their approval
>> for what I wanted to do.


ooopa -
i have some lathe and plaster ceiling which has collapsed due to a burst
pipe,
am i allowed to patch it with a plasterboard patch?
i was going to replace a few square yards with plasterboard and
insulation, but now must think again must i?


[g]

Hugo Nebula

unread,
Mar 9, 2009, 6:09:29 PM3/9/09
to
On Mon, 9 Mar 2009 06:29:18 -0700 (PDT), a certain chimpanzee,
robgraham <robkg...@btinternet.com> randomly hit a keyboard and
produced:

>Two of the walls are external and stone structure. Can someone give
>me a usable U figure for a stone wall that is 560mm thick and consists
>of an inner and out stone skin with loose rubble in the middle.
>Inside this is 50mm of rockwool and then p/b.

From the top of my head:

Outside surface resistance = 0.04m^K/W
Limestone: conductivity = 1.13W/mK; divide the thickness by this value
to give resistance.
Mortar (and presumably loose fill): conductivity = 0.84W/mK [1]
Rockwool: conductivity = 0.05m/0.038W/mK = 1.32m^K/W [2]
Plasterboard resistance = 0.06m^K/W.
Inner surface resistance = 0.13m^K/W

Add up all the resistances, then take the reciprocal to give your
U-value.

[1] It depends on the proportions of wall to rubble-fill, but I would
have thought about 75% stone to 25% mortar and crap, which gives an
average conductivity of about 1.04W/mK.

[2] If you want a precise figure, you should also include for the
studs in the dry-lining.

R = 0.04 + 0.56/1.04 + 1.32 + 0.06 + 0.13 = 2.09m^2K/W. Therefore
U-value = 1/2.09 = 0.48W/m^2K. To work out heating, probably best to
use 0.6-0.8 unless you can put actual values to the thicknesses of the
leaves of the wall.
--
Hugo Nebula
"If no one on the Internet wants a piece of this,
just how far from the pack have you strayed?"

John Rumm

unread,
Mar 9, 2009, 6:56:15 PM3/9/09
to
george (dicegeorge) wrote:
>
>>> Think twice before you pull it down. I had such a ceiling and
>>> pulled it down (for woodworm treatment in fact) planning to insulate
>>> above it and replace it with plasterboard. But Building Control got
>>> wind of this work and informed me that I had made an "unauthorised
>>> alteration to a thermal unit" and that I needed to file a
>>> regularisation application (£120 IIRC) for it and get their approval
>>> for what I wanted to do.
>
>
> ooopa -
> i have some lathe and plaster ceiling which has collapsed due to a burst
> pipe,
> am i allowed to patch it with a plasterboard patch?

yup. You can do what you like with a repair generally.

> i was going to replace a few square yards with plasterboard and
> insulation, but now must think again must i?

Even for work carried out under a building notice, most BCOs are quite
pragmatic, and work on the principle that it will not always be possible
(or even desirable) to meet modern standards on an old building, and if
you make sure what you put back is no worse than before, they are happy.

--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

Rob G

unread,
Mar 10, 2009, 4:51:51 AM3/10/09
to
On 9 Mar, 22:09, Hugo Nebula <abuse@localhost> wrote:
> On Mon, 9 Mar 2009 06:29:18 -0700 (PDT), a certain chimpanzee,
> robgraham <robkgra...@btinternet.com> randomly hit a keyboard and

Many thanks Hugo - I should have said the stone was sandstone and whin
but the values won't but be that much different and anyway the
percentage stone/rubble will be a guess.

Rob

Rob

The Natural Philosopher

unread,
Mar 10, 2009, 6:10:14 AM3/10/09
to
robgraham wrote:
> I've an old cottage. Our bedroom ceiling - lathe and plaster - is
> passed it's best and I'm going to reline it with p/b over a timber
> frame. It did just strike me that the cavity so created should be
> filled with insulation, but before I do all of this, I would like to
> calculate reasonably accurately the heat losses through all the
> surfaces. There's 6" of fibreglass in the attic.
>

sounds like a plan. Use celotex and make it utterly airtight.

> Two of the walls are external and stone structure. Can someone give
> me a usable U figure for a stone wall that is 560mm thick and consists
> of an inner and out stone skin with loose rubble in the middle.
> Inside this is 50mm of rockwool and then p/b.
>

Not good, The walls are next to bugger all, and although 50mm of
rockwool is better than nothing, 50mm of celotex is about twice as good.

> I haven't looked at u tables recently but what is the influence of a
> carpet and underlay on a wooden floor with plenty of underfloor
> ventilation ?
>

Not nearly as much as totally draughtproofing it. Nail hardboard over it
and seal with duct tape and re-lay carpets. Or lift whole floor, and put
clotex betwen joists, tape up and re-lay floor.

> An alternative thought to using u values is to take the room air
> temperature and then IR thermometer each surface; can that be used to
> work out the major heat loss ?
>

Not a bad way to at least ID cold bridges and the like.

> Thanks
>
> Rob

Martin Bonner

unread,
Mar 10, 2009, 8:36:50 AM3/10/09
to
On Mar 9, 10:09 pm, Hugo Nebula <abuse@localhost> wrote:
> [2] If you want a precise figure, you should also include for the
> studs in the dry-lining.

ABSOLUTELY! I was thinking of dry lining one wall of my kitchen
(currently just 9" brickwork). I was trying to get down to a fairly
low U-value (the current new-build standard). It looked fairly
straightforward until I factored in the studs - half the heat was
going through the studs, and half through the celotex between them!
(I wanted studs so I could screw things to the walls. I think the
solution is an overall 25mm layer of Celotex + studs with Celotex
infill for the rest.)


Rob G

unread,
Mar 10, 2009, 1:17:12 PM3/10/09
to

Celotex wasn't available when this was done !! And you don't realise
just how effective it was - the cottage was modified in the 1920's to
lift the stone slab floors, dig out, ventilate and lay suspended
wooden floors - then they added lathe and plaster to the original
distempered stone walls - unfortunately they didn't control the
underfloor ventilation going up behind the L&P to the roof space so
the whole house had zero wall insulation in the winter gales. All L&P
had to be removed and insulation added.

> Not nearly as much as totally draughtproofing it. Nail hardboard over it
> and seal with duct tape and re-lay carpets. Or lift whole floor, and put
> clotex betwen joists, tape up and re-lay floor.

I don't know what sort of floors you live with but my floors are good
quality T & G which I'm not detecting any draughts through. I've a
self made electronic draught detecting thermometer.

Rob